[Equest-users] Maximum limits for zones, systems etc.
Maryanne Mason
maryanne.mason at ausencosandwell.com
Thu Aug 26 11:04:18 PDT 2010
Hi Scott
I noticed from your list that 30 chillers are allowed, however, every time I
try to use more than 10 chillers, I get major errors. Does this mean that
only 10 chillers are allowed per circulation loop?
Regards,
MaryAnne Mason
Mechanical Engineer
Process Infrastructure
Ausenco Sandwell
1016B Sutton Drive, Suite 100
Burlington ON L7L 6B8
Canada
T +1 905 319 1698
F +1 905 319 1801
E <mailto:maryanne.mason at ausencosandwell.com>
maryanne.mason at ausencosandwell.com
W <http://www.ausenco.com/> www.ausenco.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Scott
Criswell
Sent: Wednesday, August 25, 2010 11:26 AM
To: Bishop, Bill
Cc: EQuest
Subject: Re: [Equest-users] Maximum limits for zones, systems etc.
Here is a rundown on the "MAX DEF" (maximum # of components) that can be
defined in the version of DOE-2.2 distributed w/ eQUEST version 3.63b, as
well as one change that will be present in the upcoming release of v3.64.
DOE-2.2 version 47d 47h2
eQUEST version 3.63b 3.64
-------------------------------
COMMAND NAME MAX MAX
DEF DEF
-------------------------------
SCHEDULE 2048
WEEK-SCHEDULE 2048
DAY-SCHEDULE 4096
BUILDING-SHADE 1024
CONSTRUCTION 8192
GLASS-TYPE 1024
SPACE 4096
EXTERIOR-WALL 8192
WINDOW 8192
INTERIOR-WALL 8192 12288
UNDERGROUND-WALL 8192
DESIGN-DAY 2
LAYERS 8192
MATERIAL 8192
REPORT-BLOCK 64
HOURLY-REPORT 16
RUN-PERIOD 15
PARAMETER 500
DOOR 1024
WEIGHTING-FACTOR 4096
FIXED-SHADE 1024
HOLIDAYS 2
POLYGON 32768
FLOOR 1024
GLASS-TYPE-CODE 128
SYSTEM 2048
ZONE 4096
CURVE-FIT 512
PUMP 1280
CIRCULATION-LOOP 1280
CHILLER 30
BOILER 30
DW-HEATER 1280
HEAT-REJECTION 30
PV-MODULE 30
ELEC-GENERATOR 30
THERMAL-STORAGE 30
HEAT-EXCHANGER 30
EQUIP-CTRL 30
LOAD-MANAGEMENT 20
ELEC-METER 100
FUEL-METER 15
STEAM-METER 15
CHW-METER 15
GROUND-LOOP-HX 30
LUMINAIRE-TYPE 64
LIGHTING-SYSTEM 64
LAMP-TYPE 64
COMPONENT-COST 100
UTILITY-RATE 30
BLOCK-CHARGE 200
RATCHET 100
WINDOW-LAYER 32
Bishop, Bill wrote:
I'm tempted to include multiple buildings in one model (a dormitory complex)
and I'm wondering what program limits I might bump up against. Maximum
number of zones? Systems? Surfaces? Anything else?
Thanks,
Bill
William Bishop, PE, BEMP, LEEDR AP | Pathfinder Engineers & Architects LLP
Mechanical Engineer
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
wbishop at pathfinder-ea.com
www.pathfinder-ea.com
P Sustainability - less is more.
_____
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100826/333fcfd4/attachment.htm>
More information about the Equest-users
mailing list