<html><head><style type="text/css"><!-- DIV {margin:0px;} --></style></head><body><div style="font-family:times new roman,new york,times,serif;font-size:10pt">Rohini:<br><br>Since there is no such thing as a damper that does not have a leakage value, perhaps eQuest is factoring that in. Can you just remove the economizers?<br><br>Paul Diglio<br><div><br></div><div style="font-family: times new roman,new york,times,serif; font-size: 10pt;"><br><div style="font-family: times new roman,new york,times,serif; font-size: 12pt;"><font face="Tahoma" size="2"><hr size="1"><b><span style="font-weight: bold;">From:</span></b> R B <slv3sat@gmail.com><br><b><span style="font-weight: bold;">To:</span></b> eQUEST Users List <equest-users@lists.onebuilding.org><br><b><span style="font-weight: bold;">Sent:</span></b> Tue, April 19, 2011 12:40:08 PM<br><b><span style="font-weight: bold;">Subject:</span></b> Re: [Equest-users] OA hourly data<br></font><br>
<div><font face="tahoma,sans-serif">Kamel, Bill,</font></div><div><font face="tahoma,sans-serif">Thanks for the reply. I changed the OA cfm for all the zones to 0. Now in the SV-A report the zone OA is showing as zero but the system OA ratio is 0.2 and the custom hourly report variables (ratio of outside air to supply flow - Var 39, and the minimum OA damper position - Var 80) are still varying from 0.21 to 0.56. Not sure from where eQuest is getting 0.2 value or these other values in the hourly report.</font></div>
<div><font face="tahoma,sans-serif">Does VAV have a default minimum outside air that cannot be overwritten?</font></div><div> </div><div>Thanks</div><div>-Rohini<br><br></div><div class="gmail_quote">On Tue, Apr 19, 2011 at 10:16 AM, Haddad, Kamel <span dir="ltr"><<a rel="nofollow" ymailto="mailto:Kamel.Haddad@nrcan-rncan.gc.ca" target="_blank" href="mailto:Kamel.Haddad@nrcan-rncan.gc.ca">Kamel.Haddad@nrcan-rncan.gc.ca</a>></span> wrote:<br>
<blockquote style="margin: 0px 0px 0px 0.8ex; padding-left: 1ex; border-left: 1px solid rgb(204, 204, 204);" class="gmail_quote">
<div>
<div dir="ltr" align="left"><span><font color="#0000ff" face="Arial">Rohini, Try setting all the zone level outside air fields
to the smallest number you can enter.</font></span></div>
<div dir="ltr" align="left"><span><font color="#0000ff" face="Arial"></font></span> </div>
<div dir="ltr" align="left"><span><font color="#0000ff" face="Arial">Kamel Haddad</font></span></div>
<div dir="ltr" align="left" lang="en-us"><span><font color="#0000ff" face="Arial"> </font></span></div>
<div dir="ltr" align="left" lang="en-us"><span> </span></div>
<div dir="ltr" align="left" lang="en-us">
<hr>
</div>
<div dir="ltr" align="left" lang="en-us"><font face="Tahoma"><div class="im"><b>From:</b> <a rel="nofollow" ymailto="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank" href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a>
[mailto:<a rel="nofollow" ymailto="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank" href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>R
B<br></div><b>Sent:</b> April 19, 2011 10:21<div class="im"><br><b>To:</b> eQUEST Users
List<br><b>Subject:</b> [Equest-users] OA hourly data<br></div></font><br></div><div><div></div><div class="h5">
<div></div>
<div><br clear="all"><font face="trebuchet ms,sans-serif">Hello all:</font></div>
<div><font face="trebuchet ms,sans-serif">I am trying to simulate zero outside
air. I set the min OA on the systems tab to zero, economizer to fixed fraction,
there are no OA numbers at the zone level. I would assume this will give me zero
OA but when I look at the hourly variables (ratio of outside air to supply flow
- Var 39, and the minimum OA damper position - Var 80) they vary from 0.21
to 0.56. </font></div>
<div><font face="Trebuchet MS">What am I missing? Any pointers
helpful.</font></div>
<div><font face="Trebuchet MS">-Rohini</font><br></div></div></div></div>