The photos are a little blurry, but it looks like you have 5 of  your
zones each getting a "system 2" and the rest are getting a "system 1."
Can't tell which is which from these screenshots...  Before proceeding
far past the wizards, I'd suggest re-considering following what I first
suggested:  Don't define a separate system for your DOA system in the
wizards - you'll account for it in the detailed mode.
 
Also ask yourself whether the quantity of systems matches what you're
expecting - effectively a separate heat pump furnace for each perimeter
zone, and one large one for the core.  That may be exactly what you're
intending, but only you know what you want to model.
 
That said, take a moment to double click the systems in that component
tree in your last screenshot.  That's where the tabs I'm  talking about
are found.  Heat recovery, gas preheat, defrost properties and so on are
items you define at the system level.
 
~Nick
 
 
 
 
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com 
 
From: Alan Crittendon [mailto:alanc at dwcei.com] 
Sent: Friday, November 05, 2010 4:02 PM
To: equest-users at lists.onebuilding.org
Cc: Nick Caton
Subject: RE: [Equest-users] auxilliary heat and desiccant wheel
 
Thanks that is very helpful.  However, I think I have something
fundamentally wrong with the HVAC.  I have two airside system types.
One is the packaged hvac heat pump and one is the unit I am going to use
as the fresh air erv.  I have them both assigned to the same shell
component under the first screen shown below.
 
  
 
When I try to do what you say below and modify the systems under detail
mode, I see this.
 
 
 
  Where am I supposed to modify the heat recovery?  Under each zone?
 
Alan Crittendon, PE, LEED AP
DW Collier Engineering, Inc.
(p) 731-479-2115
________________________________
From: Nick Caton [mailto:ncaton at smithboucher.com] 
Sent: Friday, November 05, 2010 2:05 PM
To: alanc at dwcei.com; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] auxilliary heat and desiccant wheel
 
Hi Alan!
 
1.       "auxilliary strip heat:" Not totally sure what specifically
you're talking about (vocabulary disconnect probably), but I think
you'll find what you're looking for under the "supplemental heat/defrost
tab" in detailed mode.
2.       Look in the same place first... alternatively you may be able
to specify dual fuel as a pre-heat option
3.       Easiest approach, for projects large and small, generally is
to:
a.       Go to the airside system(s) served by the OA unit, 
b.      Enable/define energy recovery inputs (including wheel
properties), and 
c.       Proportion out the delivered flow rates and fan/process
energies of your OA unit between the served systems
 
~Nick
 
 
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com 
 
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Alan
Crittendon
Sent: Friday, November 05, 2010 9:46 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] auxilliary heat and desiccant wheel
 
 
How do I factory in the auxilliary strip heat or use a dual fuel heat
option for packaged heat pumps?  Also how do I put in a desiccant wheel
for an outside air unit?
 
Alan Crittendon, PE, LEED AP
DW Collier Engineering, Inc.
720 Broadway St.
Suite 100
South Fulton, TN 38257
(p) 731-479-2115
(f) 731-479-8018 
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101105/39ff91c8/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101105/39ff91c8/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 20726 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101105/39ff91c8/attachment-0001.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 18567 bytes
Desc: image006.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101105/39ff91c8/attachment-0002.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 48266 bytes
Desc: image007.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101105/39ff91c8/attachment-0003.jpeg>
    
    
More information about the Equest-users
mailing list