[Bldg-sim] Expert advice to show minimum efficiency compliance Table 6.8.1C [1 Attachment]
Duggin, Cory
Cory.Duggin at tlc-eng.com
Wed Mar 7 06:24:49 PST 2018
Are you trying to show compliance with the mandatory minimum mechanical equipment efficiency or are you trying to select the App. G or ECB baseline system and efficiency?
What fluid runs through the actual DX equipment condenser water or air? I suspect your dry coolers are still creating condenser water to cool the equipment, in which case it is water-cooled.
Cory Duggin, PE, LEED AP BD+C, BEMP
Principal/Energy Modeling Wizard
USGBC MidTN Branch Leadership Group Co-chair
TLC Engineering for Architecture
direct:
615-346-1939
[just_logo_color_FINAL copy 2]
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Mayank Bhatnagar via Bldg-sim
Sent: Monday, March 05, 2018 10:36 PM
To: Javed Iqbal <javedvit at gmail.com>
Cc: Bldg-sim <bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] Expert advice to show minimum efficiency compliance Table 6.8.1C [1 Attachment]
Hi Javed,
In my opinion the air-cooled chiller efficiency should be used. As in the hybrid cooler (with water sprayer), the water spray is limited to only 200 hours in a year which is approximately 2-5% of the total hours in a year. So the worst case scenario would be air-cooled chiller.
Thanks.
Regards,
Mayank Bhatnagar
Senior Project Manager
Environmental Design Solutions Pvt. Ltd. [EDS]
D - 1/25
Vasant Vihar
New Delhi - 110057
India
On Mon, Mar 5, 2018 at 10:47 PM, Javed Iqbal via Bldg-sim <bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>> wrote:
Hello,
I would appreciate your expert advice on selecting 90.1-2010 Baseline system to show minimum efficiency compliance as given under Table 6.8.1C. One of the proposed project i am working on has two Chillers
1. One with Std. Dry Coolers
2. Second chiller has special arrangement where the surrounding air of cooling tower being cooled (dry bulb) by some sort of misting to increase the dry cooler effectiveness during extreme outdoor condition (CZ5A) ~ 80% lower water consumption compared to typical water cooled cooling tower. In this hybrid cooling tower, evaporation effect is happening but not like std. water cooled cooling tower.
To show minimum efficiency compliance, what condenser type do i need to choose; Air or Water Cooled in both the Cooling tower type; Std Dry cooler and Hybrid Dry cooler (see image below)? Also find an attachment to have more info
on the product.
[cid:image002.png at 01D3B5ED.BFFA39C0]
Thank you so much.
regards,
--
Javed Iqbal, LEED AP, CEA
Sr. Energy Analyst
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20180307/73e2a496/attachment-0002.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 4544 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20180307/73e2a496/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 151156 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20180307/73e2a496/attachment-0005.png>
More information about the Bldg-sim
mailing list