[Equest-users] Excessive Unmet Heating Load Hours withan Auto-Sized HVAC System
Bruce Easterbrook
bruce5 at bellnet.ca
Fri Jun 11 10:33:43 PDT 2010
You are in trouble shooting mode now, do a save as to get a play file.
Dakota seems right 50,000 hrs is a problem. Add in the baseboards, they
might indicate a few problems zones and give you a clue to the high
hours. Sheila has some good suggestions too. Once you figure out the
problem just go back to the original file and tune it up.
Bruce
On 11/06/2010 01:03 PM, Robert Des Rosiers wrote:
>
> Dakota:
>
> There is definitely diversity in the zones and I have used the glass
> library for all window types. Also, I agree that not having reheat is
> inappropriate for this building use due to the programmatic and
> occupancy diversity within each zone (there are two AHU's feeding
> multiple zones in the proposed design and I have maintained those
> thermal blocks per ASHRAE appendix G). Unfortunately the baseline
> system I have described is what is required per the "Required
> Treatment of District Thermal Energy" document for LEED compliance.
> Assuming the system is functioning correctly (or as best as possible
> considering the design) and the heating loads are not met would LEED
> allow the addition of zone level baseboards for purposes of the
> Optimized Energy credit?
>
> Note: I have included the suggestions listed below (except for local
> baseboard heating) and the improvement in unmet hours is marginal.
>
> Thanks -
>
> *From:* Dakota Kelley [mailto:dakotak at teliospc.com]
> *Sent:* Friday, June 11, 2010 9:40 AM
> *To:* desrosiers at studioma.com
> *Cc:* equest-users at lists.onebuilding.org
> *Subject:* RE: [Equest-users] Excessive Unmet Heating Load Hours
> withan Auto-Sized HVAC System
>
> Robert,
>
> 50,000 hours is much more than I would anticipate for a capacity
> issue. You are essentially describing a hydronic VAVT system, which
> is begging for unmet heating hours if there is a lot of diversity in
> the zones’ demands and no reheat capabilities. My experience has been
> that eQUEST over-sizes hot water systems, and this is exacerbated if
> the “simple” method is used to define the windows. It can be as much
> as 250%-300%. That many hours sounds like the system is not
> functioning as intended – almost as if the heating loop is not
> assigned to the zones/system, or something similar. Or, not having
> reheat could be inappropriate for the building use or climate.
> Regardless, adding zone reheat as Bruce and Pasha indicated should
> make a huge difference.
>
> Thanks,
>
> *DAKOTA KELLEY *
>
> Project Designer | Energy Analyst
>
> Office: 214.744.6199
>
> Cell: 214.280.3825
>
> Fax: 214.744.0770
>
> http://www.teliospc.com <http://www.teliospc.com/> 3535 Travis
> St. Suite 115
>
> dakotak at teliospc.com <mailto:dakotak at teliospc.com> Dallas, TX 75204
>
> | MEP ENGINEERING · ENERGY MODELING · LEED CONSULTATION · COMMISSIONING |
>
> * *
>
> CONFIDENTIALITY NOTICE: This email is intended only for the use of the
> individual or entity to which it is addressed,
>
> And may contain information that is privileged, confidential and
> exempt from disclosure under applicable law. If you
>
> are not the intended recipient, please email the sender immediately,
> and delete this email from all computers. Any
>
> distribution or other use is strictly prohibited. Copyright © 2009
> Telios Corporation.
>
> *From:* Bruce Easterbrook [mailto:bruce5 at bellnet.ca]
> *Sent:* Friday, June 11, 2010 6:33 AM
> *Cc:* equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] Excessive Unmet Heating Load Hours
> withan Auto-Sized HVAC System
>
> In your air side HVAC section go into the zone level and check that
> your sizing option is set to "adjust loads". If it is from loads go
> to the summary tab and change all your zones. Also beside that is
> throttling range, you can try adjusting that upwards say to 4 deg.
> You can also change your control zone to see it this helps. If your
> AHU is off at night you can also adjust it to come on before the
> occupancy. You SS-O report will show this if the hours are lumped
> near the start up time. Then add more heat as Pasha said.
> Bruce Easterbrook P.Eng.
> Abode Engineering
>
> On 10/06/2010 10:55 PM, Pasha Korber-Gonzalez wrote:
>
> I have found with my own projects that even sometimes when the HVAC
> designer has specified a specific capacity for htg water equipment
> that sometime in my model file I still have unmet loads for htg. I
> suggest at this point specify additional htg capacity by either
> increasing the reheat delta-T from say 30F to 50F and/or adding zone
> level baseboards. By adding the baseboards you are adding a component
> of the system that will supplement the skin losses being experienced
> by the simulation model.
>
> by adding baseboards for the additional requrired heat then you should
> be able to meet your heating loads.
>
> hope this helps,
>
> pasha
>
> On Thu, Jun 10, 2010 at 7:38 PM, Robert Des Rosiers
> <desrosiers at studioma.com <mailto:desrosiers at studioma.com>> wrote:
>
> All:
>
> I have completed an energy model for a baseline scenario from which to
> compare my proposed design. The baseline HVAC system is a constant
> volume single zone AHU w/ no reheat; the AHU is served by HW and CHW
> loop from a central plant. I have set this up in eQuest as a
> "Variable Air Volume" system type with the AHU fan control set to
> "Constant Volume"; my thought here is that each zone fed by the AHU
> will control temperature using a VAV box w/ no local reheat or
> cooling. Flow and temperature from the AHU will be delivered based on
> the coolest or warmest zone it serves.
>
> All seems fine with the design flows, ventilation flows and cooling
> capacities. My problem is with the heating capacity as I have
> excessive unmet heating hours (50,000). I have allowed eQuest to size
> the heating capacity of the preheat and heating coil as well as the
> minimum flow ratios. _Does anyone have any thoughts as to what is
> causing these unmet heating load hours? Is the way I have set-up the
> desired baseline HVAC system incorrect?_
>
> Any guidance is greatly appreciated. Thanks -
>
> Robert Des Rosiers, LEED-AP
>
> *STUDIO MA*
>
> 130 N Central Avenue, No.300 Phoenix, Arizona 85004
>
> Telephone 602 251 3800
>
> Fax 602 251 3100
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
> <mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message toEQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG <mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100611/1e7d43ba/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2143 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100611/1e7d43ba/attachment.jpeg>
More information about the Equest-users
mailing list