[Bldg-sim] NECB - MURB Reference Heating Type

Aaron Smith asmith at mreng.ca
Tue Feb 19 11:34:58 PST 2019


Hi David,

 

Thanks for your comments, much appreciated.  I agree that WLHP systems are somewhere in between 1 and 2 and the baseline should realistically utilize some kind of central heating and/or cooling system.  Based on my recent reply to Chris, I’m going to go with the same system you suggest - PTHP with electric resistance auxiliary heat.  I’ll post up a reply if I learn anything more definitive.

 

Aaron

 


Aaron Smith, P.Eng

Principal, Mechanical Engineer

LEED® AP BD+C, BEMP, BEAP, CGD

 

M&R Engineering Ltd.

 

From: David Eldridge [mailto:DEldridge at grummanbutkus.com] 
Sent: February-18-19 5:34 PM
To: Aaron Smith <asmith at mreng.ca>; 'Chris Hadlock' <cjhadlock at gmail.com>; bldg-sim at lists.onebuilding.org
Subject: RE: [Bldg-sim] NECB - MURB Reference Heating Type

 

One of the interesting aspects of this is the link to unitary products for instance would include certifications for water-cooled equipment consistent with a WLHP system as you mentioned Aaron – if the code just said “unitary” it would be clear - it’s only that the Table 8 reference uses the word “air-cooled” instead of applying to all unitary equipment so that a WLHP system seems to be left out of the matrix.

 

1)      Central CHW & HW w/ FCU – use identical

2)      Air-cooled unitary – use identical

3)      PTHP – use identical

4)      Other – use through-the-wall baseline

 

It’s strange to me that the WLHP option which I’d consider to be “in the middle” of the options above as sort of an option 1.5 is excluded and then you are left in “through-the-wall unit purgatory” where the baseline system is partially defined. i.e. if the fully applied system with boilers, chillers, and FCU is on one edge of the range and PTHP are on the other end of the range, why wouldn’t WLHP fit in there?

 

That said, it seems to be how it reads. So to your question, you mentioned 8.4.4.9.4 and that your sample compliance building used air-to-air heat pumps with electric resistance heat, which makes sense that a TTW unit in practice is going to be heat pump and/or electric resistance heat. A furnace option would not be part of a TTW unit either. If the baseline is supposed to make sense that is – I think an argument could be made that on an annual basis the WLHP system takes primary heat from the boiler more than the compressors for cold climates, but I’m not an expert in NECB so you’d be best positioned to comment there whether it calls for a hybrid system or not.

 

It would be pretty contrived to have a baseline that used an air-to-air heat pump as primary and then had auxiliary hot water – in practice any building that went to the trouble to add the hot water system’s cost would tend to use it as the primary system. The combo that makes practical sense is for the auxiliary heat to be electric resistance.

 

David

 

 

 

David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP

Associate

 

Direct: (847) 316-9224 | Mobile: (773) 490-5038

 

Grumman/Butkus Associates | 820 Davis Street, Suite 300 | Evanston, IL 60201

Energy Efficiency Consultants and Sustainable Design Engineers

 

 <http://grummanbutkus.com/> grummanbutkus.com |  <http://grummanbutkus.com/blog> Blog |  <https://www.facebook.com/pages/GrummanButkus-Associates/1385285015032526> Facebook |  <https://twitter.com/grummanbutkus> Twitter

 

From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Aaron Smith via Bldg-sim
Sent: Monday, February 18, 2019 10:44 AM
To: 'Chris Hadlock' <cjhadlock at gmail.com <mailto:cjhadlock at gmail.com> >
Cc: bldg-sim at lists.onebuilding.org <mailto:bldg-sim at lists.onebuilding.org> 
Subject: Re: [Bldg-sim] NECB - MURB Reference Heating Type

 

Hi Chris,

 

Thanks for your response.  It would make sense if the Reference Building were also a WLHP but based on AHRI definitions I think a WHLP is pretty clearly not:

a.      an “air-cooled unitary <http://www.ahrinet.org/Certification/AHRI-Certification-Programs/Unitary-Air-Conditioner-Equipment> ” product,

b.      a packaged terminal air conditioner <http://www.ahrinet.org/Certification/AHRI-Certification-Programs/Packaged-Terminal-Air-Conditioners>  or heat pump <http://www.ahrinet.org/Certification/AHRI-Certification-Programs/Packaged-Terminal-Heat-Pumps> , or

c.      a fan coil.

