As you have guessed, you cannot do this in the wizard. So, in the
wizard, create the u/g wall. Then in detailed mode, set the u/g wall
height to 5'. Then create new exterior walls (copying upper walls) and
set their height to 4' with their Z value at 5' -- one for each side of
the basement as appropriate, linked to the appropriate vertex.
It sounds complicated but is fairly straight forward when you get going.
Bonne chance,
Brian
Ryan Lacey wrote:
>
> Hello,
>
> I need to model a wall that is partially below grade. My basement is
> only about 4' below grade & using the wizard so far I cant figure out
> a way to represent this. What is the easiest way to go about this? I
> am trying to stay in the wizard as long as possible.
>
>
>
>
>
>
>
> Thanks,
>
>
>
> Ryan Lacey
>
> LEED AP
>
> Petersen Engineering, Inc.
>
> PO Box 4774
>
> 6 Market Square
>
> Portsmouth, NH 03801
>
> Phone 603.436.4233 x113
>
> Fax 603.436.4294
>
> www.petersenengineering.com <http://www.petersenengineering.com>
>
> ryan at petersenengineering.com
>
>
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
> ------------------------------------------------------------------------
>
> No virus found in this incoming message.
> Checked by AVG.
> Version: 7.5.552 / Virus Database: 270.10.5/1885 - Release Date: 1/9/2009 7:59 PM
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090112/a595c93b/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 6924 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090112/a595c93b/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 16340 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090112/a595c93b/attachment-0001.jpeg>
More information about the Equest-users
mailing list