[Equest-users] Building Shades

Nick Caton ncaton at smithboucher.com
Tue Jan 4 13:43:50 PST 2011


The procedure you’re describing should work fine.  In my humble opinion, it’s pretty clever actually!  

 

A no-cooling/no-heating system results in a “SUM” system post-wizards, which is just a placeholder.  The only items that might consume energy in a shell after the HVAC system is out would be internal items:  lights/receptacles/service hot water – you’re eliminating those as well by unticking all the non-HVAC enduses.

 

Considering that, you could simplify your procedure a bit I think:  There shouldn’t be a need to specify a ‘closed’ type or any other specific schedule for the shell.

 

~Nick

 

 

NICK CATON, E.I.T.

PROJECT ENGINEER

Smith & Boucher Engineers

25501 west valley parkway

olathe ks 66061

direct 913 344.0036

fax 913 345.0617

www.smithboucher.com 

 

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jonathan Bowser
Sent: Tuesday, January 04, 2011 1:55 PM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Building Shades

 

So I had a thought on using the DD wizard to introduce a building for shading purposes only, and I wanted to run it up the flag pole.

 

 

My thought was to model a building shell with an operation schedule (Wizard Screen 12 of 25) set to Closed and all of its Non-HVAC Enduses (15 of 25) toggled off.  Then create a new HVAC System with no cooling source, heating source or system type, and assign this system to the building shell’s zones.

 

 

At first glance, the simulation results come out to zero where I expect them to, but I’m not an ME, so I’m not sure if this shell would have any other impact other than shading if I were to throw this “dummy” setup in with the building I want to run the simulation against.  When I run a simulation with a single default shell/hvac system and one with a single default shell/hvac system along with the dummy setup described above, the results I’m checking against are pretty close which lends me to believe that maybe only the dummy’s shading is being taken into account.

 

Does anyone have any thoughts on this process?

 

-- Jon

 

 

 

Jonathan Bowser

Senior Software Engineer

Beck Technology 

1807 Ross Avenue, Suite 500

Dallas, TX 75201 

(214) 303-6815

www.beck-technology.com <http://www.beck-technology.com/> 

 

Innovation in All Dimensions

  

Please consider the environment before printing this e-mail 

  

This e-mail may be privileged and confidential. If you are not the intended recipient, please delete from all computers.

 

________________________________

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jonathan Bowser
Sent: Tuesday, January 04, 2011 10:09 AM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Building Shades

 

I appreciate everyone’s input and help with clarifying and showing this information.

 

-- Jon

 

 

 

Jonathan Bowser

Senior Software Engineer

Beck Technology 

1807 Ross Avenue, Suite 500

Dallas, TX 75201 

(214) 303-6815

www.beck-technology.com <http://www.beck-technology.com/> 

 

Innovation in All Dimensions

  

Please consider the environment before printing this e-mail 

  

This e-mail may be privileged and confidential. If you are not the intended recipient, please delete from all computers.

 

________________________________

From: Nick Caton [mailto:ncaton at smithboucher.com] 
Sent: Tuesday, January 04, 2011 9:09 AM
To: John T. Forester; Jonathan Bowser
Cc: equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Building Shades

 

To round out John’s thorough and detailed answer:  Yes, coming out of the wizards, multiple shells will shade each other if you do nothing else. The exterior surfaces of one shell will act like static, opaque building shades with respect to other shells.

 

The “Shading Surface – Yes/No” property for exterior surfaces John is pointing out is where you can confirm or edit that behavior (typically, when creating a 90.1 baseline model).  I find it easiest to select any exterior surface from the 3D view, switch to spreadsheet view, then drag the horizontal navigation bar all the way to the right to edit the column for this variable.

 

~Nick



 

NICK CATON, E.I.T.