 

A WLHP is water-cooled unitary product.

 

If they simply said “unitary” or “air-cooled or water-cooled unitary” then it would makes sense to me that you model an identical system but they specifically state “air-cooled unitary”.

Aaron

 


Aaron Smith, P.Eng

Principal, Mechanical Engineer

LEED® AP BD+C, BEMP, BEAP, CGD

 

M&R Engineering Ltd.

 

From: Chris Hadlock [mailto:cjhadlock at gmail.com] 
Sent: February-18-19 11:27 AM
To: Aaron Smith <asmith at mreng.ca <mailto:asmith at mreng.ca> >
Cc: bldg-sim at lists.onebuilding.org <mailto:bldg-sim at lists.onebuilding.org> 
Subject: Re: [Bldg-sim] NECB - MURB Reference Heating Type

 

Hi Aaron,

 

The way I would interpret it is the Reference system will be identical to your Proposed system (i.e. WLHP connected to fossil fuel boiler). If you had a air-source, water-source (i.e. river, lake) or ground-source, then you would have to worry about auxiliary heating (per Section 8.4.4.13.2). The "through-the-wall" system only applies in the otherwise case (i.e. when your system is not one of the ones listed). 

 

This is my interpretation - I'd be interested to hear others.

 

Chris

 

On Sun, Feb 17, 2019 at 10:10 PM Aaron Smith via Bldg-sim <bldg-sim at lists.onebuilding.org <mailto:bldg-sim at lists.onebuilding.org> > wrote:

Hello,

 

I’ve got a question about the NECB Reference Building heating system type for Multi-Unit Residential Buildings.  Specifically what should it be when you have water-loop heat pumps connected to a fossil fuel boiler?

 

Table 8.4.4.7.-A of the 2015 NECB states that Reference Building HVAC systems for Multi-Unit Residential areas are:

 

“Where the proposed building or space is heated as well as being cooled with an air-cooled unitary, packaged terminal or room air conditioner (or heat pumps), or fan coils, the reference building or space's HVAC system shall be modeled as being identical to that of the proposed building or space; otherwise, the reference building or space shall use through-the-wall systems.”

 

I’d consider water-loop heat pumps to be in the “through-the-wall systems” category so the cooling would be air-cooled DX.  It doesn’t describe the heating source for “through-the-wall systems” but 8.4.4.9.4 says that the energy type of the reference building’s heating system shall be identical to the energy type of the proposed building’s heating system.  The code considers heat pump to be an energy type so I think it should be an air-source heat pump.  I’m just not sure about the auxiliary heat – electric resistance or hot water?

 

I tried running this in CAN-QUEST but got some errors.  When I run a 4-storey office building with WLHP, the reference building is coming out as air-source heat pump with electric resistance heat so I’m leaning toward using that.  I can see there being an argument for hot water auxiliary heat though based on the proposed building having a fuel-fired boiler (to avoid fuel switching).

 

Thanks,

Aaron

 


     Aaron Smith, P.Eng

    Principal, Mechanical Engineer

 

   LEED® AP BD+C, BEMP, BEAP, CGD

       


     t: (902) 422-7393

     f: (902) 423-4945

     e:  <mailto:asmith at mreng.ca> asmith at mreng.ca

     www.mreng.ca <http://www.mreng.ca/>  

 


The electronic message contained herein is private and confidential, intended only for the recipient(s) specified. If you have received this message in error, please delete it and notify us immediately.  Any accompanying files are supplied as a matter of courtesy only.  The data are without warranty of any kind.  Any person or business making use of the data is responsible for confirming its accuracy and completeness.  M&R Engineering Ltd. is not responsible for edited or produced versions of this digital information. 

 

 

_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG <mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG> 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20190219/402bf165/attachment-0002.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1849 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20190219/402bf165/attachment-0004.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 1423 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20190219/402bf165/attachment-0005.jpg>


More information about the Bldg-sim mailing list