[Bldg-sim] eQuest ERV systems
    John Aulbach 
    jra_sac at yahoo.com
       
    Fri Mar 15 09:51:27 PDT 2024
    
    
  
 Thank you, my friend !! I love short, to the point answers.
For a multi family, needs to be system per zone.
John
    On Friday, March 15, 2024 at 02:30:02 AM MST, Brian Fountain <bfountain at greensim.com> wrote:  
 
 The HP system type does not accept the ERV keywords. 
Either change system type to PSZ or PVVT and set up a system per zone.  Or use 2.3 and the DOAS system type for the ERV.On Mar 15, 2024, at 12:21 a.m., John Aulbach via Bldg-sim <bldg-sim at lists.onebuilding.org> wrote:
Hi All.
I am trying to add ERVs to split system HP systems in eQuest, and the program doesn't ungrey the input tabs.  What am I doing wrong?
Thanks,
John R. Aulbach, PE
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
  
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20240315/1f551873/attachment.htm>
    
    
More information about the Bldg-sim
mailing list