<DIV>Jeremy:</DIV>
<DIV> </DIV>
<DIV>My space is subject to the requirements to model a cooling system in the 
baseline.</DIV>
<DIV> </DIV>
<DIV>This is where I am a bit confused. The office area has a specified cooling 
and heating system (RTU) but the warehouse area only has a heating system - 15 
unit heaters plus a ventilation system. The building is only one level - so 
do I model just one cooling and heating system (system 5) or can I model 2 
systems? - one for the office and one for the warehouse?</DIV>
<DIV> </DIV>
<DIV>If so how do I treat the fan energy from the unit heaters and the need to 
model a boiler and hot water pumps, when no such system exists?</DIV>
<DIV> </DIV>
<DIV>
<DIV>In a message dated 3/3/2011 4:13:10 P.M. Eastern Standard Time, 
Jeremy.Poling@transwestern.net writes:</DIV>
<BLOCKQUOTE 
style="PADDING-LEFT: 5px; MARGIN-LEFT: 5px; BORDER-LEFT: blue 2px solid"><FONT 
  style="BACKGROUND-COLOR: transparent" face=Arial color=#000000 size=2>
  <DIV class=WordSection1>
  <P class=MsoNormal><SPAN 
  style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri','sans-serif'">Richard,<o:p></o:p></SPAN></P>
  <P class=MsoNormal><SPAN 
  style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri','sans-serif'"><o:p> </o:p></SPAN></P>
  <P class=MsoNormal><SPAN 
  style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri','sans-serif'">First 
  check against the definitions of “space” on page  13.  If the rated 
  capacity of the heating units for the space is between 3.4 Btuh/SF and the 
  value in Table 3.1 for your climate zone, then your warehouse space is 
  considered a semi-heated space and is not subject to the requirement to model 
  a cooling system in the baseline.<o:p></o:p></SPAN></P>
  <P class=MsoNormal><SPAN 
  style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri','sans-serif'"><o:p> </o:p></SPAN></P>
  <P class=MsoNormal><SPAN 
  style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri','sans-serif'">For 
  the question on number of systems, what you’re looking is under G3.1.1: “For 
  systems 5, 6, 7, and 8, each floor shall be modeled with a separate HVAC 
  system.”  That would mean a single system for the entire warehouse 
  portion of the building and the offices (unless you claim an exemption for the 
  offices due to G3.1.1.a, G3.1.1.b, G3.1.1.c, or G3.1.1.d).  Then note any 
  requirements for system 5 from the latter portions of appendix 
  G.<o:p></o:p></SPAN></P>
  <P class=MsoNormal><SPAN 
  style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri','sans-serif'"><o:p> </o:p></SPAN></P>
  <DIV>
  <P class=MsoNormal><B><SPAN 
  style="FONT-SIZE: 7.5pt; COLOR: #1f497d; FONT-FAMILY: 'Verdana','sans-serif'">Jeremy 
  R. Poling, PE, LEED AP+BDC</SPAN></B><SPAN 
  style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri','sans-serif'"><BR><BR></SPAN><SPAN 
  style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri','sans-serif'"><o:p></o:p></SPAN></P></DIV>
  <P class=MsoNormal><SPAN 
  style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri','sans-serif'"><o:p> </o:p></SPAN></P>
  <DIV>
  <DIV 
  style="BORDER-RIGHT: medium none; PADDING-RIGHT: 0in; BORDER-TOP: #b5c4df 1pt solid; PADDING-LEFT: 0in; PADDING-BOTTOM: 0in; BORDER-LEFT: medium none; PADDING-TOP: 3pt; BORDER-BOTTOM: medium none">
  <P class=MsoNormal><B><SPAN 
  style="FONT-SIZE: 10pt; FONT-FAMILY: 'Tahoma','sans-serif'">From:</SPAN></B><SPAN 
  style="FONT-SIZE: 10pt; FONT-FAMILY: 'Tahoma','sans-serif'"> 
  equest-users-bounces@lists.onebuilding.org 
  [mailto:equest-users-bounces@lists.onebuilding.org] <B>On Behalf Of 
  </B>RJTHEACMAN@aol.com<BR><B>Sent:</B> Thursday, March 03, 2011 11:48 
  AM<BR><B>To:</B> equest-users@lists.onebuilding.org<BR><B>Subject:</B> 
  [Equest-users] Fedx<o:p></o:p></SPAN></P></DIV></DIV>
  <P class=MsoNormal><o:p> </o:p></P>
  <DIV>
  <P class=MsoNormal><SPAN 
  style="FONT-SIZE: 10pt; COLOR: black; FONT-FAMILY: 'Arial','sans-serif'">  
  <o:p></o:p></SPAN></P>
