[Equest-users] HVAC type for Exhaust Fans on parking lots
Bishop, Bill
wbishop at pathfinder-ea.com
Thu Feb 10 06:24:41 PST 2011
Claudia,
If you are doing a LEED/Appendix G model, I suggest modeling it as a
process load (Direct Loads - Interior), with the load equal to the fan
power and with a schedule that approximates when the fan will run based
on CO2. The load and schedule should be identical between your baseline
and proposed unless you can justify it through an exceptional
calculation. See Dakota Kelley's email, attached.
Regards,
Bill
William Bishop, PE, BEMP, LEED(r) AP | Pathfinder Engineers & Architects
LLP
Mechanical Engineer
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 325-6004 Ext. 114 F: (585) 325-6005
wbishop at pathfinder-ea.com www.pathfinder-ea.com
<http://www.pathfinder-ea.com/>
P Sustainability - the forest AND the trees. P
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Claudia
De Paula
Sent: Thursday, February 10, 2011 2:48 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] HVAC type for Exhaust Fans on parking lots
A non-conditioned underground parking lot has exhaust fans with VSD
which work according to CO2 levels.
How do I define this type of HVAC system?
Thanks
Claudia
________________________________
IMPORTANT: The contents of this email and any attachments are
confidential. They are intended for the named recipient(s) only.
If you have received this email in error, please notify the system
manager or the sender immediately and do not disclose the contents to
anyone or make copies thereof.
*** eSafe scanned this email for viruses, vandals, and malicious
content. ***
________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110210/8829f486/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2412 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110210/8829f486/attachment.jpeg>
-------------- next part --------------
An embedded message was scrubbed...
From: "Dakota Kelley" <dakotak at teliospc.com>
Subject: Re: [Equest-users] Different operation schedules forventilationsystem
Date: Wed, 13 Oct 2010 11:12:40 -0500
Size: 32737
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110210/8829f486/attachment.eml>
More information about the Equest-users
mailing list