[Equest-users] GSHP Loops
Nick Caton
ncaton at smithboucher.com
Mon Jun 28 11:40:56 PDT 2010
Regarding the pumps - it may seem a little unintuitive, but look to define the circulation pumps on the loops themselves, not on the GLHX element. Also, Larry's posed situation is a little simpler when you consider that "standby" pumps for redundancy don't need to be modeled. Only define the equipment that is running at any given time.
If you have multiple loops operating staged in parallel, look to define the # of pumps after doubleclicking the pump in question in detailed mode (in the component tree). Right click those fields and check those help files for more info ;).
As may be apparent, you're not going to get a lot done in the way of defining an actual system until you're in detailed mode by the way - just a heads up in case anyone hasn't realized that yet.
The GSHP curves referenced below are great if you're designing around the corresponding Carrier equipment... Some take the approach of finding the curve corresponding to the equipment that's the closest match, others are comfy with drilling their manufacturer reps and determining the exact info required to create custom performance curves... I'm aspiring to be the latter category myself =). One thing everyone seems to agree on is that the library curves (that came with eQuest) for a heatpump chiller aren't appropriate for modeling GSHP's.
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Daniel Deese
Sent: Monday, June 28, 2010 11:14 AM
To: Fish, Lawrence; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] GSHP Loops
Larry,
I just looked, and I don't think you can assign a pump to your ground source heat exchanger. It may depend on the type of the heat exchanger (lake/well, vertical loop, etc.), so don't be afraid to try. Under the heat exchanger properties, click on the "attachments" tab, and see if you can attach at pump to the loop. The pump/s described on that tab would be the two 500 gpm pumps you describe. You would then attach another pump to that circulation loop, and that pump would be your 1,000 gpm building circulation pump. Technically, your two 500 gpm pumps are acting as primary pumps for your ground loop heat exchanger, and the 1,000 gpm pump is acting at the secondary pump serving the building. If eQuest won't let you attach a primary pump to your ground loop heat exchanger, I'm stumped. If you find out that there is a geothermal heat exchanger type that will allow you to attach a primary pump to it, please respond to the list, and all would appreciate it. I hope this helps. Thanks.
daniel
Daniel I. Deese, EI| CRB Consulting Engineers |
1255 Crescent Green, Suite 350 | Cary, NC 27518 |
P: 919-852-5443 | F: 919-852-5454 | X: 4543
Email: daniel.deese at crbusa.com <mailto:daniel.deese at crbusa.com>
________________________________________________________________________________________
This document may contain confidential information and is intended for use by the addressee only. If you are not
the intended recipient, please do not transmit, copy, disclose, or utilize this communication in any manner. If you
received this message in error, please notify the sender immediately and delete this message.
ü Please consider the environment before printing this email.
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Fish, Lawrence
Sent: Thursday, June 24, 2010 4:08 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] GSHP Loops
Hi Everybody -
So I've been lurking on the list for a little bit now and have a 2 questions I was hoping could be answered. First off, looking around some people say its necessary to download the GSHP curves( from 2002 located at http://www.doe2.com/download/eQUEST/) while others say its not, does anyone know the status for the latest version, 3.63b?
Second question, a modeling question, is in terms of our GSHP. I'm still pretty new to modeling, so if it a silly question, I apologize. I have 2 500 GPM pumps (+1 Standby) that are pulling water from our well field, and 1 more 1000gpm pump (+1Standby) pumping to the different rooms in our building. In terms of the attached image, Pump Properties, what Pump(s) is eQUEST looking for? My pumping to the Well field or to the building? Do I need to average the pumps I have?
Thank you in advance for your time and help.
Best Regards,
Larry
Lawrence Fish
732-584-0262
www.psands.com <http://www.psands.com/>
PS&S
integrating design & engineering
This e-mail message and any attached files are confidential and are intended solely for the use of the addressee(s) named above. This communication may contain privileged or confidential information. If you are not the intended recipient or person responsible for delivering this confidential communication to the intended recipient, you have received this communication in error, and any review, use, dissemination, forwarding, printing, copying or other distribution of this e-mail message and any attached files is strictly prohibited. If you have received this confidential communication in error, please notify the sender immediately by reply e-mail message and permanently destroy all electronic, paper or other versions of this e-mail message and attachments thereto.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100628/c80314cf/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100628/c80314cf/attachment.jpeg>
More information about the Equest-users
mailing list