[Equest-users] (no subject)
Sami, Vikram
Vikram.Sami at perkinswill.com
Mon Jun 21 11:06:19 PDT 2010
I am assuming by ceiling you mean a dropped ceiling. If that's the case, the only time you have one is when you're floor-floor>floor -ceiling in the wizard. You will then get a plenum zone and the ceiling is the surface between them.
Ceilings separate a conditioned zone from a plenum
Floors separate two zones stacked above each other
Roof is an exterior surface (on top) of a zone.
If a floor is above a conditioned space then it is modeled as adiabatic.
Not sure about your Window question. If you set your window height as ~5ft and your overall flr-flr height is more than 10 (more than double the window height) then I can see it giving you an error for a window-wall ratio of 50.7% - you don't have enough wall width to carry out the request.
Hope this helps
Vikram Sami, LEED AP
Sustainable Design Analyst
1382 Peachtree St. NE, Atlanta, GA 30309
t: 404-443-7462 f: 404.892.5823 e: vikram.sami at perkinswill.com www.perkinswill.com<http://www.perkinswill.com/>
Perkins+Will. Ideas + buildings that honor the broader goals of society
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Ju-Yeon Julie Shin
Sent: Monday, June 21, 2010 1:19 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] (no subject)
First of all, THANK YOU ALL for helping me to build this model without giving it up.
I spent two days on the weekend to build the model and one day to define zones.
Defining zones took the entire day because multi level spaces kept giving me errors so i just assumed that they are all one level spaces. Too bad. (fig#1)
Anyway, I have few questions regarding constructions.
As you can see on the fig#2, "Building Envelope Constructions" consists of "Roof Surfaces", "Ground Floor", and "Below Grade Walls".
For the basement floor, does "Roof Surfaces" actually mean the ceiling?
Since the ground floor does not stand exactly on the basement floor (I mean they have different footprints), I believe that the exposed basement ceiling needs different construction. Am I correct? If I am, how can I assign different constructions for each part?
For the first floor, the same screen asks whether it is above a conditioned space or a parking garage, etc. It is actually located above both of them(a conditioned space and a parking lot). I am not sure which one to choose and how my decision is going to affect on the simulation.
The fig#3 is about a standard floor (6, 7, and 8th). I am still not sure how I have to understand "Roof Surfaces", "Ground Floor", and "Below Grade Walls" concepts.
I don't know why I need roof and ground constructions for a standard floor.
The last question for now is about window construction (fig#5). I put window width, height, and sill height. Then I put "% window". The entire window to wall ratio is 49%.
But whichever number I put for this percentage, it keeps telling me that it is out of range. Does anyone know how to make it work?
I like using eQUEST "UP UNTIL NOW" but at the same time I'm so frustrat ed because I have no background on it.
Again, thank you so much for helping me.
Joo Yun Julie Shin
________________________________
Hotmail: Trusted email with Microsoft's powerful SPAM protection. Sign up now.<https://signup.live.com/signup.aspx?id=60969>
This email and any files transmitted with it are confidential and intended solely for the addressee. If you are not the named addressee you should not disseminate, distribute, copy, or alter this email.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100621/4db81984/attachment.htm>
More information about the Equest-users
mailing list