[Equest-users] Energy Use due to Building Insulation Levels
David S Eldridge
DSE at grummanbutkus.com
Wed Jan 14 12:06:34 PST 2009
People can make an argument that the total energy usage due to wall/roof insulation levels can at times seem like a small percentage of the total energy use in some buildings.
This might also be true of the value of a green roof on a 40 story building - of course the effect is only 1/40th of the effect on an identical footprint one story building. But for that one level the effect is just as important as it would be for the top level (only level?) of the shorter building.
There still is an absolute amount of energy involved that can be directly affected by the selection of an optimal insulation value. Just because the building is dominated by ventilation loads doesn't mean there can't be a real savings by choosing the best insulation levels.
The idea might be worth one or two parametric runs of your simulation.
David
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Karen Walkerman
Sent: Wednesday, January 14, 2009 12:30 PM
To: James Geers
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] CO2 sensors and outside air reduction. LEED for schools & ASHRAE 90.1-2004
First of all, changing the R-value of walls and roofs can have a significant impact on overall energy use, especially in locations with extreme outdoor conditions. Granted, with more ventilation air required, the envelope is responsible for a smaller piece of the overall energy use of the building.
So, to reduce ventilation air energy use:
A. Use energy recovery ventilation! In moderate climates, energy recovery ventilation might not make a whole lot of sense, but climates where heat is needed much of the year, ERV's make a lot of sense!
B. Turn off the ventilation when it's not needed! This includes time clocks and CO2 sensors. I've seen alot of schools with old unit ventilators in each classroom. These unit ventilators often stay on all night, bringing cold air into the classroom and wasting tons of heat!
Regarding your CO2 questions:
1. Decoupling the ventilation air distribution system from an airside air conditioning system allows for the most options. Installation of CO2 sensors in each space with corresponding ventilation air VAV supply results in ventilation air being supplied only where it's needed. But, this can be cost-prohibitive, and where lots of spaces see similar occupancy, completely unnecessary.
2. It is permissible to vary the CFM between the base case and design case for ASHRAE 90.1-2004 Appendix G (G.3.1.2.5 Exception), some programs, including eQuest model DCV, so no change in ventilation rate is required, just activation of DCV.
3. In a building with 40 classrooms, you could create one branch of each type of space (classrooms, offices), and control ventilation to each block of spaces. For high-use areas with varying schedules (caffeteria, gymnasium and auditorium), have each space have it's own demand controlled ventilation.
5. If you model this in eQuest, you can still do blocks of classrooms, especially if your occupancy schedule is the same for each classroom.
Hope this helps,
--
Karen
On Wed, Jan 14, 2009 at 12:01 PM, James Geers <jgeers at sfa-architects.com<mailto:jgeers at sfa-architects.com>> wrote:
Previous posts have confirmed my suspicions that increasing the R-value of walls and roofs has little to no effect on energy performance, due to the outside air requirements.
This raises a few questions:
1. What is the most effective way to use CO2 sensors to dramatically reduce the outside air requirements?
1. Is it permissible to vary the CFM between the base case and design case in the ASHRAE 90.1-2004 Appendix G model, and consequently in the LEED template?
1. What is the most effective way to use CO2 monitoring in a building with 40 classrooms and other large spaces. If one sensor is triggered, won't the entire zone get fresh air and defeat the energy savings?
1. If every classroom has a sensor, does any one have experience with the replaceable / Mail in sensors to assure their accuracy.
1. If I model this in Equest, do I need a zone for every classroom.
Thank you for any feed back.
James F. Geers
Registered Architect
LEED Accredited Professional
SFA Architects
300 West Fourth Street
Cincinnati, Ohio 45202
513.721.0600
513.721.0611 (fax)
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090114/99a8880f/attachment.htm>
More information about the Equest-users
mailing list