[Equest-users] Interior Blind Savings

Karen Walkerman kwalkerman at gmail.com
Thu Jan 15 09:36:02 PST 2009


This effect changes depending on the type of blinds and the type of glass
being used.  A highly reflective blind with clear glass will allow much of
the solar radiation to reflect back outside of the building, but, a higher
performance glass, which blocks solar radiation, will also block solar
radiation from leaving, even with a highly reflected blind!

--
Karen


On Thu, Jan 15, 2009 at 12:18 PM, Dana Troy <DTroy at glumac.com> wrote:

>  Josh,
>
>
>
> There is a previous discussion on interior blinds in the archives:
> http://lists.onebuilding.org/htdig.cgi/bldg-sim-onebuilding.org/2007-June/005640.html
>
>
>
> As for the savings, $25 per year seems about right. Interior blinds *do
> not stop the solar radiation from entering the space* even though the
> occupants might feel cooler with the blinds drawn.
>
>
>
> When the blinds are down, the occupant does not have the sun shining
> directly on them, which makes them feel cooler than if the blinds were up
> with the sun shining on them. However, when the blinds are down, the *sun
> is still heating up the air space between the blinds and the glass*. That
> air then eventually mixes with the air in the space, which still needs to be
> cooled. eQUEST does not take into consideration that the hot air near the
> windows might take a while to get to a thermostat across the room.
>
>
>
> We had a family residence that had tinted plastic blinds on the inside of
> their floor to ceiling south facing windows. In the summers, the room would
> get to 90+ even with the blinds drawn. We installed exterior blinds about 2
> to 3 feet from the windows and the temperature never got above 80.
>
>
>
> Hope this helps.
>
>
> *Dana Troy*
>
> Energy Analyst
>
> LEED(R) Accredited Professional
>
> [image: http://www.glumac.com/glumacsig.gif] <http://www.glumac.com/>
>   ------------------------------
>
> 320 SW Washington, Suite 200
> Portland, OR 97204-2640
> T.  503.227.5280  F. 503.274.7674
>
> D. 503.345.6286
>
> dtroy at glumac.com
>
> *Thinking. Inside the building.*
> www.glumac.com
>
> [image: http://www.glumac.com/consider.gif]
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Josh Doherty
> *Sent:* Thursday, January 15, 2009 8:31 AM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] Interior Blind Savings
>
>
>
> Hello,
>
> I am using eQUEST to determine the potential savings associated with using
> interior blinds in a 2-story 1000 square foot lobby area with floor to
> ceiling windows on two exterior sides.  The model behaves like I would
> expect.  The results indicate the blind open and closed schedules play a
> very important role in the savings.  This is especially true in such a
> climate where there are cold winters (solar gain into the interior space is
> beneficial) and hot summers (solar gain into the interior space is not
> desired).  However, the best case savings I can achieve is around
> $25.00/year.  I had expected to save more money using the blinds.  Has
> anybody else played around with blinds in eQUEST?  Did you find any
> significant savings?
>
>
>
> *Josh Doherty*
>
> *DC Engineering*
>
> 123 W. Spruce Street
>
> Missoula, MT 59802
>
> Phone: (406) 829-8828   Ext. 121
>
> Fax:  (406) 829-8829
>
> jdoherty at dcengineering.net
>
>
>
>
>
>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>