Kevin Kyte
kkyte at robsonwoese.com
Mon Jan 12 11:08:40 PST 2009
In detailed edit, one can assign polygons to wall components. Make the polygon to resemble the elevation and assign to the wall component. Getting into custom rendering will certainly require a trial and error adjustment.
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Brian Fountain
Sent: Monday, January 12, 2009 1:59 PM
To: Ryan Lacey; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] EQUEST Partially Below Grade Wall
As you have guessed, you cannot do this in the wizard. So, in the wizard, create the u/g wall. Then in detailed mode, set the u/g wall height to 5'. Then create new exterior walls (copying upper walls) and set their height to 4' with their Z value at 5' -- one for each side of the basement as appropriate, linked to the appropriate vertex.
It sounds complicated but is fairly straight forward when you get going.
Bonne chance,
Brian
Ryan Lacey wrote:
Hello,
I need to model a wall that is partially below grade. My basement is only about 4' below grade & using the wizard so far I cant figure out a way to represent this. What is the easiest way to go about this? I am trying to stay in the wizard as long as possible.
[cid:image001.jpg at 01C974BF.44E2CE60]
[cid:image002.jpg at 01C974BF.44E2CE60]
Thanks,
Ryan Lacey
LEED AP
Petersen Engineering, Inc.
PO Box 4774
6 Market Square
Portsmouth, NH 03801
Phone 603.436.4233 x113
Fax 603.436.4294
www.petersenengineering.com<http://www.petersenengineering.com>
ryan at petersenengineering.com<mailto:ryan at petersenengineering.com>
________________________________
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
________________________________
No virus found in this incoming message.
Checked by AVG.
Version: 7.5.552 / Virus Database: 270.10.5/1885 - Release Date: 1/9/2009 7:59 PM
________________________________
"This message is for the designated recipient only and may contain privileged, proprietary, or otherwise private information. If you are not the intended recipient, you are hereby notified that any disclosure, copying, distribution, or the taking of any action in reliance on the contents of this information is strictly prohibited. If you have received this transmission in error, please notify the sender immediately by e-mail and delete the original message."
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090112/349ebd9c/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 6924 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090112/349ebd9c/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 16340 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090112/349ebd9c/attachment-0001.jpg>
More information about the Equest-users
mailing list