[Equest-users] Interior LPD Baseline & Proposed

Pasha Korber-Gonzalez pasha.pkconsulting at gmail.com
Mon Mar 8 21:01:25 PST 2010


David & Nick are both correct-just remember either 'space-for-space' OR
'area-by-area'.  I always use the area method--only for the reason that I
get bored and annoyed looking up individual space LPD's in the chapter 9
table.  It is more interesting to me to do the space take-offs for my
proposed building and calculate the zone area-average LPD -it helps me get
more familiar with the characteristics of the spaces/zones I am modeling.
In some models where we don't have reflected ceiling plans or LPD-zone
take-off from the lighting desingers then I can still assume the area
method which keeps my inputs simplified.

pk

On Mon, Mar 8, 2010 at 6:41 PM, David S Eldridge <DSE at grummanbutkus.com>wrote:

>  Appendix G in 2004 says to use the same method of categorization that you
> use in the proposed building.  This would be especially important if the
> areas of the project have varying schedules or methods of lighting control.
>
>
>
> David
>
> http://www.grummanbutkus.com
>
>
>
>
>
>
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Nick Caton
> *Sent:* Monday, March 08, 2010 7:36 PM
> *To:* Soham Babu; equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] Interior LPD Baseline & Proposed
>
>
>
> Hi Soham,
>
>
>
> I am no USGBC reviewer, but I have submitted comparative models in the past
> using the “actual” design, and working out an equivalent LPD for the whole
> building applied uniformly to the spaces.  I do not think there is anything
> preventing you from entering the individual space LPD’s in the proposed
> model, excepting that could take a bit more time.  You may find it pushes
> your energy savings further however depending on the rest of your model.
>
>
>
> [image: cid:489575314 at 22072009-0ABB]**
>
> * *
>
> *NICK CATON, E.I.T.***
>
> PROJECT ENGINEER
>
> 25501 west valley parkway
>
> olathe ks 66061
>
> direct 913 344.0036
>
> fax 913 345.0617
>
> *Check out our new web-site @ *www.smithboucher.com* *
>
>
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Soham Babu
> *Sent:* Wednesday, March 03, 2010 12:29 AM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] Interior LPD Baseline & Proposed
>
>
>
> Hi all,
>
>
>
> In the baseline interior LPD I have gone with  building area method, but
> for proposed the electrical floor plans as given space by space LPD ,if I go
> with space by method in proposed ASHRAE recommends ? or shall I have to go
> with both identical like if I follow building area method in baseline
> identical in proposed if yes, than can I take average  LPD of the all
> spaces?
>
>
>
> Any help will be greatly appreciated
>
>
>
> Kind Regards
>
> Soham babu
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100308/f9685507/attachment.htm>


More information about the Equest-users mailing list