Josh,
There is a previous discussion on interior blinds in the archives:
http://lists.onebuilding.org/htdig.cgi/bldg-sim-onebuilding.org/2007-Jun
e/005640.html
As for the savings, $25 per year seems about right. Interior blinds do
not stop the solar radiation from entering the space even though the
occupants might feel cooler with the blinds drawn.
When the blinds are down, the occupant does not have the sun shining
directly on them, which makes them feel cooler than if the blinds were
up with the sun shining on them. However, when the blinds are down, the
sun is still heating up the air space between the blinds and the glass.
That air then eventually mixes with the air in the space, which still
needs to be cooled. eQUEST does not take into consideration that the hot
air near the windows might take a while to get to a thermostat across
the room.
We had a family residence that had tinted plastic blinds on the inside
of their floor to ceiling south facing windows. In the summers, the room
would get to 90+ even with the blinds drawn. We installed exterior
blinds about 2 to 3 feet from the windows and the temperature never got
above 80.
Hope this helps.
Dana Troy
Energy Analyst
LEED(r) Accredited Professional
<http://www.glumac.com/>
________________________________
320 SW Washington, Suite 200
Portland, OR 97204-2640
T. 503.227.5280 F. 503.274.7674
D. 503.345.6286
dtroy at glumac.com
Thinking. Inside the building.
www.glumac.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Josh
Doherty
Sent: Thursday, January 15, 2009 8:31 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Interior Blind Savings
Hello,
I am using eQUEST to determine the potential savings associated with
using interior blinds in a 2-story 1000 square foot lobby area with
floor to ceiling windows on two exterior sides. The model behaves like
I would expect. The results indicate the blind open and closed
schedules play a very important role in the savings. This is especially
true in such a climate where there are cold winters (solar gain into the
interior space is beneficial) and hot summers (solar gain into the
interior space is not desired). However, the best case savings I can
achieve is around $25.00/year. I had expected to save more money using
the blinds. Has anybody else played around with blinds in eQUEST? Did
you find any significant savings?
Josh Doherty
DC Engineering
123 W. Spruce Street
Missoula, MT 59802
Phone: (406) 829-8828 Ext. 121
Fax: (406) 829-8829
jdoherty at dcengineering.net
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090115/2cae137e/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 50453 bytes
Desc: image001.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090115/2cae137e/attachment.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 1425 bytes
Desc: image003.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090115/2cae137e/attachment-0001.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2385 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090115/2cae137e/attachment.jpeg>
More information about the Equest-users
mailing list