[Equest-users] auxilliary heat and desiccant wheel
Nick Caton
ncaton at smithboucher.com
Fri Nov 5 12:05:12 PDT 2010
Hi Alan!
1. "auxilliary strip heat:" Not totally sure what specifically
you're talking about (vocabulary disconnect probably), but I think
you'll find what you're looking for under the "supplemental heat/defrost
tab" in detailed mode.
2. Look in the same place first... alternatively you may be able
to specify dual fuel as a pre-heat option
3. Easiest approach, for projects large and small, generally is
to:
a. Go to the airside system(s) served by the OA unit,
b. Enable/define energy recovery inputs (including wheel
properties), and
c. Proportion out the delivered flow rates and fan/process
energies of your OA unit between the served systems
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Alan
Crittendon
Sent: Friday, November 05, 2010 9:46 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] auxilliary heat and desiccant wheel
How do I factory in the auxilliary strip heat or use a dual fuel heat
option for packaged heat pumps? Also how do I put in a desiccant wheel
for an outside air unit?
Alan Crittendon, PE, LEED AP
DW Collier Engineering, Inc.
720 Broadway St.
Suite 100
South Fulton, TN 38257
(p) 731-479-2115
(f) 731-479-8018
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101105/744fff33/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101105/744fff33/attachment.jpeg>
More information about the Equest-users
mailing list