[Equest-users] (no subject)

Bruce Easterbrook bruce5 at bellnet.ca
Wed Mar 3 05:31:13 PST 2010


I would think the difference is in your ventilation.  Your proposed 
seems to be bringing in much more outside air.
Bruce

On 03/03/2010 08:10 AM, Karen Walkerman wrote:
> with the VAV system, it is likely that your boiler is being used to 
> re-heat cool air.  This can account for significant additional boiler 
> energy use, as well as boiler energy use in the summer.  If this is an 
> Appendix G baseline, take a look at the controls required for water 
> temperature.  Also, due to the high increase in boiler energy use 
> between the proposed and baseline, I'm guessing there may be a space 
> that requires significant cooling all year.  If this is the case, you 
> may be required to provide a separate cooling system for this space.
>
> --
> Karen
>
> On Wed, Mar 3, 2010 at 6:33 AM, Paul S. <sep.paul at gmail.com 
> <mailto:sep.paul at gmail.com>> wrote:
>
>     I've got the result of the end use between baseline and proposed
>     design, everything seems logical except the boilers consumption.
>     Boilers are the same type in the baseline and proposed design.
>
>     Boilers in the baseline are sized by eQUEST, in the proposed boilers
>     are given calculated by the engineers.
>
>     The only difference is in the proposed design we used air-cooled
>     chillers and FCU and for the baseline water-cooled and packaged VAVs.
>
>     Any suggestion about this difference in BTU consumption. And why in
>     baseline desing in June July we have BTU consumption while in the 2
>     designs have same temperatures and same schedules.
>
>     thanks
>
>     _______________________________________________
>     Equest-users mailing list
>     http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>     To unsubscribe from this mailing list send  a blank message to
>     EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>     <mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>    
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100303/20724cbe/attachment.htm>


More information about the Equest-users mailing list