[Equest-users] (no subject)
Carol Gardner
cmg750 at gmail.com
Tue Oct 19 13:34:18 PDT 2010
I can't believe that this model can be done without modeling each exposure
as required by App G. You need to model at least the 4 exposures per floor
unless you are modeling a teeny building, which this is not. Then the donut
hole problem goes away. On the subject of donut holes, I'd avoid them
because when you put 2 vetices "close" you create a series of errors, e.g.
exterior walls that should be interior walls, etc. Not worth it.
Carol
On Tue, Oct 19, 2010 at 9:19 AM, Nick Caton <ncaton at smithboucher.com> wrote:
> I’d like to echo and add to Andrew’s illustration:
>
>
>
> I’ve used this approach often to make wraparound zones/shells in the past.
>
>
>
>
> Something to note is that Andrew has a vertex highlighted in the screenshot
> below which I learned can be a time-saver, so is important to think about
> when preparing your CAD reference. Try to make a point to define a vertex
> at each corner of the “donut hole,” even if you don’t need to to make the
> shape. This will create a separate partition/exterior wall where the two
> “face-to-face” partitions exist, so that you can easily modify (or delete)
> them later in detailed as may be necessary.
>
>
>
> ~Nick
>
> [image: cid:489575314 at 22072009-0ABB]**
>
> * *
>
> *NICK CATON, E.I.T.***
>
> PROJECT ENGINEER
>
> 25501 west valley parkway
>
> olathe ks 66061
>
> direct 913 344.0036
>
> fax 913 345.0617
>
> *Check out our new web-site @ *www.smithboucher.com* *
>
>
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Reilman, Andrew
> *Sent:* Tuesday, October 19, 2010 10:44 AM
> *To:* Eddie Corwin; equest-users at lists.onebuilding.org
>
> *Subject:* Re: [Equest-users] (no subject)
>
>
>
> You can fake a donut zone though. The vertices just need to be "close".
> The picture I attached shows this a little exaggerated.
>
>
>
>
>
> Regards,
>
> *Andrew Reilman, P.E.
> **Associate*
> *Senior Engineer,** *LEED® AP BD+C
> *Syska Hennessy Group, Inc.*
> A member company of SH Group, Inc.**
>
> [image: http://www.syska.com/images/LOGOS/SyskaLogo_transp.gif]
>
> 11500 W. Olympic Blvd.,
> Suite 680
> Los Angeles, CA 90064
> Tel: 310.254.3894
> Cell: 510-710-4817
> Fax: 310.473.7468
> Email: areilman at syska.com
> http://www.syska.com
>
> [image: http://www.syska.com/images/grnsig.gif]Please consider the
> environment before printing this e-mail
> ------------------------------
>
> This email and any files transmitted with it are the property of SH Group,
> Inc. and are intended solely for the use of the individual or entity to
> which they are addressed. The information contained herein may include trade
> secrets or privileged or otherwise confidential information and unauthorized
> review, forwarding, printing, distributing, or using such information is
> strictly prohibited and may be unlawful. If you received this message in
> error, or have reason to believe you are not authorized to receive it,
> please promptly delete this message and notify the sender by e-mail.
> ------------------------------
>
>
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Eddie Corwin
> *Sent:* Tuesday, October 19, 2010 8:28 AM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] (no subject)
>
>
>
> You can not make a "Doughnut" zone. you will need to separate the
> perimeter zone into two or more zones. Using the "Core/Shell Zoning pattern
> that is available in the wizard works well.
>
>
>
>
> ------------------------------
>
> *From:* Erik Weiss <ew0187 at gmail.com>
> *To:* equest-users at lists.onebuilding.org
> *Sent:* Tue, October 19, 2010 11:22:08 AM
> *Subject:* [Equest-users] (no subject)
>
> I am creating a 20 floor building and the core is defined. i am trying to
> create the zones within the core and the large single zone surrounding the
> core. I am unable to create 1 single zone surrounding the core because the
> wizard does not allow you to select the same vertex twice in a single zone.
> Is there anyway around this
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
--
Carol Gardner PE
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101019/0a2f71f0/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 2443 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101019/0a2f71f0/attachment.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101019/0a2f71f0/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 19198 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101019/0a2f71f0/attachment-0001.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 91 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101019/0a2f71f0/attachment-0001.gif>
More information about the Equest-users
mailing list