[Equest-users] Where to find summary of overridden defaults etc.
Carol Gardner
cmg750 at gmail.com
Wed Apr 20 13:44:52 PDT 2011
You're probably getting at the nature of the reviewer's comment better than
I did, Nick. I read "over-sizing" rather that "auto-sizing" because I had
just read that section in the User's Manual.
So basically we are doing auto-sizing but we call it "sizing runs" which we
use to input the pertinent data into the baseline, e.g. kW/cfm, cooling coil
size, heating coil size and/or cfm, or some combination of output from our
sizing runs.
On Wed, Apr 20, 2011 at 1:32 PM, Nick Caton <ncaton at smithboucher.com> wrote:
> In brief, I do what Carol’s describing. I haven’t read up on what the
> user’s manual might say about “manual oversizing,” but all my baseline
> system capacities are auto-sized using the same heating/cooling capacity
> factors described… I’ve yet to encounter any opposition from my reviewers
> using this approach.
>
>
>
> For clarification and in contrast: baseline system efficiencies and fan
> energies are not auto-sized, but rather separately calculated and entered by
> hand, working from the auto-sized heating/cooling/airflow capacities derived
> from a sizing run.
>
>
>
> If after a sizing run, incrementally adjusting heating/cooling capacities
> were necessary to correct unmet hours (though I haven’t run into that case
> for a long while – when it comes up it’s usually resolved checking/fixing
> other items), I suppose I would intuitively adjust the 1.15/1.25 factors a
> bit at a time until the numbers worked out, then proceed with the efficiency
> & fan calcs.
>
>
>
> As to a “manual” capacity oversizing approach: It’s news to me…
>
>
>
> ~Nick
>
>
>
> [image: cid:489575314 at 22072009-0ABB]**
>
> * *
>
> *NICK CATON, E.I.T.***
>
> PROJECT ENGINEER
>
> Smith & Boucher Engineers
>
> 25501 west valley parkway
>
> olathe ks 66061
>
> direct 913 344.0036
>
> fax 913 345.0617
>
> www.smithboucher.com* *
>
>
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Carol Gardner
> *Sent:* Wednesday, April 20, 2011 3:00 PM
> *To:* Mark Darrall
> *Cc:* equest-users at lists.onebuilding.org
>
> *Subject:* Re: [Equest-users] Where to find summary of overridden defaults
> etc.
>
>
>
> Just a couple of comments, Mark. If a default was overridden, it would be
> you who did it so you would know what you overrode it with. If I am
> misunderstanding and you just couldn't see what the default was you can view
> it, usually by right clicking on the input box.
>
> I am curious why the reviewer asked that autosizing not be done for the
> baseline. I was reading my Std 90 2004 User's guide this morning and was
> kind of surprised that in it they more or less suggest you need to oversize
> by hand. I'm not sure why. I know that you need to be careful where you put
> the 15% and 25% sizing increases in eQUEST but it's relatively easy to get
> them in the right spot.
>
> As a check let me know what you think of my methodology. I set the system
> sizing ratio on the first screen of the Air-Side HVAC System to 1.0, and
> then set the Cool Size Ratio to 1.15 on the first screen under the Cooling
> tab, and the Heat Size Ratio to 1.25 of the first screen under the Heating
> tab. Is this what others do?
>
> Carol
>
> On Wed, Apr 20, 2011 at 11:15 AM, Mark Darrall <MDarrall at a2so4.com> wrote:
>
> Thanks, everyone!
>
>
>
> Don’t forget, too, that the Appendix G requirements don’t always jive with
> default eQ values. Also, my reviewer has asked that autosizing not be done
> for baseline, which probably meant more overrides…
>
>
>
> I appreciate the tip on searching the .inp file. Thanks!
>
>
>
> MARK DARRALL, AIA, LEED AP BD+C, NCARB
> Senior Project Manager
>
>
>
> [image: a2so4-email]
>
>
>
> DESIGN ENRICHING LIFE // LIFE ENRICHING DESIGN
>
>
>
> A2SO4 Architecture, LLC
>
> Union Station
> 300 South Meridian Street / 250
> Indianapolis, Indiana 46225
> TEL 317 388 8850
>
> FAX 317 280 0692
>
> MOB 765 749 0841
> www.a2so4.com
>
>
>
> *Please consider the environment before printing this e-mail*.
