<DIV>Marcus,</DIV>
<DIV><BR>You need to remove any specification of OA flow at the zone level.  In eQUEST, zonal values often/always(?) trump system values.  In order to remove the value and leave the cell blank, right click and hit "restore default".  </DIV>
<DIV> </DIV>
<DIV>Paul</DIV>
<DIV> </DIV>
<DIV> </DIV>
<DIV> </DIV>
<DIV>
<DIV><FONT size=2>Paul Erickson</FONT></DIV>
<DIV><FONT size=2>Sustainable Team Leader</FONT></DIV>
<DIV><FONT size=2>Affiliated Engineers, Inc</FONT></DIV>
<DIV><A href="http://www.aeieng.com/"><FONT size=2>www.aeieng.com</FONT></A></DIV>
<DIV><FONT size=2>608.236.1112</FONT></DIV>
<DIV><FONT size=2>303.859.7523 - c</FONT></DIV>
<DIV>
<DIV>
<DIV><A href="mailto:mschrader@aeieng.com"></A></DIV><FONT face=Arial></FONT></DIV>
<DIV>
<DIV><SPAN lang=NL style="FONT-SIZE: 13.5pt; COLOR: green; FONT-FAMILY: Webdings">P</SPAN><FONT face=Verdana color=navy size=2><SPAN lang=NL style="FONT-SIZE: 10pt; COLOR: navy; FONT-FAMILY: Verdana"> </SPAN></FONT><FONT face=Verdana color=green size=1><SPAN style="FONT-SIZE: 7.5pt; COLOR: green; FONT-FAMILY: Verdana">P</SPAN></FONT><FONT face=Verdana color=green size=1><SPAN lang=NL style="FONT-SIZE: 7.5pt; COLOR: green; FONT-FAMILY: Verdana">lease consider the environment before printing this</SPAN></FONT><FONT face=Verdana color=navy size=2><SPAN lang=NL style="FONT-SIZE: 10pt; COLOR: navy; FONT-FAMILY: Verdana"> </SPAN></FONT><FONT face=Verdana color=green size=1><SPAN style="FONT-SIZE: 7.5pt; COLOR: green; FONT-FAMILY: Verdana">message.</SPAN></FONT></DIV></DIV></DIV><BR><BR>>>> "Marcus Eliason" <meliason@essexco.com> 9/24/2008 3:16 PM >>><BR><BR>Hello,<BR><BR>I am working on a building comprising three main zones.  One of these zones<BR>has a 100% OA requirement.  I would like for eQuest to auto size the supply<BR>cfm for all zones, thus in the wizard I do not specify any flowrate or OA%.<BR>Once in the detailed mode, under the "Outdoor Air" tab and the "Outside Air<BR>and Economizer" screen, I set the minimum outside air ratio to 1.0.  After<BR>running the simulation and checking the SV-A report, it says that the OA%<BR>for this zone for the simulation was actually 3%, not the 100% this zone<BR>requires.  Can anyone tell me how to force eQuest to 100% OA?  I looked at<BR>the help for the outside air ratio and it stated that it was for winter<BR>heating periods.  Is there a work around for this?  I have attached the .inp<BR>and .pd2 files for this project.<BR><BR>Thank you for your assistance.<BR><BR>Marcus Eliason<BR>Essex Engineering Corporation<BR>404.365.9482<BR>meliason@essexco.com<BR><BR></DIV></BODY></HTML>