[Bldg-sim] eQuest ERV systems
Brian Fountain
bfountain at greensim.com
Fri Mar 15 02:29:57 PDT 2024
The HP system type does not accept the ERV keywords.
Either change system type to PSZ or PVVT and set up a system per zone. Or use 2.3 and the DOAS system type for the ERV.
On Mar 15, 2024, 12:21 a.m., at 12:21 a.m., John Aulbach via Bldg-sim <bldg-sim at lists.onebuilding.org> wrote:
>Hi All.
>I am trying to add ERVs to split system HP systems in eQuest, and the
>program doesn't ungrey the input tabs. What am I doing wrong?
>Thanks,
>John R. Aulbach, PE
>
>------------------------------------------------------------------------
>