[Equest-users] eQuest supply cfm and OA
Paul Erickson
perickson at aeieng.com
Wed Sep 24 17:19:43 PDT 2008
Marcus,
You need to remove any specification of OA flow at the zone level. In eQUEST, zonal values often/always(?) trump system values. In order to remove the value and leave the cell blank, right click and hit "restore default".
Paul
Paul Erickson
Sustainable Team Leader
Affiliated Engineers, Inc
www.aeieng.com ( http://www.aeieng.com/ )
608.236.1112
303.859.7523 - c
( mailto:mschrader at aeieng.com )
PPlease consider the environment before printing thismessage.
>>> "Marcus Eliason" <meliason at essexco.com> 9/24/2008 3:16 PM >>>
Hello,
I am working on a building comprising three main zones. One of these zones
has a 100% OA requirement. I would like for eQuest to auto size the supply
cfm for all zones, thus in the wizard I do not specify any flowrate or OA%.
Once in the detailed mode, under the "Outdoor Air" tab and the "Outside Air
and Economizer" screen, I set the minimum outside air ratio to 1.0. After
running the simulation and checking the SV-A report, it says that the OA%
for this zone for the simulation was actually 3%, not the 100% this zone
requires. Can anyone tell me how to force eQuest to 100% OA? I looked at
the help for the outside air ratio and it stated that it was for winter
heating periods. Is there a work around for this? I have attached the .inp
and .pd2 files for this project.
Thank you for your assistance.
Marcus Eliason
Essex Engineering Corporation
404.365.9482
meliason at essexco.com