PROJECT ENGINEER

Smith & Boucher Engineers

25501 west valley parkway

olathe ks 66061

direct 913 344.0036

fax 913 345.0617

www.smithboucher.com 

 

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of John T. Forester
Sent: Monday, January 03, 2011 2:48 PM
To: Jonathan Bowser
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Building Shades

 

If you are in the detailed edit mode and double-click on an exterior wall or roof and the second properties tab (Daylighting – Shading – Other) will show you if that surface is a shading surface or not.  You can alternatively review all of your external constructions in the spreadsheet view (also in detailed edit mode).  It is the last column in the spreadsheet.

 

Coming from the wizard, you can go into detailed edit mode and check to see how the construction in being handled then return to the wizard without losing anything as long as no changes are made in the detailed edit mode.  If you right click in the field and then choose Item Help, you can read about how eQuest handles this input variable.

 

 

 

John T. Forester, P.E., LEED AP, Mechanical Design Engineer I BVH Integrated Services I 617.658.9008 tel I 617.244.3753 fax I One Gateway Center Suite 506, Newton MA 02458 I www.bvhis.com I Hartford ● New Haven ● Boston

 

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Rob Hudson
Sent: Monday, January 03, 2011 3:34 PM
To: Jonathan Bowser
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Building Shades

 

that is my assumption as well.  i haven't truly modeled two separate buildings before for a project, but i did try a litmus test model once.
what i did was created two shells one north of the other and looked at the output reports for solar loads on the southern faces.  the northern one did have a smaller load on the southern face, which leads me to believe that this part of eQuest works just fine.  if anyone has an actual project that they can speak of then that would be a better answer, but for now this is what i got,

Rob

On Mon, Jan 3, 2011 at 3:31 PM, Jonathan Bowser <JonathanBowser at beck-technology.com> wrote:

Thanks for the quick response, Rob.  For my own sanity, could I have something else clarified as well?

 

I’ve always been under the assumption that if I model multiple shells in the wizard, the shading effects of the shells are taken into account when performing the analysis.  Is this actually the case?

 

 

Note: I understand this isn’t the same thing as creating a building shade in the detailed edit mode since I’m actually introducing more components into the analysis.

 

-- Jon

 

 

 

Jonathan Bowser

Senior Software Engineer

Beck Technology 

1807 Ross Avenue, Suite 500

Dallas, TX 75201 

(214) 303-6815

www.beck-technology.com <http://www.beck-technology.com/> 

 

Innovation in All Dimensions

  

Please consider the environment before printing this e-mail 

  

This e-mail may be privileged and confidential. If you are not the intended recipient, please delete from all computers.

 

________________________________

From: Rob Hudson [mailto:rdh4176 at gmail.com] 
Sent: Monday, January 03, 2011 2:24 PM
To: Jonathan Bowser
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Building Shades

 

You cannot do this through the wizards, it must be done in the detailed edit mode after the wizard has been completed.  shades are easy to inpliment as long as you have the information (size and orientation) of the surrounding buildings readily available.

hope this helps!

Rob

On Mon, Jan 3, 2011 at 3:19 PM, Jonathan Bowser <JonathanBowser at beck-technology.com> wrote:

After searching through the archive, I’ve learned I can create Building Shades in the detailed mode in eQUEST.  Is it possible to do something similar through one of the wizards?

 

Essentially I’d like a quick, easy way of modeling surrounding buildings so that their shading effects are taken into account.

 

-- Jon

 

 

Jonathan Bowser

Senior Software Engineer

Beck Technology 

1807 Ross Avenue, Suite 500

Dallas, TX 75201 

(214) 303-6815

www.beck-technology.com <http://www.beck-technology.com/> 

 

Innovation in All Dimensions

  

Please consider the environment before printing this e-mail 

  

This e-mail may be privileged and confidential. If you are not the intended recipient, please delete from all computers.

 


_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG




-- 
Rob Hudson


_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG




-- 
Rob Hudson

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110104/fcc6e853/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110104/fcc6e853/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 35051 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110104/fcc6e853/attachment-0001.jpeg>


More information about the Equest-users mailing list