[Equest-users] OA hourly data
Paul Diglio
paul.diglio at sbcglobal.net
Tue Apr 19 10:24:57 PDT 2011
Rohini:
Since there is no such thing as a damper that does not have a leakage value,
perhaps eQuest is factoring that in. Can you just remove the economizers?
Paul Diglio
________________________________
From: R B <slv3sat at gmail.com>
To: eQUEST Users List <equest-users at lists.onebuilding.org>
Sent: Tue, April 19, 2011 12:40:08 PM
Subject: Re: [Equest-users] OA hourly data
Kamel, Bill,
Thanks for the reply. I changed the OA cfm for all the zones to 0. Now in the
SV-A report the zone OA is showing as zero but the system OA ratio is 0.2 and
the custom hourly report variables (ratio of outside air to supply flow - Var
39, and the minimum OA damper position - Var 80) are still varying from 0.21 to
0.56. Not sure from where eQuest is getting 0.2 value or these other values in
the hourly report.
Does VAV have a default minimum outside air that cannot be overwritten?
Thanks
-Rohini
On Tue, Apr 19, 2011 at 10:16 AM, Haddad, Kamel <Kamel.Haddad at nrcan-rncan.gc.ca>
wrote:
Rohini, Try setting all the zone level outside air fields to the smallest
number you can enter.
>
>Kamel Haddad
>
>
>
________________________________
>From: equest-users-bounces at lists.onebuilding.org
>[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of R B
>Sent: April 19, 2011 10:21
>
>To: eQUEST Users List
>Subject: [Equest-users] OA hourly data
>
>
>
>Hello all:
>I am trying to simulate zero outside air. I set the min OA on the systems tab
>to zero, economizer to fixed fraction, there are no OA numbers at the zone
>level. I would assume this will give me zero OA but when I look at the hourly
>variables (ratio of outside air to supply flow - Var 39, and the minimum OA
>damper position - Var 80) they vary from 0.21 to 0.56.
>
>What am I missing? Any pointers helpful.
>-Rohini
>