[Bldg-sim] Modeling zones that are conditioned but not controlled
Jim Dirkes
jim at buildingperformanceteam.com
Fri Feb 23 08:18:22 PST 2018
My opinion:
If there is no thermostat, the design essentially says that a wide
temperature variation is acceptable. You might consider arguing that those
zones *cannot *have unmet load hours because the design does not attempt to
control temperature.
For your own peace of mind (if your software allows it), you might also
report hourly temperatures in the zone to confirm that temps don't go crazy
unexpectedly during occupied hours.
On Fri, Feb 23, 2018 at 10:47 AM, Jones, Christopher via Bldg-sim <
bldg-sim at lists.onebuilding.org> wrote:
> I am wondering what others do for building zones that are conditioned but
> have no direct HVAC control. For example, a typical school will have a DOAS
> with perimeter radiation in exterior zones. There will be temperature and
> CO2 DCV in these occupied zones. The corridor will have transfer air and
> may have a couple of small supply diffusers from the DOAS but there is no
> thermostat to control the temperature in that corridor.
>
>
>
> If there is no thermostat, there is no setpoint so how does one determine
> if the corridor has unmet loads? How would one model the corridor zone in
> the baseline case for Appendix G?
>
>
>
>
>
> *Christopher R. Jones*, P.Eng.
>
> Technical Specialist
>
> Sustainability & Energy
>
>
>
> T +1 416-644-0252 <(416)%20644-0252>
>
>
>
> 2300 Yonge Street, Suite 2300
>
> Toronto, ON M4P 1E4 Canada
>
> wsp.com
>
>
>
>
>
> *Please consider the environment before printing...*
>
>
>
>
>
> ------------------------------
>
>
> NOTICE: This communication and any attachments ("this message") may
> contain information which is privileged, confidential, proprietary or
> otherwise subject to restricted disclosure under applicable law. This
> message is for the sole use of the intended recipient(s). Any unauthorized
> use, disclosure, viewing, copying, alteration, dissemination or
> distribution of, or reliance on, this message is strictly prohibited. If
> you have received this message in error, or you are not an authorized or
> intended recipient, please notify the sender immediately by replying to
> this message, delete this message and all copies from your e-mail system
> and destroy any printed copies. You are receiving this communication
> because you are listed as a current WSP contact. Should you have any
> questions regarding WSP's electronic communications policy, please consult
> our Anti-Spam Commitment at www.wsp.com/casl. For any concern or if you
> believe you should not be receiving this message, please forward this
> message to caslcompliance at wsp.com so that we can promptly address your
> request. Note that not all messages sent by WSP qualify as commercial
> electronic messages.
>
> AVIS : Ce message, incluant tout fichier l'accompagnant (« le message »),
> peut contenir des renseignements ou de l'information privilégiés,
> confidentiels, propriétaires ou à divulgation restreinte en vertu de la
> loi. Ce message est destiné à l'usage exclusif du/des destinataire(s)
> voulu(s). Toute utilisation non permise, divulgation, lecture,
> reproduction, modification, diffusion ou distribution est interdite. Si
> vous avez reçu ce message par erreur, ou que vous n'êtes pas un
> destinataire autorisé ou voulu, veuillez en aviser l'expéditeur
> immédiatement et détruire le message et toute copie électronique ou
> imprimée. Vous recevez cette communication car vous faites partie des
> contacts de WSP. Si vous avez des questions concernant la politique de
> communications électroniques de WSP, veuillez consulter notre Engagement
> anti-pourriel au www.wsp.com/lcap. Pour toute question ou si vous croyez
> que vous ne devriez pas recevoir ce message, prière de le transférer au
> conformitelcap at wsp.com afin que nous puissions rapidement traiter votre
> demande. Notez que ce ne sont pas tous les messages transmis par WSP qui
> constituent des messages electroniques commerciaux.
>
>
>
> -LAEmHhHzdJzBlTWfa4Hgs7pbKl
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
--
James V Dirkes II, CEO / President
The Building Performance Team Inc.
1631 Acacia Dr, Grand Rapids, MI 49504
(alphabet soup of efforts for greater understanding: PE, BEMP, BCxP, LEED
AP)
Direct / Mobile: 616.450.8653
jim at buildingperformanceteam.com
Website <http://buildingperformanceteam.com>l LinkedIn
<https://www.linkedin.com/pub/jim-dirkes/7/444/413>
*Coffee conversation:*The first idea is the worst, but it is the most
important because it starts discussion and becomes the building block
for other ideas.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20180223/170b9818/attachment-0002.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 25844 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20180223/170b9818/attachment-0002.png>
More information about the Bldg-sim
mailing list