<br><font size=2 face="sans-serif">All,</font>
<br>
<br><font size=2 face="sans-serif">This is a professional listserv and
we sure have the need to keep that in mind. Also, when we post questions,
if we include the research we have already done, it will leave the responders
with a reduced chance of "flaming", and can be helpful to other
users as well.</font>
<br>
<br><font size=2 face="sans-serif">That being said, Adrian, here is what
I believe you need:</font>
<br>
<br>
<table align=center>
<tr>
<td>
<br><font size=2><b>ECONO-LOW-LIMIT</b></font>
<p><font size=3>for all economizer types, specifies a minimum temperature
below which the outside air dampers return to their minimum position. If
not specified, there is no minimum allowable temperature.</font>
<p><font size=3>This feature may be useful when the building has a heat-recovery
chiller, and it is desireable to run the chiller at low outside-air temperatures
to provide space heating. It may also be useful for buildings having humidifiers,
where the use of extremely cold, dry outside air to provide space cooling
may actually introduce an energy penalty (but see ECONO-MIN-W for a better
way to integrate an economizer with a humidifier).</font></table>
<br>
<br><img src=cid:_1_08BF4A6C08BF46B400483ED58525778C>
<br>
<br><font size=2 face="sans-serif">Thanks.<br>
</font><font size=3 color=#008000>_____________________________________________________________________________________</font><font size=3>
<br>
</font><font size=1 face="Arial"><b><br>
Anand Varahala, LEED<sup>®</sup> AP</b> | </font><font size=1 color=#008000 face="Arial"><b>
Schneider Electric </b></font><font size=1 face="Arial"><b> | Energy
Solutions</b> | <b>Application Engineer</b> <b><br>
Phone:</b> +1 </font><font size=1 face="Arial">(919) 227-3920</font><font size=1 face="Arial">
| <b>Fax:</b> </font><font size=1 face="Arial">+1 (859) 962-4561</font><font size=1 face="Arial">
| </font><font size=1 face="Arial"> </font><font size=1 face="Arial"><b>Mobile:</b>
</font><font size=1 face="Arial">+1 (919) 720-0769</font><font size=1 face="Arial">
<b><br>
Email:</b> </font><a href="mailto:Anand.Varahala@us.schneider-electric.com"><font size=1 color=blue face="Arial"><u>Anand.Varahala@us.schneider-electric.com</u></font></a><font size=1 face="Arial">
| <b>Site:</b> </font><a href="http://www.schneider-electric.us/"><font size=1 color=blue face="Arial"><u>www.schneider-electric.us</u></font></a><font size=1 face="Arial">
| <b>Address:</b> </font><font size=1 face="Arial">4917 Waters
Edge Dr, Suite 270, Raleigh NC 27606</font><font size=1 face="Arial"> USA</font><font size=5 color=#008000 face="Webdings"><br>
P</font><font size=1 color=#00a000 face="Arial"> Please consider the environment
before printing this e-mail</font><font size=1 face="Arial"> </font>
<br>
<br>
<br>
<br><font size=2 color=#800080 face="sans-serif">----- Message from Carol
Gardner <cmg750@gmail.com> on Thu, 26 Aug 2010 15:13:25 -0700 -----</font>
<table>
<tr>
<td>
<div align=right><font size=3><b>To:</b></font></div>
<td><font size=3>Adrian Gurga <gurga@illinois.edu></font>
<tr>
<td>
<div align=right><font size=3><b>cc:</b></font></div>
<td><font size=3>equest-users@lists.onebuilding.org</font>
<tr>
<td>
<div align=right><font size=3><b>Subject:</b></font></div>
<td><font size=3>Re: [Equest-users] Warning: ECONO-LOW-LIMIT = *UNUSED*</font></table>
<br><font size=3>If you have an economizer you had better put the econo-low-limit
temperature in. It is necessary. You can access help screens in DD edit
also. Once again I encourage you to read the on line help using the pull
down menu. I do believe econo-low-limit temp is available in the wizards
too.<br>
<br>
</font>
<br><font size=3>On Thu, Aug 26, 2010 at 12:37 PM, Adrian Gurga <</font><a href=mailto:gurga@illinois.edu><font size=3 color=blue><u>gurga@illinois.edu</u></font></a><font size=3>>
wrote:</font>
<br><font size=3>Chris,</font>
<p><font size=3>I understand. For some reason it appears that the wizards
will sometimes generates a DOE2 input which doesn't include the econo-low-limit
line and thereby generates a warning. I'm not sure what causes this to
happen, but as long as the model runs without it, I won't bother. Thanks
for direction to the DOE2 definitions file, that's the one I was looking
for. It describes in detail what econo-low-limit is used for and it probably
isn't relevant to my purposes. I think we can call this case
closed.</font>
<p>
<br><font size=3>On Thu, Aug 26, 2010 at 2:00 PM, Otto Schwieterman <</font><a href=mailto:oschwieterman@fhai.com target=_blank><font size=3 color=blue><u>oschwieterman@fhai.com</u></font></a><font size=3>>
wrote:</font>
<br><font size=2 color=#004080>I would tweak it in the detailed edit mode
because it is very unlikely that you can get good results by simply using
the wizard. There are too many major variables that you cannot change in
the wizard. You might as well pick the cost/energy consumption via experience
if you are not going to go into the detailed edit mode. </font>
<p><font size=2 color=#004080> </font>
<p><font size=2 color=#004080>If you simply need eQUEST to spit something
out so you have results to show I would ignore the econo-low-limit but
remember that the results mean nothing.</font>
<p><font size=2 color=#004080> </font>
<p><font size=2><b>From:</b> Adrian Gurga [mailto:</font><a href=mailto:gurga@illinois.edu target=_blank><font size=2 color=blue><u>gurga@illinois.edu</u></font></a><font size=2>]
</font>
<p><font size=3><b>Sent:</b> Thursday, August 26, 2010 1:38 PM<b><br>
To:</b> James Hansen</font>
<br><font size=3><b>Cc:</b> </font><a href="mailto:equest-users@lists.onebuilding.org" target=_blank><font size=3 color=blue><u>equest-users@lists.onebuilding.org</u></font></a>
<br><font size=3><b><br>
Subject:</b> Re: [Equest-users] Warning: ECONO-LOW-LIMIT = *UNUSED*</font>
<p><font size=3> </font>
<p><font size=3>Excellent. Thanks James. And yes, it's up to
us to figure out how to use it, which I think qualifies as "no support".
