[Equest-users] Actual Building Energy Cost
John Aulbach
jra_sac at yahoo.com
Thu Jun 17 09:52:16 PDT 2010
Two situations:
1) Matching energy use - accurate metering
2) Matching energy bills - need first accurate energy measurement..THEN you need to input the rates correctly, including taxes..
Don't confuse the two..
My FOUR cents !!!!!
________________________________
From: "Li, Lan" <lli at sbmce.com>
To: Eric O'Neill <elo at MichaelsEngineering.com>; Nick Caton <ncaton at smithboucher.com>; David Bastow <dbastow at mcclure-engineering.com>; aazhari at jainconsultants.com; equest-users at lists.onebuilding.org
Sent: Thu, June 17, 2010 6:53:03 AM
Subject: Re: [Equest-users] Actual Building Energy Cost
In one of my learning course, the instructor mentioned that after they used eQuest simulated an existing campus, they were not able to have the simulation results to match utility bills close enough. It turned out that the economizer damper was on all the time and the some meters were set up wrong which leads the historical data was inaccurate.
Lan
Lan Li, PE
Mechanical Engineer
Scheeser Buckley Mayfield LLC
1540 Corporate Woods Parkway
Uniontown, OH 44685
Phone: (330) 896-4664 ext. 123
Cell: (330) 904-6292
Fax: (330) 896-9180
lli at sbmce.com
www.sbmce.com
ColumbusBranch Office (614) 448-1498
Please consider the environment before printing this email.
This e-mail (including any attachments) is confidential and may be legally privileged. If you are not an intended recipient or an authorized representative of an intended recipient, you are prohibited from using, copying or distributing the information in this e-mail or its attachments. If you have received this e-mail in error, please notify the sender immediately by return e-mail and delete all copies of this message and any attachments.
Thank you
________________________________
From:Eric O'Neill [mailto:elo at MichaelsEngineering.com]
Sent: Thursday, June 17, 2010 8:11 AM
To: Nick Caton; David Bastow; aazhari at jainconsultants.com; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Actual Building Energy Cost
Nick,
I should make it clear that my initial questions weren’t meant to drill David. I’m genuinely interested if the DOE projects required an extremely high level of technical accuracy on the input side. (Although they were also somewhat of a reaction to those requirements.) We have this discussion in our office every so often, and I’m usually somewhat on my own, but I’m still not convinced.
Would you mind elaborating a little more about why you feel this to be true:
“HOWEVER: The concept of building a model for an existing building, whose modeled energy consumption/costs fall within a 1-2% of historical utility records, is entirely feasible – and a reasonable requirement if the goal is to generate a model for predictive purposes.”
So let me ask it this way. Let’s say you’ve got a model, and it’s coming in about 6% low (both heating and electric), but to the best of your knowledge everything is set up properly. You’ve got to start making some educated guesses to close the gap. Do you assume the boiler needs a tuning (drop your efficiency a few percent) and the AHU coils need to be cleaned (bump up your static)? Or do you bump up your infiltration slightly (because it’s probably not a very tight building). Or did some maintenance guy came along and switched on both the boiler pump manually on when he got a cold complaint, and no one returned them to auto? Or maybe you have data from a few years with abnormally warm summers and cold winters. I could go on practically ad nauseum. There’s just so many things that can be wrong with an existing building, as all of you probably know.
Whatever you choose, that guess you make may interact (or lack an interaction) with some measures you’re predicting. So, predicatively, what makes a 1-2% off model better than a 5-6% off model unless you really spend the time and find out whether your inputs are accurate?
Cheers,
Eric
From:Nick Caton [mailto:ncaton at smithboucher.com]
Sent: Wednesday, June 16, 2010 5:43 PM
To: Eric O'Neill; David Bastow; aazhari at jainconsultants.com; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Actual Building Energy Cost
While I (and I am sure many others) have books to write regarding my thoughts on the topic, I think I might suggest a simple step back: The concept of predictively modeling to within a few percentage points of accuracy is ridiculous. There are simply way to many things that could not be known. HOWEVER: The concept of building a model for an existing building, whose modeled energy consumption/costs fall within a 1-2% of historical utility records, is entirely feasible – and a reasonable requirement if the goal is to generate a model for predictive purposes. How often such predictive models’ accuracy is misinterpreted is something I get depressed to think about.
