[Equest-users] Warning: ECONO-LOW-LIMIT = *UNUSED*
Anand.Varahala at us.schneider-electric.com
Anand.Varahala at us.schneider-electric.com
Fri Aug 27 06:09:24 PDT 2010
All,
This is a professional listserv and we sure have the need to keep that in
mind. Also, when we post questions, if we include the research we have
already done, it will leave the responders with a reduced chance of
"flaming", and can be helpful to other users as well.
That being said, Adrian, here is what I believe you need:
ECONO-LOW-LIMIT
for all economizer types, specifies a minimum temperature below which the
outside air dampers return to their minimum position. If not specified,
there is no minimum allowable temperature.
This feature may be useful when the building has a heat-recovery chiller,
and it is desireable to run the chiller at low outside-air temperatures to
provide space heating. It may also be useful for buildings having
humidifiers, where the use of extremely cold, dry outside air to provide
space cooling may actually introduce an energy penalty (but see
ECONO-MIN-W for a better way to integrate an economizer with a
humidifier).
Thanks.
_____________________________________________________________________________________
Anand Varahala, LEED® AP | Schneider Electric | Energy Solutions |
Application Engineer
Phone: +1 (919) 227-3920 | Fax: +1 (859) 962-4561 | Mobile: +1 (919)
720-0769
Email: Anand.Varahala at us.schneider-electric.com | Site:
www.schneider-electric.us | Address: 4917 Waters Edge Dr, Suite 270,
Raleigh NC 27606 USA
P Please consider the environment before printing this e-mail
----- Message from Carol Gardner <cmg750 at gmail.com> on Thu, 26 Aug 2010
15:13:25 -0700 -----
To:
Adrian Gurga <gurga at illinois.edu>
cc:
equest-users at lists.onebuilding.org
Subject:
Re: [Equest-users] Warning: ECONO-LOW-LIMIT = *UNUSED*
If you have an economizer you had better put the econo-low-limit
temperature in. It is necessary. You can access help screens in DD edit
also. Once again I encourage you to read the on line help using the pull
down menu. I do believe econo-low-limit temp is available in the wizards
too.
On Thu, Aug 26, 2010 at 12:37 PM, Adrian Gurga <gurga at illinois.edu> wrote:
Chris,
I understand. For some reason it appears that the wizards will sometimes
generates a DOE2 input which doesn't include the econo-low-limit line and
thereby generates a warning. I'm not sure what causes this to happen, but
as long as the model runs without it, I won't bother. Thanks for direction
to the DOE2 definitions file, that's the one I was looking for. It
describes in detail what econo-low-limit is used for and it probably
isn't relevant to my purposes. I think we can call this case closed.
On Thu, Aug 26, 2010 at 2:00 PM, Otto Schwieterman <oschwieterman at fhai.com
> wrote:
I would tweak it in the detailed edit mode because it is very unlikely
that you can get good results by simply using the wizard. There are too
many major variables that you cannot change in the wizard. You might as
well pick the cost/energy consumption via experience if you are not going
to go into the detailed edit mode.
If you simply need eQUEST to spit something out so you have results to
show I would ignore the econo-low-limit but remember that the results mean
nothing.
From: Adrian Gurga [mailto:gurga at illinois.edu]
Sent: Thursday, August 26, 2010 1:38 PM
To: James Hansen
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Warning: ECONO-LOW-LIMIT = *UNUSED*
Excellent. Thanks James. And yes, it's up to us to figure out how to use
it, which I think qualifies as "no support". I'm sure the programmers
responsible for the software are perfectly competent, and I did not mean
to suggest otherwise. I suppose what I really meant to say was that the
software has no customer support, which is understandable because it's
free.
Now back to the model. So one would have to go into the detailed mode in
order to change this parameter? If one was to work with a model only via
the DD wizard as we sometimes do for order of magnitude estimates, would
it be OK to leave ecnono-low-limit unused? or would this result in
inaccurate results?
On Thu, Aug 26, 2010 at 12:22 PM, James Hansen <JHANSEN at ghtltd.com> wrote:
See below. Also, the technical support isn?t ?very poor?, it?s just that
the people working on technical issues are actually programmers. It?s up
to us to figure out how to use it properly.