I'm sure the programmers responsible for the software are perfectly competent,
and I did not mean to suggest otherwise. I suppose what I really
meant to say was that the software has no customer support, which is understandable
because it's free. </font>
<p><font size=3> </font>
<p><font size=3>Now back to the model. So one would have to go into
the detailed mode in order to change this parameter? If one was to
work with a model only via the DD wizard as we sometimes do for order of
magnitude estimates, would it be OK to leave ecnono-low-limit unused? or
would this result in inaccurate results?</font>
<p><font size=3>On Thu, Aug 26, 2010 at 12:22 PM, James Hansen <</font><a href=mailto:JHANSEN@ghtltd.com target=_blank><font size=3 color=blue><u>JHANSEN@ghtltd.com</u></font></a><font size=3>>
wrote:</font>
<p><font size=2 color=#004080>See below. Also, the technical support
isn’t “very poor”, it’s just that the people working on technical issues
are actually programmers. It’s up to us to figure out how to use
it properly.</font>
<p><font size=2 color=#004080> </font>
<p>
<p><font size=2 color=#004080> </font>
<p><font size=2 color=#008080><b>GHT Limited</b></font><font size=2><b><br>
James Hansen, PE, LEED AP</b></font>
<p><font size=2><b>Senior Associate</b></font>
<p><font size=1>1010 N. Glebe Rd, Suite 200</font>
<p><font size=1>Arlington, VA 22201-4749</font>
<p><font size=1>703-338-5754 (Cell)</font>
<p><font size=1>703-243-1200 (Office)</font>
<p><font size=1>703-276-1376 (Fax)</font>
<p><a href=http://www.ghtltd.com/ target=_blank><font size=2 color=blue><u>www.ghtltd.com</u></font></a>
<p><font size=2 color=#3f8080><b> </b></font>
<p><font size=2 color=#004080> </font>
<p><font size=2><b>From:</b> </font><a href="mailto:equest-users-bounces@lists.onebuilding.org" target=_blank><font size=2 color=blue><u>equest-users-bounces@lists.onebuilding.org</u></font></a><font size=2>
[mailto:</font><a href="mailto:equest-users-bounces@lists.onebuilding.org" target=_blank><font size=2 color=blue><u>equest-users-bounces@lists.onebuilding.org</u></font></a><font size=2>]
<b>On Behalf Of </b>Adrian Gurga<b><br>
Sent:</b> Thursday, August 26, 2010 1:13 PM</font>
<p><font size=3><b><br>
To:</b> </font><a href="mailto:equest-users@lists.onebuilding.org" target=_blank><font size=3 color=blue><u>equest-users@lists.onebuilding.org</u></font></a><font size=3><b><br>
Subject:</b> Re: [Equest-users] Warning: ECONO-LOW-LIMIT = *UNUSED*</font>
<p><font size=3> </font>
<p><font size=3>Carol,</font>
<p><font size=3> </font>
<p><font size=3>With all due respect, "</font><font size=2>Only to
input the temperature and to look at your help screen." is not a complete
sentence. Please reply using English if you'd like to post on a listserv.
If you have advice on how to address this warning, please provide
it. Additionally, "F</font><font size=3>laming" (</font><a href="http://www.urbandictionary.com/define.php?term=flaming" target=_blank><font size=3 color=blue><u>http://www.urbandictionary.com/define.php?term=flaming</u></font></a><font size=3>) is
a behavior typically reserved for prepubescents on chat forums,
not professional listservs. Please show some professional courtesy
in your responses. Now, let's move forward amicably and discuss
the actual topic of the post.</font>
<p><font size=3> </font>
<p><font size=3>All,</font>
<p><font size=3> </font>
<p><font size=3>We all know that as eQUEST is free software, it has very
poor technical support which is why listservs like this exist.
