[Equest-users] Reports

tim tim.jgrier at fuse.net
Tue Jul 20 06:11:20 PDT 2010


I also see now there are 2 tabs in results viewing mode in the project
browser.  One is "Reports" and gives me individual charts or spreadsheets.  

 

On a related note, I remember a question about running baseline & proposed
in the same model.  Originally, I was thinking the similarly to the answer
that was given - there has to be 2 models, but I just set up a model with 2
HVAC systems (1 geothermal to cover perimeter & 1 PSZ to cover the one core
zone that is actually gas & electric heat, but 90.1G seems to tell me to
assign PSZ).  

 

First in the building wizard, I assigned these systems as described above.
Then, while in the EEM run wizard, I created a new run and called it "Whole
Building EEM Baseline".  I went to the run details of that one and deleted
the geothermal systems and assigned the PSZ to all zones.  Went back into
the first Whole Building EEM & the geothermal was still there assigned to
perimeter zones so long story short, I think I am running a "baseline case"
& a proposed in the same model.  

 

Some of the reports show a case just called "baseline" as well, but I'm
thinking I can ignore that one so I can get the results I need side-by-side.

 

Hope this can help someone.

Tim

 

 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of tim
Sent: Tuesday, July 20, 2010 8:43 AM
To: 'Martz, Amanda'; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Reports

 

Doi - thanks

 

I see also .csv files are generated in the project folder so I'll check
those out as well.

 

Anybody have an example of a LEED section 1.4 table that USGBC accepted by
any chance?

 

Tim

 

 

From: Martz, Amanda [mailto:amartz at klingstubbins.com] 
Sent: Tuesday, July 20, 2010 8:37 AM
To: tim; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Reports

 

When you run the simulation, a window should pop up with three buttons that
say "return to input building description" or "view summary results/reports"
or "view detailed simulation output file." The first option returns you to
the model, the second shows you a bar graph with electricity usage, and the
third shows you the couple thousand page report that you're probably looking
for. 

 

  _____  

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of tim
Sent: Tuesday, July 20, 2010 8:32 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Reports

 

How do I get reports?  

 

I have set up fairly simple simulations, using as many defaults as possible.
Then I run the simulations and go to "Project & Site", but no summaries are
available in the simulation output folder.  I have results, but no reports.
Do I need to change a setting in each properties dialog or what?

 

Trying to fill out the LEED 1.4 table & to find out what the actual capacity
of my auto-sized heating is, but there are also many other items in that
table I need to find - hoping when I learn how reports are generated and
viewed, I can find it all and report it to LEED.

 

 

Thanks in advance,

Tim