GHT Limited
James Hansen, PE, LEED AP
Senior Associate
1010 N. Glebe Rd, Suite 200
Arlington, VA 22201-4749
703-338-5754 (Cell)
703-243-1200 (Office)
703-276-1376 (Fax)
www.ghtltd.com
From: equest-users-bounces at lists.onebuilding.org [mailto:
equest-users-bounces at lists.onebuilding.org] On Behalf Of Adrian Gurga
Sent: Thursday, August 26, 2010 1:13 PM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Warning: ECONO-LOW-LIMIT = *UNUSED*
Carol,
With all due respect, "Only to input the temperature and to look at your
help screen." is not a complete sentence. Please reply using English if
you'd like to post on a listserv. If you have advice on how to address
this warning, please provide it. Additionally, "Flaming" (
http://www.urbandictionary.com/define.php?term=flaming) is a behavior
typically reserved for prepubescents on chat forums, not professional
listservs. Please show some professional courtesy in your responses.
Now, let's move forward amicably and discuss the actual topic of the
post.
All,
We all know that as eQUEST is free software, it has very poor technical
support which is why listservs like this exist. Here is the research I've
done so far. Inputting a seach for "econo-low-limit" or even just "econo"
in the eQUEST helpfile produces no results. Are there "pull down help
menus" which discuss this topic as Carol suggests? If so, please direct
me to them. Googling "econo-low-limit" produces one relevent hit other
than this listserv, a user poses the same question I have, but is issue is
never resolved (http://www.energymodelhelp.com/SMF/index.php?topic=107.0
). A search of "econo-low-limit" on this listserv will yield five
results. In four of these, "econo-low-limit" is simply listed as an
input, in the fifth, it is suggested as a way of manipulating the model.
However, I cannot find anywhere on this listserv where the warning
"econo-low-limit" = unused has been discussed. Therefore, I assume it's a
reasonable to post and and I hope it will be helpful to future users.
I can't figure out where to specify an econo-low-limit in the DD wizard,
if I need to go into the detailed edit to address this, please let me know
where that variable is edited. I have attempted to edit the files
manually in notepad to specify an econo-low-limit, so far have had no
luck, but truthfully I'm not too experienced with manual edits. If anyone
could provide some assistance with where to edit this parameter, it would
be appreciated. Alternatively, if this warning does not have detrimental
impact on the outputs, I will just ignore it.
Thanks for your thoughts and comments.
--
Adrian Gurga
Smart Energy Design Assistance Center
University of Illinois - Urbana-Champaign
www.sedac.org
(217) 244-4671
(800) 214-7954
On Thu, Aug 26, 2010 at 11:08 AM, Carol Gardner <cmg750 at gmail.com> wrote:
That was polite, Jason. Users of this list need to be responsible enough
to at least look at the pull down help menus before asking a question on
the listserv, It is impolite and wasteful of everyone's time to not do so.
I have sympathy for someone who is learning but if they really care to
learn this skill and be in the business they need to learn to at least try
to find the answers they need. Perhaps the college systems have changed,
which would be a shame, but when I was in school I had to research and
find my own answers. Since I'm older than dirt we didn't have listservs,
Google, or any of those useful tools that now make finding answers so much
easier.
I rest my case,
Carol
On Thu, Aug 26, 2010 at 8:11 AM, Jason Glazer <jglazer at gard.com> wrote:
Carol,
The eQUEST-user mailing list is for users of all experience levels:
"The eQUEST-users mailing list is for everyone that uses the eQUEST
program. Users at every experience level are encouraged to join this
mailing list and share their questions and knowledge. Users of the DOE-2.2
and D2Comply are also welcome. The mailing list will be a user-to-user
support forum for eQUEST, DOE-2.2, and D2Comply."
We appreciate your contribution but please either reply politely or not at
all.
Jason
On 8/26/2010 9:29 AM, Carol Gardner wrote:
Only to input the temperature and to look at your help screen. This is
something you really should be able to figure out yourself. If you can't
try another profession.
Carol
On Tue, Aug 24, 2010 at 11:55 AM, Adrian Gurga <gurga at illinois.edu
<mailto:gurga at illinois.edu>> wrote:
I am working with a model and am working with the following warning
whenever it runs the BDL Load File Log
Line 1336: Warning Encountered:
INPUT-TYPE COEFFICIENTS ..
ECONO-LOW-LIMIT = *UNUSED*
Any ideas?
--
Adrian Gurga
Smart Energy Design Assistance Center
University of Illinois - Urbana-Champaign
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100827/83ce36b6/attachment.htm>
-------------- next part --------------