Why not just do it detailed edit? It's pretty easy to do there so I'm wondering if you have a reason I am not thinking about for going back into the wizards.<br><br>Carol<br><br><div class="gmail_quote">On Wed, Apr 13, 2011 at 2:21 PM, Nick Caton <span dir="ltr"><<a href="mailto:ncaton@smithboucher.com">ncaton@smithboucher.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex;">
<div link="blue" vlink="purple" lang="EN-US">
<div>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">Hey Travis,</span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">What you’ve currently got is:</span></p>
<p><span style="font-size:11.0pt;color:#1F497D"><span>-<span style="font:7.0pt "Times New Roman"">
</span></span></span><span style="font-size:11.0pt;color:#1F497D">A 60ton unit for each floor’s core zone (2 total)</span></p>
<p><span style="font-size:11.0pt;color:#1F497D"><span>-<span style="font:7.0pt "Times New Roman"">
</span></span></span><span style="font-size:11.0pt;color:#1F497D">A series of 5 and 7.5 ton units each serving one perimeter zone
(8 total) </span><span style="font-size:11.0pt;font-family:Wingdings;color:#1F497D">ß</span><span style="font-size:11.0pt;color:#1F497D"> note: cooling capacities appear to have been edited after the
wizards</span></p>
<p><span style="font-size:11.0pt;color:#1F497D"><span>-<span style="font:7.0pt "Times New Roman"">
</span></span></span><span style="font-size:11.0pt;color:#1F497D">Total units: 10</span></p>
<p><span style="font-size:11.0pt;color:#1F497D"><span>-<span style="font:7.0pt "Times New Roman"">
</span></span></span><span style="font-size:11.0pt;color:#1F497D">Picture:</span></p>
<p class="MsoNormal"><img src="cid:image002.png@01CBF9F6.DAA887A0" height="370" width="616"><span style="font-size:11.0pt;color:#1F497D"></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">It sounds like the desired is to have:</span></p>
<p><span style="font-size:11.0pt;color:#1F497D"><span>-<span style="font:7.0pt "Times New Roman"">
</span></span></span><span style="font-size:11.0pt;color:#1F497D">A 60ton unit for each floor’s core zone (2 total)</span></p>
<p><span style="font-size:11.0pt;color:#1F497D"><span>-<span style="font:7.0pt "Times New Roman"">
</span></span></span><span style="font-size:11.0pt;color:#1F497D">15 ton units each serving two perimeter zones (4 total)</span></p>
<p><span style="font-size:11.0pt;color:#1F497D"><span>-<span style="font:7.0pt "Times New Roman"">
</span></span></span><span style="font-size:11.0pt;color:#1F497D">Total units: 6</span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">To pull this off you need to</span></p>
<p><span style="font-size:11.0pt;color:#1F497D"><span>1.<span style="font:7.0pt "Times New Roman"">
</span></span></span><span style="font-size:11.0pt;color:#1F497D">Go back to wizards</span></p>
<p><span style="font-size:11.0pt;color:#1F497D"><span>2.<span style="font:7.0pt "Times New Roman"">
</span></span></span><span style="font-size:11.0pt;color:#1F497D">Review/Correct the tonnage for the smaller units, as necessary
(wizard inputs don’t reflect 15 tons all around)</span></p>
<p><span style="font-size:11.0pt;color:#1F497D"><span>3.<span style="font:7.0pt "Times New Roman"">
</span></span></span><span style="font-size:11.0pt;color:#1F497D">Select “system per site” in the first screen of each
system (note: you’ve got “system per zone” selected
currently, which assigns one system of the specified sort to each zone in the
shell associated… this is the main source of your system quantity issue).</span></p>
<p><span style="font-size:11.0pt;color:#1F497D"><span>4.<span style="font:7.0pt "Times New Roman"">
</span></span></span><span style="font-size:11.0pt;color:#1F497D">Assign the perimeter zones to the appropriate systems (looks
like you’ve already done this correctly, but review to be sure
assignments are correct).</span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">When finished and on exiting the DD wizard, you should observe
the correct quantity of systems and zone assignments on review of the airside
HVAC tab/component tree.</span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">Best of luck!</span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">~Nick</span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<div>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"><img src="cid:image001.jpg@01CBF9F4.1E135130" alt="cid:489575314@22072009-0ABB" height="37" width="119"></span><b><span style="font-size:11.0pt;color:#2D4D5E"></span></b></p>
<p class="MsoNormal"><b><span style="font-size:11.0pt;color:#2D4D5E"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size:11.0pt;color:#2D4D5E">NICK CATON, E.I.T.</span></b><b><span style="color:#2D4D5E"></span></b></p>
