Thank you Nick,
The responses received point to using a different baseline system and I agree with those interpretations. In my specific case, high rise residential with retail on the main floor, I am going to use System 1, PTAC for the residential and System 3, PSZ for the retail.
However, it seems to me that I could also assign System 5 to the retail spaces. The non-denominate space (retail) is larger than 20,000 ft2 and the building is large enough to meet the threshold for System 5.
The standard doesn’t explicitly indicate that the non-denominate spaces are to be on System 3 or 4 therefore, I believe I could select System 5 although it would not be an apples-to-apples comparison. The proposed design has packaged single zone systems serving the retail spaces making tenant sub-metering simpler.
[Title: RWDI - Description: RWDI logo]<http://www.rwdi.com/assets/logos/RWDI-logo.gif>
Christopher Jones, P.Eng. | Senior Energy Analyst
RWDI
901 King Street West, Suite 400, Toronto, ON M5V 3H5 Canada
Tel: (519) 823-1311 ext 2052
rwdi.com<http://www.rwdi.com/>
From: Nicholas Caton [mailto:Nicholas.Caton at schneider-electric.com]
Sent: Monday, February 20, 2017 10:47 AM
To: Javed Iqbal; Chris Jones
Cc: bldg-sim at lists.onebuilding.org
Subject: RE: [Bldg-sim] Baseline HVAC system type question
Right.
My framework is typically to piece this out in two steps:
1. Ignoring the possibility of G31.1.1A exceptions to start, determine the baseline system type for the whole building using the other prescriptions in play. In this case it would have to be system type 1 / 2 due to the predominantly residential situation.
2. Consider whether ANY singular or combined areas of the facility meet the 2 consistent requirements of G3.1.1A:
a. Total sum area > 20,000ft2 (aside: I’ve deliberately put forward alternative baseline systems where I haven’t met this threshold, but it totally makes sense to have a distinct/different baseline system)
b. “nonpredominant conditions” - this isn’t a glossary term and is subject to interpretation. My successful interpretations (as measured by non-rejected LEED submissions) have included:
i. non-residential vs. residential occupancies (this is pretty clear cut as a listed example in the standard)
ii. very different load profiles (i.e. large greenhouse attached to a school, or where in the proposed design you’re excluding cooling for a warehouse)
iii. very different occupancy/usage profiles (i.e. a chunk of the facility requires 24/7 ventilation or process loads resulting in very different system operations)
The interpretation below would look to agree and clash with my usual interpretation depending on circumstance. At the end of the day I feel the presence of non-predominant conditions should not substantially help nor hinder the baseline case in an artificial manner relative to the proposed case. So long as you’re holding to that “spirit” of the standard, you should be fine specifying alternative baseline systems.
~Nick
[cid:image002.png at 01D28C24.6C558160]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Regional Energy Engineering Manager
Energy and Sustainability Services
Schneider Electric
D 913.564.6361
M 785.410.3317
F 913.564.6380
E nicholas.caton at schneider-electric.com<mailto:nicholas.caton at schneider-electric.com>
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
[cid:image003.png at 01D28C24.6C558160]
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Javed Iqbal via Bldg-sim
Sent: Friday, February 17, 2017 7:47 AM
To: Chris Jones <Christopher.Jones at rwdi.com<mailto:Christopher.Jones at rwdi.com>>
Cc: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] Baseline HVAC system type question
Dear Chris,
The ASHRAE INTERPRETATION IC 90.1-2007<https://www.google.hu/url?sa=t&rct=j&q=&esrc=s&source=web&cd=3&ved=0ahUKEwjfrKS8oJfSAhXHiRoKHeV4CB4QFggrMAI&url=https%3A%2F%2Fwww.ashrae.org%2FFile%2520Library%2FdocLib%2FPublic%2F20100603_ic90120075.pdf&usg=AFQjCNGEpwM5bZsLYbRcfbO4CiEaSuvcAA&sig2=EN5_0kGzKchtWsr_RjQ1lQ> might help you. It states
Exception a to G3.1.1 should be utilized first to determine if multiple baseline HVAC system types from Table G3.1.1A are appropriate. However, exception a to G3.1.1 only applies if the separate area is greater than 20,000 ft2 and that area must qualify for a different baseline HVAC system type based on a different building type, heating source, number of floors, or residential vs non-residential classification. For example, if the office area and the warehouse area of a building are both greater than 20,000 ft2 and the office uses electric heat while the warehouse uses gas heat, then two separate baseline systems types could be utilized. If exception b to G3.1.1 applies to portions of the areas served by one of the baseline HVAC systems, then separate single-zone systems conforming with the requirements of System 3 or System 4 (depending on building heating source) can be utilized.
