[Equest-users] Throttling Range and Pipe Insulation
    Daniel Vilavedra 
    Daniel.Vilavedra at pgigrup.com
       
    Wed Jan 27 06:17:45 PST 2010
    
    
  
Hello walt,
 
Could you tell how did you change the footprint to one zone per floor or
send me a picture showing it? My model is also outside of the throttling
range and I'm trying to change it. I don't find where the option is.
 
Thanks a lot
 
 
________________________________
De: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] En nombre de Walt
Henry
Enviado el: martes, 26 de enero de 2010 22:19
Para: Daniel Bersohn; equest-users at lists.onebuilding.org
Asunto: Re: [Equest-users] Throttling Range and Pipe Insulation
Hello Daniel,
 
Thanks for your responses to my requests.
 
1)       I did find the zone that was under heated in the reports.  This
building has three zones and the basement was the under heated zone.  I
changed the footprint to one zone per floor in lieu of perimeter/core
and dropped the percentage from 34.1 to 0.9 so I am content with that
since this is an existing system the we can't change.  
 
2)  I found the location of the losses tab in the water loop and see how
the UA can be changed so that should solve the pipe insulation savings
dilemma.  I can't fully agree with you regarding the need to insulate
steam piping.  Although the pipe does heat the zone it is in the process
of condensation in the piping degrades the quality of the steam reaching
the distributors, radiators in this case.  This is a church and the
piping to be insulated is basically 400' of 4", 120' of 2" and 100' of
1".  The function of the piping is to deliver good quality steam to the
radiators and without insulation on long runs, even if they are in a
heated zone takes away steam quality from the zone above and the
radiators in the zone where the pipe is located.
 
Thanks again!
 
Walt
________________________________
From: Daniel Bersohn [mailto:Daniel.Bersohn at BuroHappold.com] 
Sent: Thursday, January 21, 2010 6:09 PM
To: Walt Henry; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Throttling Range and Pipe Insulation
 
Walt,
 
1)       This means that you have a zone that's not getting heating or
cooling when it wants it.  34.1% probably means there's an issue with
your system topology or your system really has unmet load hours in real
life.  If you have one thermostat and lots of rooms with different
internal loads and exposures you're guaranteed to get a lot of unmet
load hours.  The plant having zero unmet load hours means the plant is
satisfying all the requests its getting from equipment that serves
zones.  So the zones aren't getting what they want from AHUs, radiators,
etc. but the plant is doing everything AHUs, radiators etc. want it to.
2)       Any piping downstream of a steam control valve in a two-pipe
system in the same space served by the radiator doesn't need insulation
because it's acting as a radiator.  In a one-pipe system,0 if you have
TRVs on the air vents, any pipe that only serves one radiator and is in
the same space as that radiator need not be insulated since it serves as
a radiator.  If you don't have TRVs on your air vents in a one pipe
system (or in place of the control valves on two-pipe for that matter)
the insulation probably doesn't matter that much since all the radiators
deliver heat (and too much of it at that) at the same time as all the
uninsulated pipe.  For the remaining pipe you'd estimate the surface
area of the piping to be insulated and multiply the U factor of the
insulation by the surface area of the pipe.  Put that into the hot water
loop you're using as an analog for your steam system in detailed mode.
 
Daniel Bersohn, LEED AP
Mechanical Engineer
Buro Happold Consulting Engineers PC
100 Broadway
New York, NY 10005 USA
+1 212 334 2025 Office
+1 212 616 0391 Desk
daniel.bersohn at burohappold.com
www.burohappold.com <http://www.burohappold.com/> 
________________________________
From: Walt Henry [mailto:WHenry at thielsch.com] 
Sent: Thursday, January 21, 2010 8:55 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Throttling Range and Pipe Insulation
 
Good morning eQUEST users,
 
I have two requests:
 
1)       What is the definition of "throttling range"?  I have always
had 0 until my last project which is a Police Station.  We do mostly
energy retrofits and the existing boiler, 37 years old, has an input of
450 MBH.  The total HVAC load is 222.651 MBH per eQUEST.  For the first
time Report BEPU shows my base case model to be 34.1% outside of the
throttling range.  What does this mean?  The % of hours any plant load
is not satisfied is 0.
 
2)       I have a church to model, starting this morning, which has no
insulation on the steam piping and we want to determine the savings by
putting 1" of              fiberglass on the pipes.  Usually we would
determine the savings in e-plus but is there any way to model this in
eQUEST?  There are other measures and it would be convenient to have
everything in one report.
 
Walt Henry
Energy Specialist
RISE Engineering
1341 Elmwood Ave.
Cranston, RI 02910
U.S.A.
Phone:  401-784-3700 Ext. 119
Fax:      401-784-3710    
 
This message has been scanned by MailController
<http://www.mailcontroller.altohiway.com/> .
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100127/54602402/attachment.htm>
    
    
More information about the Equest-users
mailing list