[Bldg-sim] eQuest ERV systems

Brian Fountain bfountain at greensim.com
Fri Mar 15 02:29:57 PDT 2024


The HP system type does not accept the ERV keywords. 

Either change system type to PSZ or PVVT and set up a system per zone.  Or use 2.3 and the DOAS system type for the ERV.

On Mar 15, 2024, 12:21 a.m., at 12:21 a.m., John Aulbach via Bldg-sim <bldg-sim at lists.onebuilding.org> wrote:
>Hi All.
>I am trying to add ERVs to split system HP systems in eQuest, and the
>program doesn't ungrey the input tabs.  What am I doing wrong?
>Thanks,
>John R. Aulbach, PE
>
>------------------------------------------------------------------------
>
>_______________________________________________
>Bldg-sim mailing list
>http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>To unsubscribe from this mailing list send  a blank message to
>BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20240315/5cd5da24/attachment.htm>


More information about the Bldg-sim mailing list