Hope this helps you!!
On Fri, Feb 17, 2017 at 2:17 PM, Chris Jones via Bldg-sim <bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>> wrote:
Jim,
My question is about the retail spaces on the main floor. I agree, the residential tower has System 1 but I am still not entirely sure about the retail spaces. They make up more than 20,000 ft2 so Exception G3.1.1.(a) applies but I am not sure if I use the area/number of floors of the entire building when selecting the retail baseline system. Or do I use the area/number of floors of the retail spaces when selecting the retail baseline System?
[Title: RWDI - Description: RWDI logo]<http://www.rwdi.com/assets/logos/RWDI-logo.gif>
Christopher Jones, P.Eng. | Senior Energy Analyst
RWDI
901 King Street West, Suite 400, Toronto, ON M5V 3H5 Canada
Tel: (519) 823-1311 ext 2052<tel:(519)%20823-1311>
rwdi.com<http://www.rwdi.com/>
From: Jim Dirkes [mailto:jim at buildingperformanceteam.com<mailto:jim at buildingperformanceteam.com>]
Sent: Friday, February 17, 2017 7:54 AM
To: Chris Jones
Cc: Anderson Letti; bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] Baseline HVAC system type question
Chris,
Residential is ALWAYS System 1 or 2, never one of the others.
On Fri, Feb 17, 2017 at 7:39 AM, Chris Jones via Bldg-sim <bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>> wrote:
Thank you Anderson,
In this case, the retail is more than 20,000 ft2 so I need to select a different baseline system.
My follow-up question: the building is more than 5 floors (majority is residential) but the retail only occupies the ground floor. Would I select System 7, VAV reheat as the building is more than 5 floors.
Or would I select System 3 for the retail because the that space only occupies 1 floor?
[Title: RWDI - Description: RWDI logo]<http://www.rwdi.com/assets/logos/RWDI-logo.gif>
Christopher Jones, P.Eng. | Senior Energy Analyst
RWDI
901 King Street West, Suite 400, Toronto, ON M5V 3H5 Canada
Tel: (519) 823-1311 ext 2052<tel:(519)%20823-1311>
rwdi.com<http://www.rwdi.com/>
From: Anderson Letti [mailto:anderson.a.letti at gmail.com<mailto:anderson.a.letti at gmail.com>]
Sent: Thursday, February 16, 2017 2:23 PM
To: Chris Jones
Cc: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] Baseline HVAC system type question
I believe that if the retail gross floor area is less than 1900 m2 you can use system 1, otherwise you can use exception a of section G3.1.1.
2017-02-16 17:12 GMT-02:00 Chris Jones via Bldg-sim <bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>>:
Standard 90.1-2007. The building is a high rise residential with the ground floor mainly retail. 90.1-2007 says to use the predominant condition to select the baseline system. In this case residential is the predominant condition therefore I am assuming the retail spaces would also have System 1, PTAC? Heating is fossil fuel.