Here is the research I've done so far. Inputting a seach for
"econo-low-limit" or even just "econo" in the eQUEST
helpfile produces no results. Are there "pull down help menus"
which discuss this topic as Carol suggests? If so, please direct
me to them. Googling "econo-low-limit" produces one relevent
hit other than this listserv, a user poses the same question I have, but
is issue is never resolved (</font><a href="http://www.energymodelhelp.com/SMF/index.php?topic=107.0" target=_blank><font size=3 color=blue><u>http://www.energymodelhelp.com/SMF/index.php?topic=107.0</u></font></a><font size=3> ).
A search of "econo-low-limit" on this listserv will yield
five results. In four of these, "econo-low-limit" is simply
listed as an input, in the fifth, it is suggested as a way of manipulating
the model. However, I cannot find anywhere on this listserv where
the warning "econo-low-limit" = unused has been discussed. Therefore,
I assume it's a reasonable to post and and I hope it will be helpful to
future users. </font>
<p><font size=3> </font>
<p><font size=3>I can't figure out where to specify an econo-low-limit
in the DD wizard, if I need to go into the detailed edit to address this,
please let me know where that variable is edited. I have attempted
to edit the files manually in notepad to specify an econo-low-limit, so
far have had no luck, but truthfully I'm not too experienced with manual
edits. If anyone could provide some assistance with where to edit
this parameter, it would be appreciated. Alternatively, if this
warning does not have detrimental impact on the outputs, I will just ignore
it.</font>
<p><font size=3> </font>
<p><font size=3>Thanks for your thoughts and comments.</font>
<p><font size=3> </font>
<p><font size=3>-- </font><font size=2 color=#8f8f8f><br>
Adrian Gurga<br>
Smart Energy Design Assistance Center<br>
University of Illinois - Urbana-Champaign</font><font size=2 color=blue><u><br>
</u></font><a href=http://www.sedac.org/ target=_blank><font size=2 color=#0060a0><u>www.sedac.org</u></font></a><font size=2 color=#8f8f8f><br>
(217) 244-4671<br>
(800) 214-7954</font>
<p><font size=3> </font>
<p><font size=3>On Thu, Aug 26, 2010 at 11:08 AM, Carol Gardner <</font><a href=mailto:cmg750@gmail.com target=_blank><font size=3 color=blue><u>cmg750@gmail.com</u></font></a><font size=3>>
wrote:</font>
<p><font size=3>That was polite, Jason. Users of this list need to be responsible
enough to at least look at the pull down help menus before asking a question
on the listserv, It is impolite and wasteful of everyone's time to not
do so. I have sympathy for someone who is learning but if they really care
to learn this skill and be in the business they need to learn to at least
try to find the answers they need. Perhaps the college systems have changed,
which would be a shame, but when I was in school I had to research and
find my own answers. Since I'm older than dirt we didn't have listservs,
Google, or any of those useful tools that now make finding answers so much
easier.<br>
<br>
I rest my case,<br>
<br>
Carol</font>
<p><font size=3> </font>
<p><font size=3>On Thu, Aug 26, 2010 at 8:11 AM, Jason Glazer <</font><a href=mailto:jglazer@gard.com target=_blank><font size=3 color=blue><u>jglazer@gard.com</u></font></a><font size=3>>
wrote:</font>
<p><font size=3>Carol,<br>
<br>
The eQUEST-user mailing list is for users of all experience levels:<br>
<br>
"The eQUEST-users mailing list is for everyone that uses the
eQUEST program. Users at every experience level are encouraged to join
this mailing list and share their questions and knowledge. Users of the
DOE-2.2 and D2Comply are also welcome. The mailing list will be a user-to-user
support forum for eQUEST, DOE-2.2, and D2Comply."<br>
<br>
We appreciate your contribution but please either reply politely or not
at all.<br>
<br>
Jason</font>
<p><font size=3><br>
<br>
On 8/26/2010 9:29 AM, Carol Gardner wrote:</font>
<br><font size=3>Only to input the temperature and to look at your help
screen. This is<br>
something you really should be able to figure out yourself. If you can't<br>
try another profession.<br>
<br>
Carol<br>
<br>
On Tue, Aug 24, 2010 at 11:55 AM, Adrian Gurga <</font><a href=mailto:gurga@illinois.edu target=_blank><font size=3 color=blue><u>gurga@illinois.edu</u></font></a>
<p><font size=3><mailto:</font><a href=mailto:gurga@illinois.edu target=_blank><font size=3 color=blue><u>gurga@illinois.edu</u></font></a><font size=3>>>
wrote:<br>
<br>
I am working with a model and am working with the following
warning<br>
whenever it runs the BDL Load File Log<br>
<br>
Line 1336: Warning Encountered:<br>
INPUT-TYPE COEFFICIENTS ..<br>
ECONO-LOW-LIMIT = *UNUSED*<br>
<br>
Any ideas?<br>
<br>
--<br>
Adrian Gurga<br>
Smart Energy Design Assistance Center<br>
University of Illinois - Urbana-Champaign</font>