[Equest-users] HVAC type for Exhaust Fans on parking lots

Nick Caton ncaton at smithboucher.com
Fri Feb 11 07:27:34 PST 2011


As an extra suggestion, you can take the approach Bill is describing but
instead define the ventilation systems as a direct load on a sub-meter
to your default electric meter.  The advantage to this extra step is you
can reference report PS-B to more easily document the garage ventilation
system demand/consumption on the EAp2 template as a process load
separate from your other "misc. equip" loads, the same way elevators get
a separate line.  My last reviewer demanded this be broken out
separately.

 

Attached discussion describes the suggestion more thoroughly.

 

To my knowledge nobody has yet put forth a "standard" or "baseline"
schedule to use for garage ventilation, so I've always resolved to model
them identically thus far.  

 

>From discussions with various others, I understand CO/CO2-sensored
systems don't operate terribly often, even in busy garages.  I suspect
the predominance of modern catalytic converters (fewer cars from the
70's and earlier are driven daily) has a lot to do with the ppm values
not getting approached.

 

~Nick

 

 

 

NICK CATON, E.I.T.

PROJECT ENGINEER

Smith & Boucher Engineers

25501 west valley parkway

olathe ks 66061

direct 913 344.0036

fax 913 345.0617

www.smithboucher.com 

 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bishop,
Bill
Sent: Thursday, February 10, 2011 8:25 AM
To: Claudia De Paula; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] HVAC type for Exhaust Fans on parking lots

 

Claudia,

 

If you are doing a LEED/Appendix G model, I suggest modeling it as a
process load (Direct Loads - Interior), with the load equal to the fan
power and with a schedule that approximates when the fan will run based
on CO2. The load and schedule should be identical between your baseline
and proposed unless you can justify it through an exceptional
calculation. See Dakota Kelley's email, attached.

 

Regards,

Bill

 

William Bishop, PE, BEMP, LEED(r) AP | Pathfinder Engineers & Architects
LLP

Mechanical Engineer

 

 134 South Fitzhugh Street                 Rochester, NY 14608
T: (585) 325-6004 Ext. 114                F: (585) 325-6005

wbishop at pathfinder-ea.com           www.pathfinder-ea.com
<http://www.pathfinder-ea.com/> 

P   Sustainability - the forest AND the trees. P 

________________________________

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Claudia
De Paula
Sent: Thursday, February 10, 2011 2:48 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] HVAC type for Exhaust Fans on parking lots

 

A non-conditioned underground parking lot has exhaust fans with VSD
which work according to CO2 levels.

How do I define this type of HVAC system?

 

Thanks

Claudia

 

 

________________________________

IMPORTANT: The contents of this email and any attachments are
confidential. They are intended for the named recipient(s) only.
If you have received this email in error, please notify the system
manager or the sender immediately and do not disclose the contents to
anyone or make copies thereof.
*** eSafe scanned this email for viruses, vandals, and malicious
content. *** 

________________________________

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110211/2d50ee6e/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110211/2d50ee6e/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2412 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110211/2d50ee6e/attachment-0001.jpeg>
-------------- next part --------------
An embedded message was scrubbed...
From: "Nick Caton" <ncaton at smithboucher.com>
Subject: Re: [Equest-users] Cooking Equipment and Elevators/ Exhaust fans
Date: Mon, 24 Jan 2011 16:44:23 -0600
Size: 55419
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110211/2d50ee6e/attachment.eml>


More information about the Equest-users mailing list