<p class="MsoNormal"><span style="font-size:7.5pt;color:#CC9900">PROJECT ENGINEER</span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;color:#2D4D5E">Smith & Boucher Engineers</span><span style="font-size:7.5pt;color:#CC9900"></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;color:#2D4D5E">25501 west valley parkway</span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;color:#2D4D5E">olathe ks 66061</span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;color:#2D4D5E">direct <a href="tel:913%20344.0036" value="+19133440036" target="_blank">913 344.0036</a></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;color:#2D4D5E">fax <a href="tel:913%20345.0617" value="+19133450617" target="_blank">913 345.0617</a></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"><a href="http://www.smithboucher.com" title="blocked::www.smithboucher.com" target="_blank"><span style="font-size:10.0pt">www.smithboucher.com</span></a></span><u><span style="font-size:10.0pt;color:blue"> </span></u><span style="font-size:11.0pt;color:#1F497D"></span></p>
</div>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<div>
<div style="border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b><span style="font-size:10.0pt">From:</span></b><span style="font-size:10.0pt">
<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>
[mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Travis
Rhodes<br>
<b>Sent:</b> Wednesday, April 13, 2011 12:08 PM<br>
<b>To:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a></span></p><div class="im"><br>
<b>Subject:</b> Re: [Equest-users] Difference between wizard and detailed mode</div><p></p>
</div>
</div><div class="im">
<p class="MsoNormal"> </p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">Thanks</span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Copperplate Gothic Light";color:#1F497D">Travis Rhodes</span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">ENERGY ADVISOR</span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"><a href="tel:%28916%29732-5274" value="+19167325274" target="_blank">(916)732-5274</a></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"><a href="mailto:trhodes@smud.org" target="_blank">trhodes@smud.org</a></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<div style="border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b><span style="font-size:10.0pt">From:</span></b><span style="font-size:10.0pt"> Carol Gardner
[mailto:<a href="mailto:cmg750@gmail.com" target="_blank">cmg750@gmail.com</a>] <br>
<b>Sent:</b> Wednesday, April 13, 2011 10:05 AM<br>
<b>To:</b> Travis Rhodes<br>
<b>Cc:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Equest-users] Difference between wizard and detailed mode</span></p>
</div>
<p class="MsoNormal"> </p>
<p class="MsoNormal" style="margin-bottom:12.0pt">Hi Travis,<br>
<br>
You need to attach the .inp file that this .pd2 file uses, too.<br>
<br>
Carol</p>
<div>
<p class="MsoNormal">On Wed, Apr 13, 2011 at 9:56 AM, Travis Rhodes <<a href="mailto:TRhodes@smud.org" target="_blank">TRhodes@smud.org</a>> wrote:</p>
<div>
<div>
<p class="MsoNormal">I’m
trying to set up a really simple 2 story building with 6 rooftop units. Two 60
tons supply cooling only to the core of the two floors and the 4 15 ton units
take care of the perimeter. One unit supplies air to two walls on the first
floor and another unit takes the other two walls on that floor. This is
repeated on the second floor. In the wizard I set it up exactly like this and
inputted the performance data for each unit and named each unit but when I go
to detailed mode to modify the schedules to reflect the controls of the system
it has broken everything out completely different than what I assumed I had set
up in the wizard. I’ve attached the .pd2 file, I don’t know if this
is sufficient for anyone to look at what I’ve done.</p>
<p class="MsoNormal"> </p>
<p class="MsoNormal">I
appreciate anyone help on this. </p>
<p class="MsoNormal"> </p>
<p class="MsoNormal"><span style="font-size:10.0pt">Error! Filename not specified.</span></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"> </span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt"> </span></b></p>
<p class="MsoNormal"> </p>
</div>
</div>
<p class="MsoNormal" style="margin-bottom:12.0pt"><br>
_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a></p>
</div>
<p class="MsoNormal"><br>
<br clear="all">
<br>
-- <br>
Carol Gardner PE</p>
</div></div>
</div>
<br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br><br clear="all"><br>-- <br>Carol Gardner PE<br>
<div style="visibility: hidden; left: -5000px;" id="avg_ls_inline_popup"></div><style type="text/css">#avg_ls_inline_popup{position: absolute;z-index: 9999;padding: 0px 0px;margin-left: 0px;margin-top: 0px;overflow: hidden;word-wrap: break-word;color: black;font-size: 10px;text-align: left;line-height: 130%;}</style>