[Equest-users] pool heating baseline system
Nick Caton
ncaton at smithboucher.com
Tue Jan 25 19:38:11 PST 2011
Well I've given a little extra effort =)... I've flip-flopped a few
times, and now feel confident of the following:
1. This query boils down to this paraphrase: Does Table G3.1.11
(Service Hot-Water Systems) or G3.1.12 (Receptacle and other loads)
apply to pool water heating?
2. Definitions Section 3: service water heating - heating water
for domestic or commercial purposes other than space heating and process
requirements.
3. We can strike out space heating, so we can conclude pool water
heating is either a process energy OR service water heating... it cannot
be both.
4. GRAMMAR LESSON FOR ANSI/ASHRAE/IESNA - WOOHOO!
a. Per the definition Mirza transcribed below, pool heating is
pretty clearly "...maintaining comfort and amenities for the occupants
of a building."
b. So (clearly) pool heating energy simply [IS/IS NOT] a process
energy, and therefore [IS/IS NOT] a process load. Read that whole
definition from both angles, and you can see this definition was not
crafted by an English teacher! This doesn't make anyone's life easier,
but I maintain this definition can be read either way.
5. Where the glossary fails us, we have to look elsewhere.
Fortunately, this seems much more clear: Pool water heating must be a
form of service water heating, otherwise it wouldn't be explicitly
addressed multiples times under Section 7 "SERVICE WATER HEATING."
Clever eh =)?
In conclusion, within the context of "do I model pool energy under the
requirements of Table G3.1.11 or G3.1.12?" The answer is clearly
G3.1.11 because it is a variety of service hot-water system. To extend
the argument, pool water heating is NOT a process energy and so should
NOT be modeled as such (equally in both models), even if it would save
time (bummer!). I might suggest documenting the pool heating
consumptions/demands separately from domestic water heating consumption
in the LEED template.
Table G3.1.11 is agreeably crystal-clear in requiring you to use
straight electric resistance heating for the baseline pool heating
system.
If LEED was an episode of "America's Next Top Model," and the 90.1-2007
steering committee were the judges, heat-pump pool heating strategies
would be rated "Platinum-Sexy."
I might also watch more TV... kinda sad... ^_^
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
Smith & Boucher Engineers
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
www.smithboucher.com
From: Dahlstrom, Aaron [mailto:ADahlstrom at in-posse.com]
Sent: Tuesday, January 25, 2011 7:59 PM
To: Mirza Sajjal; Nick Caton; Pasha Korber-Gonzalez
Cc: equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] pool heating baseline system
Mirza -
I agree with your logic about the intent of the standard and its
definition of non-regulated process. This may be a prejudice that
harkens back to LEED v2.1, but if I see a regulation in 90.1 for
efficiency, I assume that ASHRAE intended to "regulate" the energy use
of that category, and thus it falls on the non-process side of things.
While there may be circumstances where "pool heating" might seem more
like a process load (eg freeze protection for an outdoor decorative
fountain in a cold climate?), it seems like the intent of 90.1 was to
regulate pool heating energy usage for a large proportion of typical
pool installations.
I think your question re: how to interpret the wording of G3.1.11 is
important.
On the face of App G, the standard appears to reward heat pump pool
heaters, by allowing them to compare to straight resistance heat in the
baseline.
In my admittedly limited experience, I haven't seen an electric
resistance pool heater, so I share your reservations about making a
false comparison. (then again ...
http://www.little-giant.com/water-heating-products/pool-spa-heaters/elec
tric-pool-spa-heaters.html)
If we can't find help for you on this list, an "unofficial
interpretation" by the 90.1 Standards Committee might be the way to go.
(Maybe Nick could even slip the question in when he's out at the winter
meetings this week ;) ?)
