[Equest-users] Difference between wizard and detailed mode
Carol Gardner
cmg750 at gmail.com
Wed Apr 13 14:27:44 PDT 2011
Why not just do it detailed edit? It's pretty easy to do there so I'm
wondering if you have a reason I am not thinking about for going back into
the wizards.
Carol
On Wed, Apr 13, 2011 at 2:21 PM, Nick Caton <ncaton at smithboucher.com> wrote:
> Hey Travis,
>
>
>
> What you’ve currently got is:
>
> - A 60ton unit for each floor’s core zone (2 total)
>
> - A series of 5 and 7.5 ton units each serving one perimeter zone
> (8 total) ß note: cooling capacities appear to have been edited after the
> wizards
>
> - Total units: 10
>
> - Picture:
>
>
>
> It sounds like the desired is to have:
>
> - A 60ton unit for each floor’s core zone (2 total)
>
> - 15 ton units each serving two perimeter zones (4 total)
>
> - Total units: 6
>
>
>
> To pull this off you need to
>
> 1. Go back to wizards
>
> 2. Review/Correct the tonnage for the smaller units, as necessary
> (wizard inputs don’t reflect 15 tons all around)
>
> 3. Select “system per site” in the first screen of each system
> (note: you’ve got “system per zone” selected currently, which assigns one
> system of the specified sort to each zone in the shell associated… this is
> the main source of your system quantity issue).
>
> 4. Assign the perimeter zones to the appropriate systems (looks
> like you’ve already done this correctly, but review to be sure assignments
> are correct).
>
>
>
> When finished and on exiting the DD wizard, you should observe the correct
> quantity of systems and zone assignments on review of the airside HVAC
> tab/component tree.
>
>
>
> Best of luck!
>
>
>
> ~Nick
>
>
>
> [image: cid:489575314 at 22072009-0ABB]**
>
> * *
>
> *NICK CATON, E.I.T.***
>
> PROJECT ENGINEER
>
> Smith & Boucher Engineers
>
> 25501 west valley parkway
>
> olathe ks 66061
>
> direct 913 344.0036
>
> fax 913 345.0617
>
> www.smithboucher.com* *
>
>
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Travis Rhodes
> *Sent:* Wednesday, April 13, 2011 12:08 PM
> *To:* equest-users at lists.onebuilding.org
>
> *Subject:* Re: [Equest-users] Difference between wizard and detailed mode
>
>
>
> Thanks
>
>
>
> Travis Rhodes
>
> ENERGY ADVISOR
>
> (916)732-5274
>
> trhodes at smud.org
>
>
>
> *From:* Carol Gardner [mailto:cmg750 at gmail.com]
> *Sent:* Wednesday, April 13, 2011 10:05 AM
> *To:* Travis Rhodes
> *Cc:* equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] Difference between wizard and detailed mode
>
>
>
> Hi Travis,
>
> You need to attach the .inp file that this .pd2 file uses, too.
>
> Carol
>
> On Wed, Apr 13, 2011 at 9:56 AM, Travis Rhodes <TRhodes at smud.org> wrote:
>
> I’m trying to set up a really simple 2 story building with 6 rooftop units.
> Two 60 tons supply cooling only to the core of the two floors and the 4 15
> ton units take care of the perimeter. One unit supplies air to two walls on
> the first floor and another unit takes the other two walls on that floor.
> This is repeated on the second floor. In the wizard I set it up exactly like
> this and inputted the performance data for each unit and named each unit but
> when I go to detailed mode to modify the schedules to reflect the controls
> of the system it has broken everything out completely different than what I
> assumed I had set up in the wizard. I’ve attached the .pd2 file, I don’t
> know if this is sufficient for anyone to look at what I’ve done.
>
>
>
> I appreciate anyone help on this.
>
>
>
> Error! Filename not specified.
>
> * *
>
> * *
>
> * *
>
> * *
>
> * *
>
> * *
>
> * *
>
> * *
>
> * *
>
> * *
>
> * *
>
> * *
>
> * *
>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
>
> --
> Carol Gardner PE
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
--
Carol Gardner PE
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110413/e8265543/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 17443 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110413/e8265543/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110413/e8265543/attachment.jpeg>
More information about the Equest-users
mailing list