[Bldg-sim] measurement of SHGC in the field
Nathan Brown
nathan at coolshadow.com
Fri Nov 10 10:07:30 PST 2017
Hi Chris —
That instrument won’t do it, because it is not sensitive to infrared. More than half of irradiance is in the near IR (aka solar infrared). You need a pyranometer (LiCor is our go-to <https://www.licor.com/env/products/light/pyranometer.html>, or an Eppley <http://www.eppleylab.com/instrument-list/standard-precision-pyranometer/> for critical measurements, although that is probably overkill for this). I would measure vertical irradiance just inside and just outside the glass under direct sunlight. Here in the Bay Area, there is a tool lending library that will loan a pyranometer. Perhaps you can find a similar source closer to you.
Best,
Nathan
Nathan Brown, BEMP, LEED AP ~ Associate
LOISOS + UBBELOHDE
- - - - - - - - - - - - - - - - - - - - - - - - - - -
1917 Clement Avenue, Building 10A
Alameda,CA 94501 USA
- - - - - - - - - - - - - - - - - - - - - - - - - - -
510 521 3800 VOICE
510 521 3820 FAX
- - - - - - - - - - - - - - - - - - - - - - - - - - -
www.coolshadow.com <http://www.coolshadow.com/>
> On Nov 10, 2017, at 3:08 AM, Chris Yates via Bldg-sim <bldg-sim at lists.onebuilding.org> wrote:
>
> Dear all
>
> We are trying to get a reasonable estimate for SHGC in the field.
>
> Our project is a retrofit of a relatively recent build that has overheating problems. No records exist of the original glazing spec.
>
> The glazing has a slight green tint; i.e. the "look and feel" of a fairly modern spectrally selective product with g-value (sorry SHGC) of about 0.4. However, a team member has now produced some records indicating this is significantly higher (more like 0.6).
>
> Does anybody have any experience or know of any research relating to this?
>
> I was thinking of something like this, taking measurements on the horizontal and vertical plane inside and out: https://www.uv-light.co.uk/meters/irradiance-and-exposure/ <https://www.uv-light.co.uk/meters/irradiance-and-exposure/>
>
> Our saint gobain rep tells me their spectrographic equipment is 50,000 GBP - a bit out of our price range! (They've offered to test a sample for us!).
>
> Cheers
>
> Chris
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20171110/5f50af8e/attachment-0002.html>
More information about the Bldg-sim
mailing list