>
>
>
> CONFIDENTIALITY NOTICE: This email and any files transmitted with it are
> confidential and intended solely for the use of the individual or entity to
> which they are addressed. If you are not the intended recipient, you may not
> review, copy or distribute this message. If you have received this email in
> error, please notify the sender immediately and delete the original message.
> Neither the sender nor the company for which he or she works accepts any
> liability for any damage caused by any virus transmitted by this email.
>
>
>
> *From:* R B [mailto:slv3sat at gmail.com]
> *Sent:* Wednesday, April 20, 2011 1:12 PM
> *To:* Nick Caton
> *Cc:* Mark Darrall; equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] Where to find summary of overridden defaults
> etc.
>
>
>
> If in the baseline (and may be the proposed case), I have made changes from
> the auto-sizing (and from the proposed design) to reduce the unmet hours, I
> count that as default over-ridden. This is usually a small number (less than
> 5 if I remember correctly).
>
> On Wed, Apr 20, 2011 at 11:36 AM, Nick Caton <ncaton at smithboucher.com>
> wrote:
>
> Hi Mark,
>
>
>
> For eQuest, I don’t believe there is any reasonable way to tally “default
> overrides.” For LEED submittals, I typically enter zeroes at the
> corresponding template queries, and that’s what I’ve suggested to others for
> initial submittals. I’ve heard others enter “9999” in all fields without
> comment, but 0 seems less conspicuous to me =).
>
>
>
> There’s further discussion on this topic in the archives –
> bookmark/favorite these links if you haven’t already:
>
> http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/
>
> http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/
>
>
>
> If a reviewer were to push me to come up with a figure without any specific
> guidance after an initial submittal, I suppose I would paste the .inp file
> into a word document, ctrl+f for instances of the text “..” without quotes,
> and explain that number represents an estimate of the number of non-library
> entries in the project (screengrab):
>
> *Error! Filename not specified.*
>
> I would probably wonder about the reviewer somewhere along the way too...
> Anyone familiar with eQuest and LEED knows there’s no way to finish a
> 90.1-based model without a horde of non-default entries… I’m having
> difficulty guessing at how this figure could help an eQuest model reviewer
> do their job properly. Perhaps it’s specific to other software packages…
> Thoughts anyone?
>
>
>
> To be clear, I’d sooner advise just entering 0’s in lieu of jumping through
> any unnecessary hoops.
>
>
>
> ~Nick
>
>
>
> *Error! Filename not specified.*
>
> * *
>
> *NICK CATON, E.I.T.*
>
> PROJECT ENGINEER
>
> Smith & Boucher Engineers
>
> 25501 west valley parkway
>
> olathe ks 66061
>
> direct 913 344.0036
>
> fax 913 345.0617
>
> www.smithboucher.com* *
>
>
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Mark Darrall
> *Sent:* Wednesday, April 20, 2011 10:11 AM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] Where to find summary of overridden defaults
> etc.
>
>
>
> Hi,
>
>
>
> I know that when a run has issues, it creates an ATTN report with the
> warnings listed. But how can I find out how many default values have been
> overridden without going through every screen and counting them?
>
>
>
> Thanks, all!
>
>
>
> MARK DARRALL, AIA, LEED AP BD+C, NCARB
> Senior Project Manager
>
>
>
> *Error! Filename not specified.*
>
>
>
> DESIGN ENRICHING LIFE // LIFE ENRICHING DESIGN
>
>
>
> A2SO4 Architecture, LLC
>
> Union Station
> 300 South Meridian Street / 250
> Indianapolis, Indiana 46225
> TEL 317 388 8850
>
> FAX 317 280 0692
>
> MOB 765 749 0841
> www.a2so4.com
>
>
>
> *Please consider the environment before printing this e-mail*.
>
>
>
> CONFIDENTIALITY NOTICE: This email and any files transmitted with it are
> confidential and intended solely for the use of the individual or entity to
> which they are addressed. If you are not the intended recipient, you may not
> review, copy or distribute this message. If you have received this email in
> error, please notify the sender immediately and delete the original message.
> Neither the sender nor the company for which he or she works accepts any
> liability for any damage caused by any virus transmitted by this email.
>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
>
> --
> Carol Gardner PE
>
--
Carol Gardner PE
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110420/cb216415/attachment.htm>
More information about the Equest-users
mailing list