<font face="Times New Roman, Times, serif">I would think the difference
is in your ventilation.  Your proposed seems to be bringing in much
more outside air.<br>
Bruce<br>
</font><br>
On 03/03/2010 08:10 AM, Karen Walkerman wrote:
<blockquote
 cite="mid:69a9bc0a1003030510y332ebf20pe127da3e0e9be7f@mail.gmail.com"
 type="cite">with the VAV system, it is likely that your boiler is
being used to re-heat cool air.  This can account for significant
additional boiler energy use, as well as boiler energy use in the
summer.  If this is an Appendix G baseline, take a look at the controls
required for water temperature.  Also, due to the high increase in
boiler energy use between the proposed and baseline, I'm guessing there
may be a space that requires significant cooling all year.  If this is
the case, you may be required to provide a separate cooling system for
this space.
  <div><br>
  </div>
  <div>--</div>
  <div>Karen <br>
  <br>
  <div class="gmail_quote">On Wed, Mar 3, 2010 at 6:33 AM, Paul S. <span
 dir="ltr"><<a moz-do-not-send="true"
 href="mailto:sep.paul@gmail.com">sep.paul@gmail.com</a>></span>
wrote:<br>
  <blockquote class="gmail_quote"
 style="border-left: 1px solid rgb(204, 204, 204); margin: 0pt 0pt 0pt 0.8ex; padding-left: 1ex;">I've
got the result of the end use between baseline and proposed<br>
design, everything seems logical except the boilers consumption.<br>
Boilers are the same type in the baseline and proposed design.<br>
    <br>
Boilers in the baseline are sized by eQUEST, in the proposed boilers<br>
are given calculated by the engineers.<br>
    <br>
The only difference is in the proposed design we used air-cooled<br>
chillers and FCU and for the baseline water-cooled and packaged VAVs.<br>
    <br>
Any suggestion about this difference in BTU consumption. And why in<br>
baseline desing in June July we have BTU consumption while in the 2<br>
designs have same temperatures and same schedules.<br>
    <br>
thanks<br>
    <br>
_______________________________________________<br>
Equest-users mailing list<br>
    <a moz-do-not-send="true"
 href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org"
 target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a
 moz-do-not-send="true"
 href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
    <br>
  </blockquote>
  </div>
  <br>
  </div>
  <pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
  </pre>
</blockquote>
</body>
</html>