Rob,<br><br>Assuming you are looking at Table G3.1.1A in Standard 90 the key would be in the use of the word AND: 3 stories or less AND less than 25,000 sf for PSZ vs 5 stories or less AND between 25,000 and 100,000 sf for VAV. So I think you should use VAV and that the below grade floor doesn't even come into play.<br>
<br>Others?<br><br>Carol<br><br><div class="gmail_quote">On Mon, Mar 29, 2010 at 12:42 PM, Rob Hudson <span dir="ltr"><<a href="mailto:rdh4176@gmail.com">rdh4176@gmail.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">
I have an office building that i am modeling that has 3 above ground floors and one below ground floor. the total square footage is 32,000. would this qualify as a VAV for the baseline or a single zone constant volume?<br>
The below ground floor is the part that is making me have second thoughts. my first thought was VAV, but i figured i would pose the question to get some healthy conversion.<br><br>thanks,<br clear="all"><br>-- <br><font color="#888888">Rob Hudson<br>
</font><br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br>