Rohini:
Won't happen. IPLV is a number which has one equation and 4 unknowns. Actually,
three unknowns as you know the 100% point. You need a manufacturer's curve run
at 85°F constant condenser water temperature. Let eQuest do the curve bending
after that. ARI curve won't work right.
John R. Aulbach, PE, CEM
Senior Energy Engineer
________________________________
PartnerEnergy
1990 E. Grand Avenue, El Segundo, CA 90245
W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745
www.ptrenergy.com| jaulbach at ptrenergy.com
________________________________
From: R B <slv3sat at gmail.com>
To: eQUEST Users List <equest-users at lists.onebuilding.org>
Sent: Fri, February 25, 2011 7:25:18 AM
Subject: [Equest-users] using IPLV in eQuest
Hi All,
I would like to compare two screw chillers with same full load kW/ton and
different IPLV kW/ton. I am using the full load number for the EIR. Where can
the IPLV number be used? Is there some way to scale the performance curves to
reflect different IPLV's?
-Rohini