I haven’t done the DOE-modeling work that’s being referenced with such requirements, but I have done work for educational clients (physics/building science departments) who wish to get these models set up for ongoing study/tweaking purposes. The exercise is challenging, and as close as energy modeling gets to “fun,” when you can rest at ease knowing the client is fully on board with what the model is and isn’t.
It’s fully rational to squirm and cringe when you have to make models that you know will be mis-used and mis-understood, despite your best efforts. Fortunate is the practicing energy modeler who gets to work for fully educated clients and design teams all the time =).
Rather than drill David, I think it would be safe to assume those DOE requirements exist to calibrate a model to a given degree to whatever historical records are available, NOT to mandate a level of accuracy for predictive purposes. If I’m wrong, I hope that work never crosses my desk!
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olatheks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
From:equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Eric O'Neill
Sent: Wednesday, June 16, 2010 4:52 PM
To: David Bastow; aazhari at jainconsultants.com; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Actual Building Energy Cost
How much effort was put into minimizing the error of your inputs to justify that level of accuracy in your output? For example, did you convert real weather data for the two years and use an average of the simulations? Were you modeling small buildings so you could get a fairly reasonable infiltration rate empirically? Were occupancy schedules trended, and for how long? Were all the systems and controls working correctly, with all sensors calibrated regularly?
1 to 2% seems to me to be fairly unreasonable. Unless you do an amazing job verifying your inputs, in my opinion that level of precision doesn’t get you a better model. If you set everything up as best you can and it comes in there, great! But a correctly set up model can be off by over 2% because of a couple “El Nino” years, a facilities guy locking a humidity high limit to 50% for a summer, or any number of operational factors. On the other side of it, we’ve tried to match a simple DOE2.2 model to a DOE2.1e model with limited success (I don’t think we got within 3%, although we didn’t spend too much time with it). Who knows what the difference would be with E+.
I know I always squirm when I’m asked to do existing building models, and it may be irrational. Heck, if the DOE is asking for 1-2%, I probably am being irrational. But it seems to me that the error from assumptions could easily swing a model 1-2% (what would a 30% error on your infiltration do to an otherwise correct building?). What are other people’s thoughts?
Eric
From:equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of David Bastow
Sent: Wednesday, June 16, 2010 3:48 PM
To: aazhari at jainconsultants.com; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Actual Building Energy Cost
On all the DOE modeling projects that we have done, of an existing building, they have required the model to be within 1 to 2% or less of the actual energy usage, based on an average two year history. Is that what you are talking about?
David A. Bastow
McClure Engineering, Inc.
________________________________
From:equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Ahmed Azhari
Sent: Wednesday, June 16, 2010 12:10 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Actual Building Energy Cost
Hi all,
Does anyone have a ballpark percentage of the actual annual energy cost versus the modeled annual energy cost for a building?
Thanks,
__________________________________________________________________________
Ahmed Azhari, B.Eng., LEED® AP
Energy Analyst
Jain Sustainability Consultants Inc.
2260 Argentia Road, 2nd Floor
Mississauga, Ontario L5N 6H7 , CANADA
Tel: (905) 542 7211 Ext 234
Fax: (905) 542 7622
Email:aazhari at jainconsultants.com
Web: www.jainassoc.com
NOTICE OF CONFIDENTIALITY
This communication, including any attachments, is intended only for the use of the addressees and is confidential.
If you received this communication in error, please permanently delete the entire communication from any computer or other storage medium.
Please consider your environmental responsibility before printing this e-mail & any documents
__________ Information from ESET Smart Security, version of virus signature database 5202 (20100616) __________
The message was checked by ESET Smart Security.
http://www.eset.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100617/767d8363/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100617/767d8363/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 1257 bytes
Desc: image002.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100617/767d8363/attachment.gif>
More information about the Equest-users
mailing list