Thomas/Kelsey:
A little while ago Adam Boyd put forward a very handy resource I'm attaching.
You're right in that the root issue here is that you can't really model a wall with no mass. When you specify a layer by U-value only (simplified method), notice that you cannot enter a mass for that layer. If you read the associated help files you'll learn this method of specifying materials is only intended for things with negligible mass (i.e. air films). Specifying a whole construction with layers and ignoring mass means you have a wall which is going to act really weird when it comes time to figure out heat retention/transfer behavior with the exterior. It works fine in simpler loads/modeling programs that assume information for you, but in eQuest you have to account for mass in your constructions.
That said, Appendix G and Appendix A do not explicitly tell us the thermal mass properties of the intended baseline construction layers, but helpful fellows like Adam have shared the legwork of looking these items up - read the thread below, examine and try to import the attached .inp into your model.
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Kelsey VanTassel
Sent: Wednesday, June 02, 2010 8:43 AM
To: Thomas Vu; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] BDL Error
Hello Thomas,
I don't think you can make a construction where all the layers are R-value inputs. For a construction to have layers the program must be able to calculate some mass for the wall. If you want to specify only the thermal resistance of the wall choose "u-value input" when you create a new construction and put in the overall u-value for the wall assembly.
Kelsey Van Tassel
Mechanical Engineer | kvantassel at sustaineng.com
We've moved. Please see below for my new contact info.
901 Deming Way, Ste. 201
Madison, WI 53717
608.836.4488 ext. 20| Fax: 608.836.4477
2009 Dane County Small Business Award Recipient
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Thomas Vu
Sent: Tuesday, June 01, 2010 7:38 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] BDL Error
All,
I get the following BDL error in my model
WALL has no heat capacity. U-Value used.
I am modeling the baseline envelope as prescribed in Appendix G of 90.1-2004. Referring to Appendix A of 90.1-2004 to model the baseline envelope, I created layers for the wall construction seen in the attached screenshot. The resulting U-value for the wall is 0.124. Can I not model a wall in this manner? It seems specifying the U-value alone in the construction layer would do the same thing.
Thomas Vu, E.I.
Graduate Student
Dept. of Mechanical and Aerospace Engineering
University of Florida
vietdrum at ufl.edu
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Adam.Boyd at CH2M.com
Sent: Tuesday, April 27, 2010 10:36 AM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] 90.1 and Appendix A Materials
A while back I developed an INP file that contained all the baseline constructions for every climate zone. If you've got the ASHRAE Fundamentals handbook for looking up material properties, this was a pretty routine process. First create the new materials/layers/constructions in detailed edit mode, Appendix A has some detailed descriptions on what those should be (see A3.3.1 for steel framed wall). Next open the inp file and delete everything except the materials, layers and constructions. You can then import that inp file into any project using the eQuest import function. I've attached the file I created for this and just ask that you let me know if you find any mistakes!
I've been considering creating a similar file with the ASHRAE recommended schedules from the 90.1 User's Manual, but not sure if this would be as useful.
Adam
From: Seth P. Spangler [mailto:sspangle at rmf.com]
Sent: Tuesday, April 27, 2010 5:26 AM
To: Paul Riemer; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] 90.1 and Appendix A Materials
Paul,
I've been browsing through the ASHRAE DOE-2 files since receiving your email. I believe I have been following the same rabbit trail that Nick has so it would be great to have canned constructions. Can you explain the best method for importing the ASHRAE constructions into a model? I assume the edit must be made in the INP file. I typically try to avoid editing the INP file since my knowledge of the "code" behind eQuest is limited.
Thanks
Seth Spangler, LEED® AP
Project Engineer
RMF Engineering, Inc
Ph: (843) 971-9639 ext:1497
Fax: (843) 971-9641
sspangle at rmf.com
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Paul Riemer
Sent: Monday, April 26, 2010 5:00 PM
To: 'Nick Caton'; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] 90.1 and Appendix A Materials
Nick,
The DO2.1e input files available as part of the 90.1 User's Manual rely on the DOE2 library of construction materials.
Paul Riemer
Dunham
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nick Caton
Sent: Monday, April 26, 2010 3:43 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] 90.1 and Appendix A Materials
Has anyone invested the time to create or otherwise stumbled across an *.inp file that contains the materials defined in Appendix A9 for easy import/use?
I had a model reviewer (not USGBC) who was unsatisfied with the material thermal properties in the default DOE2 library. I ultimately went through the enormously entertaining exercise of defining materials with matching prescriptive R-values, while still using library data to retain appropriate thermal massing properties to avoid construction errors from weightless constructions.
This was an isolated case, but I could see such a file being a very handy resource for most modelers, particularly if it contained the contents of Tables A9.2A and 9.2B to pull the effective insulation/framing properties into our custom construction layers.
If this is flying over anyone's head who's interested, attached is a partial example of what I'm talking about - if you click File à Import File... and navigate to this file, you'll have a couple defined materials ready to access for your project within seconds - conceivably everything within 90.1 if someone had the time to invest...
On a related note... and I should have asked before, but does Section A9.2 possibly exempt the rest of Section A9 for eQuest users who rely on unmodified default library entries to define their custom envelope constructions?
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100604/94eec2d1/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100604/94eec2d1/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 31773 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100604/94eec2d1/attachment-0001.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Ashrae Baseline Constructions Import File.inp
Type: application/octet-stream
Size: 3730 bytes
Desc: Ashrae Baseline Constructions Import File.inp
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100604/94eec2d1/attachment.obj>
More information about the Equest-users
mailing list