[Equest-users] Baseline Building HVAC system

Carol Gardner cmg750 at gmail.com
Mon Mar 29 13:38:08 PDT 2010


Rob,

Assuming you are looking at Table G3.1.1A in Standard 90 the key would be in
the use of the word AND: 3 stories or less AND less than 25,000 sf for PSZ
vs 5 stories or less AND between 25,000 and 100,000 sf for VAV. So I think
you should use VAV and that the below grade floor doesn't even come into
play.

Others?

Carol

On Mon, Mar 29, 2010 at 12:42 PM, Rob Hudson <rdh4176 at gmail.com> wrote:

> I have an office building that i am modeling that has 3 above ground floors
> and one below ground floor.  the total square footage is 32,000.  would this
> qualify as a VAV for the baseline or a single zone constant volume?
> The below ground floor is the part that is making me have second thoughts.
> my first thought was VAV, but i figured i would pose the question to get
> some healthy conversion.
>
> thanks,
>
> --
> Rob Hudson
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100329/f624cd19/attachment.htm>


More information about the Equest-users mailing list