Another option is to export the idf file (or copy the final idf from the
OpenStudio output folders if there are measures) and run the simulation
using EP-Launch (or equivalent). The eso will automatically be converted
with the ReadVarsESO post-processer and saved as a csv file.
I don't know if there's a way to run ReadVarsESO within the OpenStudio
workflow.
Mike
On 6/17/2019 9:04 AM, Gurneet Singh via Bldg-sim wrote:
> Hi Karol,
>
> You can use the openstudio measure to export an output variable in csv
> or xls file format. You have to use this in conjunction with Add
> Output Variable measure.
>
> Add Output Variable: https://bcl.nrel.gov/node/37843
> Export Output Variable : https://bcl.nrel.gov/node/83268
>
> I hope it helps.
>
> Regards
>
> Gurneet Singh
> Director
>
> Environmental Design Solutions Pvt. Ltd.
> D-1/25, Vasant Vihar, New Delhi 110057
>
> [m] +91 9899240140 [t] +91 11 2614 7085 [f] +91 11 4056 8633
> gurneet at edsglobal.com <mailto:gurneet at edsglobal.com> |
> www.edsglobal.com <http://www.edsglobal.com/>
>
>
> On Mon, Jun 17, 2019 at 4:18 PM Karol Bandurski via Bldg-sim
> <bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>> wrote:
>
> Dear Experts,
>
> We start work with student in OpenStudio. Now we would like to
> explore hourly results.
>
> 1)Is some simple way to export all hourly results to *.csv / *.xls
> format?
>
> 2)We try to use DView. But it is not manage to open file, it close
> itself. What could be wrong…
>
> Our file:
>
> https://www.dropbox.com/s/7c87etxszrlwbiz/eplusout.sql?dl=0
>
> Kind regards,
> Karol
>
> --------------------------------------------------------------------
>
> Karol BANDURSKI M. Sc.
>
> Faculty of Civil and Environemntal Engeneering
>
> Division of Heating, Air Conditioning and Air Protection
>
> Poznan University of Technology
>
> https://www.researchgate.net/profile/Karol_Bandurski
>
> www.put.poznan.pl/~karol.bandurski
> <http://www.put.poznan.pl/~karol.bandurski>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
> <mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20190617/12cc5b27/attachment-0002.html>
More information about the Bldg-sim
mailing list