Aaron Dahlstrom , PE, LEED(r) AP
In Posse - A subsidiary of AKF| 1500 Walnut Street, Suite 1414,
Philadelphia, PA 19102
d: 215-282-6753| m: 267-507-5470| In Posse: 215-282-6800| AKF:
215-735-7290
e: ADahlstrom at in-posse.com | in posse web: www.in-posse.com
<http://www.in-posse.com/> | akf web: www.akfgroup.com
<http://www.akfgroup.com/>
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Mirza
Sajjal
Sent: Tuesday, January 25, 2011 7:36 PM
To: Nick Caton; Pasha Korber-Gonzalez
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] pool heating baseline system
Pasha/Nick,
Thanks for the response.
I would assume pool space conditioning and pool water heating are not
process energy (?) as 90.1 defines process energy as:
"Energy consumed in support of a manufacturing, industrial, or
commercial process other than conditioning spaces and maintaining
comfort and amenities for the occupants of a building."
I did notice the baseline efficiency for heat pump pool heaters in table
7, but was trying to figure out if the system types had to be the same
in baseline and proposed since App. G mentions only energy source:
"Where the energy source is electricity, the heating method shall be
electric resistance."
Considering the savings are significant when using electric resistance
pool heating in the baseline, I want to prevent any issues I may
encounter during the LEED review process since the reviewer may have a
different interpretation/opinion.
Mirza
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nick
Caton
Sent: Tuesday, January 25, 2011 7:05 PM
To: Pasha Korber-Gonzalez; Mirza Sajjal
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] pool heating baseline system
Whether or not it's a process load may come down to semantics (I think
you can make a case either way if you reference the 90.1 glossary terms
- see 'process load' and 'process energy'), but I think it's moot in a
broad sense...
If there weren't significant savings to be credited, then I'd probably
try to call it a process load and make each model identical. That would
be the simplest and most time efficient approach.
However, if there are major savings using heatpumps relative to
"conventional" heating means, then even if it is a "process load" I
would pursue modeling them differently as an exceptional calculation.
Oh, and 90.1 does define a baseline efficiency (COP) for heat pump pool
heating equipment: Take a closer look the table in chapter 7. You
might also review the prescriptive pool requirements for other means to
differentiate the proposed design other than in heating efficiency.
Best of luck!
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
Smith & Boucher Engineers
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Pasha
Korber-Gonzalez
Sent: Tuesday, January 25, 2011 4:50 PM
To: Mirza Sajjal
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] pool heating baseline system
Isn't the pool heating system considered as a process load for 90.1
since it has no effect on the overall building design? It would be
exactly the same in the baseline as it is for the proposed case.
...just a thought, although I haven't run into this scenario with any of
my sim projects.
Pasha
On Tue, Jan 25, 2011 at 3:19 PM, Mirza Sajjal <ms2995 at gmail.com> wrote:
Can anyone tell me what the baseline pool heating system should be if
the design calls for heat pumps? Per App. G Table G3.1.11 the
requirement is that the energy source be the same, in this case
electricity. Can we model the baseline as electric water heaters or
should the system type (heat pumps) also remain the same in the baseline
since electric resistance pool heating is unconventional? Theres a huge
energy savings difference between the two baselines and was wondering
how others have modeled this in terms of LEED.
Your opinion and insight is much appreciated.
Thanks in advance for any response.
Mirza
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
This message has been scanned by MailController
<http://www.mailcontroller.altohiway.com/> .
This e-mail may contain information that is confidential, privileged or
otherwise protected from disclosure. If you are not an intended
recipient of this e-mail, do not duplicate or redistribute it by any
means. Please delete it and any attachments and notify the sender that
you have received it in error. Unintended recipients are prohibited from
taking action on the basis of information in this e-mail. E-mail
messages may contain computer viruses or other defects, may not be
accurately replicated on other systems, or may be intercepted, deleted
or interfered without the knowledge of the sender or the intended
recipient. If you are not comfortable with the risks associated with
e-mail messages, you may decide not to use e-mail to communicate with In
Posse.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110125/8eb68d2b/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110125/8eb68d2b/attachment.jpeg>
More information about the Equest-users
mailing list