  <DIV>
  <P class=MsoNormal><SPAN 
  style="FONT-SIZE: 10pt; COLOR: black; FONT-FAMILY: 'Arial','sans-serif'">I am 
  modeling a 110,000 sf. Fedex sorting facility for LEED and the building has a 
  small office area that is heated and cooled by rooftop units and the 
  remainder of the warehouse is only heated.<o:p></o:p></SPAN></P></DIV>
  <DIV>
  <P class=MsoNormal><SPAN 
  style="FONT-SIZE: 10pt; COLOR: black; FONT-FAMILY: 'Arial','sans-serif'"> <o:p></o:p></SPAN></P></DIV>
  <DIV>
  <P class=MsoNormal><SPAN 
  style="FONT-SIZE: 10pt; COLOR: black; FONT-FAMILY: 'Arial','sans-serif'">In 
  accordance with ASHRAE 90.1 2007 if no cooling system exists the cooling 
  system shall be identical to the system modeled in the baseline building 
  design.<o:p></o:p></SPAN></P></DIV>
  <DIV>
  <P class=MsoNormal><SPAN 
  style="FONT-SIZE: 10pt; COLOR: black; FONT-FAMILY: 'Arial','sans-serif'"> <o:p></o:p></SPAN></P></DIV>
  <DIV>
  <P class=MsoNormal><SPAN 
  style="FONT-SIZE: 10pt; COLOR: black; FONT-FAMILY: 'Arial','sans-serif'">That 
  system is a system 5 packaged vav with reheat, which includes a hot water 
  boiler. <o:p></o:p></SPAN></P></DIV>
  <DIV>
  <P class=MsoNormal><SPAN 
  style="FONT-SIZE: 10pt; COLOR: black; FONT-FAMILY: 'Arial','sans-serif'"> <o:p></o:p></SPAN></P></DIV>
  <DIV>
  <P class=MsoNormal><SPAN 
  style="FONT-SIZE: 10pt; COLOR: black; FONT-FAMILY: 'Arial','sans-serif'">We 
  have (15) gas-fired unit heaters that provide heat to the 
  warehouse.<o:p></o:p></SPAN></P></DIV>
  <DIV>
  <P class=MsoNormal><SPAN 
  style="FONT-SIZE: 10pt; COLOR: black; FONT-FAMILY: 'Arial','sans-serif'"> <o:p></o:p></SPAN></P></DIV>
  <DIV>
  <P class=MsoNormal><SPAN 
  style="FONT-SIZE: 10pt; COLOR: black; FONT-FAMILY: 'Arial','sans-serif'">My 
  question is do I set up my heating system with 15 hot water boilers, the same 
  heating capacity as the unit heaters?<o:p></o:p></SPAN></P></DIV>
  <DIV>
  <P class=MsoNormal><SPAN 
  style="FONT-SIZE: 10pt; COLOR: black; FONT-FAMILY: 'Arial','sans-serif'"> <o:p></o:p></SPAN></P></DIV>
  <DIV>
  <P class=MsoNormal><SPAN 
  style="FONT-SIZE: 10pt; COLOR: black; FONT-FAMILY: 'Arial','sans-serif'">For 
  the fan energy, do I set my air quantity the same as my unit 
  heaters?<o:p></o:p></SPAN></P></DIV>
  <DIV>
  <P class=MsoNormal><SPAN 
  style="FONT-SIZE: 10pt; COLOR: black; FONT-FAMILY: 'Arial','sans-serif'"> <o:p></o:p></SPAN></P></DIV>
  <DIV>
  <P class=MsoNormal><SPAN 
  style="FONT-SIZE: 10pt; COLOR: black; FONT-FAMILY: 'Arial','sans-serif'">How 
  do I address the VAV portion of the system as well as the hot water 
  pumps?<o:p></o:p></SPAN></P></DIV>
  <DIV>
  <P class=MsoNormal><SPAN 
  style="FONT-SIZE: 10pt; COLOR: black; FONT-FAMILY: 'Arial','sans-serif'"> <o:p></o:p></SPAN></P></DIV>
  <DIV>
  <P class=MsoNormal><SPAN 
  style="FONT-SIZE: 10pt; COLOR: black; FONT-FAMILY: 'Arial','sans-serif'">I 
  have my model setup with (2) separate HVAC systems (1) Packaged VAV with 
  Reheat and (2) Packaged rooftop DX units with a gas 
  furnace.<o:p></o:p></SPAN></P></DIV>
  <DIV>
  <P class=MsoNormal><SPAN 
  style="FONT-SIZE: 10pt; COLOR: black; FONT-FAMILY: 'Arial','sans-serif'"> <o:p></o:p></SPAN></P></DIV>
  <DIV>
  <P class=MsoNormal><SPAN 
  style="FONT-SIZE: 10pt; COLOR: black; FONT-FAMILY: 'Arial','sans-serif'">Any 
  help will be greatly appreciated.<o:p></o:p></SPAN></P></DIV>
  <DIV>
  <P class=MsoNormal><SPAN 
  style="FONT-SIZE: 10pt; COLOR: black; FONT-FAMILY: 'Arial','sans-serif'"> <o:p></o:p></SPAN></P></DIV>
  <DIV>
  <P class=MsoNormal><SPAN 
  style="FONT-SIZE: 10pt; COLOR: black; FONT-FAMILY: 'Arial','sans-serif'">Richard 
  Dominick, P.E.<o:p></o:p></SPAN></P></DIV>
  <DIV>
  <P class=MsoNormal><SPAN 
  style="FONT-SIZE: 10pt; COLOR: black; FONT-FAMILY: 'Arial','sans-serif'">TEC 
  Engineers, LLC.<o:p></o:p></SPAN></P></DIV>
  <DIV>
  <P class=MsoNormal><SPAN 
  style="FONT-SIZE: 10pt; COLOR: black; FONT-FAMILY: 'Arial','sans-serif'">Norwalk, 