[Bldg-sim] EnergyPlus - Surface Outside Face Sunlit Fraction for Shading Devices
Michael J Witte
mjwitte at gard.com
Thu Oct 4 12:10:15 PDT 2018
Correct. Sunlit area applies to direct (beam) solar and is the result of
the surface (building and shading) shading calculations.
Shading devices (blinds, shades, and screens) are modeled as part of the
window system, because there can be more interactions than just
impacting sunlit area. There can be inter-reflections between the
glazing and the shading device, beam can be changed to diffuse, etc.
There are many output variables that report various details of the
window system and shading device. Search the RDD output for "Surface
Window".
Mike
On 10/3/2018 10:12 AM, Spyros Akritidis via Bldg-sim wrote:
>
> Hello everyone!
>
> I am using EnergyPlus in order to calculate the sunlit fraction (by
> unreflected beam solar radiation, as specified in the Input-Output
> Reference) of window glazing areas with the presence of external
> shading devices (e.g. venetian blinds, shades). The output values of
> Surface Outside Face Sunlit Fraction seem to be unaffected by the
> presence of these shading devices.
>
> I also tried another case: I removed the shading devices and added an
> overhang (through the Shading:Building:Detailed object in EnergyPlus).
> This time I get variable output values of Surface Outside Face Sunlit
> Fraction, indicating that the overhang was taken into account.
>
> So, is it safe to suppose that, at the moment (at least), EnergyPlus
> cannot calculate the sunlit area of external surfaces that are shaded
> by shading devices like blinds, shades, screens etc.(I guess it has to
> do with the polygon clipping algorithms) ?
>
> Or is there a way that can be calculated in EnergyPlus?
>
> Thanks,
>
> Spyros
>
> Spyros Akritidis
>
> Research Student
>
> School of Architecture, Building and Civil Engineering
>
> Loughborough University
>
> m: +44 077 6399 5008
>
> e: S.Akritidis at lboro.ac.uk <mailto:S.Akritidis at lboro.ac.uk>
>
> Linkedin-logo 2 <https://uk.linkedin.com/in/spyrosakritidis>photo
> <https://www.researchgate.net/profile/Spyros_Akritidis>
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20181004/219044f8/attachment-0002.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 1209 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20181004/219044f8/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 867 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20181004/219044f8/attachment-0005.png>
More information about the Bldg-sim
mailing list