[Equest-users] Heat Pump Efficiencies

Daniel Deese Daniel.Deese at crbusa.com
Wed Mar 24 07:21:56 PDT 2010


Michael,

 

            Typically equest stores the efficiency of a given piece of equipment as either the Heat Input Ratio (HIR) or as the Electric Input Ratio (EIR).  This is under the "Equipment Efficiency" heading on the "Basic Specifications" tab if you open the equipment properties within the detailed interface.  The Electric Input Ratio should be the inverse of the COP.  I hope this helps.  Thanks.

 

daniel

 

Daniel I. Deese, EI| CRB Consulting Engineers | 

1255 Crescent Green, Suite 350 | Cary, NC 27518 | 

P: 919-852-5443 | F: 919-852-5454 | X: 4543

Email: daniel.deese at crbusa.com <mailto:daniel.deese at crbusa.com>  

________________________________________________________________________________________

 

This document may contain confidential information and is intended for use by the addressee only. If you are not 

the intended recipient, please do not transmit, copy, disclose, or utilize this communication in any manner. If you 

received this message in error, please notify the sender immediately and delete this message.

 

ü Please consider the environment before printing this email.

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of M. Shields
Sent: Wednesday, March 24, 2010 9:59 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Heat Pump Efficiencies

 

Hi All,

 

I am still fairly new to equest and I am having a bit of trouble with setting up my HVAC.  I created a building model using the equest wizard and now I have made a number of changes within the detailed DOE2 interface.  The building uses air source heat pumps for the HVAC and I would like to change the EER/COP values without going back to the wizard, but I cannot figure where these values are stored.  Is there an easy way to make changes like that within DOE2?

 

Thanks,

Michael Shields

 

____________________________
Michael Shields
Facility Strategies Group
2222 Gold Hill Road, Suite 5
Fort Mill, SC 29708
Phone: 803-493-4507
Fax: 803-548-2511
Email: mshields at fstrategies.com

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100324/5d806de3/attachment.htm>


More information about the Equest-users mailing list