[Equest-users] using IPLV in eQuest
    James Waechter 
    jamesw at McKinstry.com
       
    Fri Feb 25 08:55:29 PST 2011
    
    
  
John,
 
If the only parameter Rohini enters into the program is the full-load EIR – which he said is the same for both chillers – how will eQuest know to bend the curves differently for the two chiller options.  It is my understanding that program would use the same chiller efficiency curves for both machines even though their IPLVs are different.
 
In order to overcome this issue, are you saying Rohini should get chiller performance data from each of the manufacturers and enter his own custom curves?  I recall there was a discussion on that topic a few months back.
 
Regards,
James Waechter Jr., P.E., CEM, LEED A.P.
Energy Engineer – Rocky Mountain Region
p 303 215 4062 | m 727 686 3248
McKinstry
Consulting | Construction | Energy | Facility Services
www.mckinstry.com <http://www.mckinstry.com/>  
 
 
 
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of John Aulbach
Sent: Friday, February 25, 2011 9:41 AM
To: R B; eQUEST Users List
Subject: Re: [Equest-users] using IPLV in eQuest
 
Rohini:
 
Won't happen. IPLV is a number which has one equation and 4 unknowns. Actually, three unknowns as you know the 100% point. You need a manufacturer's curve run at 85F constant condenser water temperature. Let eQuest do the curve bending after that. ARI curve won't work right.
 
 
John R. Aulbach, PE, CEM
Senior Energy Engineer
________________________________
Partner Energy
1990 E. Grand Avenue, El Segundo, CA 90245
W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745
www.ptrenergy.com <http://www.ptrenergy.com/>  | jaulbach at ptrenergy.com <mailto:%7C%20jaulbach at ptrenergy.com> 
 
________________________________
From: R B <slv3sat at gmail.com>
To: eQUEST Users List <equest-users at lists.onebuilding.org>
Sent: Fri, February 25, 2011 7:25:18 AM
Subject: [Equest-users] using IPLV in eQuest
Hi All, 
I would like to compare two screw chillers with same full load kW/ton and different IPLV kW/ton. I am using the full load number for the EIR. Where can the IPLV number be used? Is there some way to scale the performance curves to reflect different IPLV's?
-Rohini
 
This email is the property of McKinstry or one of its affiliates and may contain confidential and/or privileged information. If you are not the intended recipient or have received this e-mail in error please notify the sender immediately and delete this e-mail. 
Any unauthorized copying, disclosure or distribution of the material in this e-mail is strictly forbidden.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110225/a3a0d4b1/attachment.htm>
    
    
More information about the Equest-users
mailing list