[Equest-users] Maximum limits for zones, systems etc.
Patrick J. O'Leary, Jr.
poleary1969 at gmail.com
Thu Aug 26 11:38:16 PDT 2010
i have a similar question on the use of electrical meters, from the
doe22vol3-topics.pdf file, page 331 (by pagen umber, or by the (page 333
of 387), this is the pertinent text:
"This capability is now extended by adding the ELEC-METER command that
allows you to define up to *25* meters to which electrical equipment can
be attached. In addition, the concept of "meter levels" is added; this
allows you to define sub- metering of usage and demand."
i note below the limit is listed as: ELEC-METER 100
where does this come from?
i have tried creating a building meter, created/assigned 44 submeters to
it, and then not had any of the meters over 25 report any electrical
consumption.
is the limit 100 building meters assigned to a utility and each meter
can then only have 25 sub-meters attached to it?
On 8/26/10 11:04 AM, Maryanne Mason wrote:
>
> Hi Scott
>
> I noticed from your list that 30 chillers are allowed, however, every
> time I try to use more than 10 chillers, I get major errors. Does this
> mean that only 10 chillers are allowed per circulation loop?
>
> Regards,
>
> *MaryAnne Mason*
> Mechanical Engineer
> Process Infrastructure
>
> Ausenco Sandwell
> 1016B Sutton Drive, Suite 100
> Burlington ON L7L 6B8
> Canada
>
> *T* +1 905 319 1698
> *F* +1 905 319 1801
> *E* maryanne.mason at ausencosandwell.com
> <mailto:maryanne.mason at ausencosandwell.com>
> *W* www.ausenco.com <http://www.ausenco.com/>
>
> *From:* equest-users-bounces at lists.onebuilding.org
> [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of
> *Scott Criswell
> *Sent:* Wednesday, August 25, 2010 11:26 AM
> *To:* Bishop, Bill
> *Cc:* EQuest
> *Subject:* Re: [Equest-users] Maximum limits for zones, systems etc.
>
> Here is a rundown on the "MAX DEF" (maximum # of components) that can
> be defined in the version of DOE-2.2 distributed w/ eQUEST version
> 3.63b, as well as one change that will be present in the upcoming
> release of v3.64.
>
> DOE-2.2 version 47d 47h2
> eQUEST version 3.63b 3.64
> -------------------------------
> COMMAND NAME MAX MAX
> DEF DEF
> -------------------------------
> SCHEDULE 2048
> WEEK-SCHEDULE 2048
> DAY-SCHEDULE 4096
> BUILDING-SHADE 1024
> CONSTRUCTION 8192
> GLASS-TYPE 1024
> SPACE 4096
> EXTERIOR-WALL 8192
> WINDOW 8192
> INTERIOR-WALL 8192 12288
> UNDERGROUND-WALL 8192
> DESIGN-DAY 2
> LAYERS 8192
> MATERIAL 8192
> REPORT-BLOCK 64
> HOURLY-REPORT 16
> RUN-PERIOD 15
> PARAMETER 500
> DOOR 1024
> WEIGHTING-FACTOR 4096
> FIXED-SHADE 1024
> HOLIDAYS 2
> POLYGON 32768
> FLOOR 1024
> GLASS-TYPE-CODE 128
> SYSTEM 2048
> ZONE 4096
> CURVE-FIT 512
> PUMP 1280
> CIRCULATION-LOOP 1280
> CHILLER 30
> BOILER 30
> DW-HEATER 1280
> HEAT-REJECTION 30
> PV-MODULE 30
> ELEC-GENERATOR 30
> THERMAL-STORAGE 30
> HEAT-EXCHANGER 30
> EQUIP-CTRL 30
> LOAD-MANAGEMENT 20
> ELEC-METER 100
> FUEL-METER 15
> STEAM-METER 15
> CHW-METER 15
> GROUND-LOOP-HX 30
> LUMINAIRE-TYPE 64
> LIGHTING-SYSTEM 64
> LAMP-TYPE 64
> COMPONENT-COST 100
> UTILITY-RATE 30
> BLOCK-CHARGE 200
> RATCHET 100
> WINDOW-LAYER 32
>
>
>
> Bishop, Bill wrote:
>
> I'm tempted to include multiple buildings in one model (a dormitory
> complex) and I'm wondering what program limits I might bump up
> against. Maximum number of zones? Systems? Surfaces? Anything else?
>
> Thanks,
>
> Bill
>
> *William Bishop, PE, BEMP, LEED^® AP **|** Pathfinder Engineers &
> Architects LLP*
>
> Mechanical Engineer
>
> 134 South Fitzhugh Street
> Rochester, NY 14608
> T: (585) 325-6004 Ext. 114
> F: (585) 325-6005
>
> wbishop at pathfinder-ea.com <mailto:wbishop at pathfinder-ea.com>
>
> www.pathfinder-ea.com <http://www.pathfinder-ea.com>
>
> P Sustainability -- less is more.
>
>
> ------------------------------------------------------------------------
>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message toEQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG <mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100826/04414f15/attachment.htm>
More information about the Equest-users
mailing list