[Bldg-sim] building indoor temperature and humidity prediction
Davidson, Tom
TDavidson at DLBASSOCIATES.com
Mon Mar 5 13:47:36 PST 2018
Ibrahim,
Every building is obviously quite different, but I was involved with logging indoor and outdoor humidity levels in a new near-passive residence recently, and am posting the results as an image (assuming that an image can be posted here). There was an extremely high correlation between average indoor and outdoor humidity levels in the month of Dec 2017 (look at slopes of the two values, which are both absolute humidity levels). There is significantly less variability in the indoor levels than the outdoor levels. I guess this speaks to the ability of indoor components to absorb moisture and provide a dampening effect on the outdoor humidity variations.
[cid:image003.png at 01D3B4A1.316F2BE0]
Thomas A. Davidson, PE
DLB Associates | 265 Industrial Way West | Eatontown, NJ 07724
tdavidson at dlbassociates.com | 732-927-5108 | f: 732-774-5000
DLB Website<http://www.dlbassociates.com> | YouTube<http://www.youtube.com/user/TheDLBAssociates> | LinkedIn<http://www.linkedin.com/company/dlb-associates> | Twitter<http://twitter.com/DLBAssociates> | Facebook<https://www.facebook.com/DLBAssociates>
From: Nicholas Caton [mailto:Nicholas.Caton at schneider-electric.com]
Sent: Monday, March 05, 2018 1:25 PM
To: Ibrahim NEYA
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] building indoor temperature and humidity prediction
Hello Ibrahim,
If it’s an existing/built building, you’ll want to acquire a quantity of these to measure directly: http://www.onsetcomp.com/products/data-loggers/ux100-003. Very useful for objectively quantifying occupant comfort issues and operation/malfunctions of building or space-level humidity controls, which can then support energy savings/costs associated with correcting those kinds of issues.
If it’s a new building or else only on paper at the moment, any number of energy simulation software can report temperature and RH of airstreams at a system or zonal resolution. eQuest/doe2 is among them, however I’m inclined to suggest/request you to be more specific about your purpose and end-goals, supplemented with any existing building simulation experience/skillsets. eQuest comes with a definite learning curve before it’s outputs can be leveraged with confidence, and there might be software more purpose-built options appropriate to your task(s) at hand that I or others could suggest.
~Nick
[cid:image001.png at 01D3B49F.DA1EFCE0]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Regional Energy Engineering Manager
Energy and Sustainability Services
Schneider Electric
D 913.564.6361
M 785.410.3317
F 913.564.6380
E nicholas.caton at schneider-electric.com<mailto:nicholas.caton at schneider-electric.com>
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
[cid:image002.png at 01D3B49F.DA1EFCE0]
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Ibrahim NEYA via Bldg-sim
Sent: Monday, March 05, 2018 11:47 AM
To: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: [Bldg-sim] building indoor temperature and humidity prediction
Hi everybody,
Please, could someone help me to find a software that can predict the indoor temperature and humidity of a building?
Thank you very much for your help
Regards
--
NEYA Ibrahim
Ingénieur en Génie Electrique et Énergétique
Tél : 00226 61 85 77 07
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20180305/d6a0f14b/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 255 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20180305/d6a0f14b/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 8477 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20180305/d6a0f14b/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 84168 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20180305/d6a0f14b/attachment-0002.png>
More information about the Bldg-sim
mailing list