[Title: RWDI - Description: RWDI logo]<http://www.rwdi.com/assets/logos/RWDI-logo.gif>
Christopher Jones, P.Eng. | Senior Energy Analyst
RWDI
901 King Street West, Suite 400, Toronto, ON M5V 3H5 Canada
Tel: (519) 823-1311 ext 2052<tel:(519)%20823-1311>
rwdi.com<http://www.rwdi.com/>
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org<mailto:bldg-sim-bounces at lists.onebuilding.org>] On Behalf Of Jim Dirkes via Bldg-sim
Sent: Wednesday, February 15, 2017 6:42 PM
To: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: [Bldg-sim] ASHRAE Building Performance Analysis conference needs knowledgeable presenters
What have you learned in the past few years that others will benefit from hearing about? Sample topics of interest might be:
* Making the business case for modeling
* Modeling challenging or unusual projects or systems
* Post-occupancy modeling tips, tricks and lessons learned
* Emerging trends
This conference has been an amazing event to learn, share and network. It's very much worth attending ... and of you present a topic part or all of your registration fee is waived (I should know that detail, but forgot and can't look it up right now.)
Registration is available NOW. Presentations are being solicited NOW. Find more information HERE <https://www.ashrae.org/membership--conferences/conferences/ashrae-conferences/2017-ashrae-building-performance-analysis-conference> - or feel free to call me and discuss a possible topic or other concern.
--
James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504
Direct: 616.450.8653<tel:(616)%20450-8653>
jim at buildingperformanceteam.com<mailto:jim at buildingperformanceteam.com>
Website <http://buildingperformanceteam.com> l LinkedIn<https://www.linkedin.com/pub/jim-dirkes/7/444/413> | May 2016 ASHRAE Journal article on energy modeling<http://buildingperformanceteam.com/bpt-insights-blog/item/73-modeled-performance-isn-t-actual-performance>
Choice. It is perhaps the most distinct and dignifying characteristic of humans. Consciously and with understanding, we choose what is true, honorable, right, pure, lovely … or otherwise. Like the rest of humanity, my choices don’t always align with true, honorable, right, pure, and lovely, but I know those are what I set my sights upon. I choose them.
________________________________
RWDI - A Platinum Member of Canada's 50 Best Managed Companies
This communication is intended for the sole use of the party to whom it was addressed and may contain information that is privileged and/or confidential. Any other distribution, copying or disclosure is strictly prohibited. If you received this email in error, please notify us immediately by replying to this email and delete the message without retaining any hard or electronic copies of same. Outgoing emails are scanned for viruses, but no warranty is made to their absence in this email or attachments. If you require any information supplied by RWDI in a different format to facilitate accessibility, contact the sender of the email, email solutions at rwdi.com<mailto:solutions at rwdi.com> or call +1.519.823.1311<tel:(519)%20823-1311>.
________________________________
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
--
Att.,
Eng. Anderson Letti
ASHRAE BEMP Certified - Building Energy Modeling Professional [https://docs.google.com/uc?export=download&id=0B7au6A8M6Tlyc0UwczE3aTRLX28&revid=0B7au6A8M6TlydWNTNkNMWkE2UExxdE40N1VVSEpkSjhhRklRPQ]
Rua 3700, 249. CEP 88330-203
Bal. Camboriú - SC - Brasil
Tell: +55 47 99632 3912<tel:+55%2047%2099632-3912>
Skype: anderson.letti
________________________________
RWDI - A Platinum Member of Canada's 50 Best Managed Companies
This communication is intended for the sole use of the party to whom it was addressed and may contain information that is privileged and/or confidential. Any other distribution, copying or disclosure is strictly prohibited. If you received this email in error, please notify us immediately by replying to this email and delete the message without retaining any hard or electronic copies of same. Outgoing emails are scanned for viruses, but no warranty is made to their absence in this email or attachments. If you require any information supplied by RWDI in a different format to facilitate accessibility, contact the sender of the email, email solutions at rwdi.com<mailto:solutions at rwdi.com> or call +1.519.823.1311<tel:(519)%20823-1311>.
________________________________
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
--
James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504
Direct: 616.450.8653<tel:(616)%20450-8653>
jim at buildingperformanceteam.com<mailto:jim at buildingperformanceteam.com>
Website <http://buildingperformanceteam.com> l LinkedIn<https://www.linkedin.com/pub/jim-dirkes/7/444/413> | May 2016 ASHRAE Journal article on energy modeling<http://buildingperformanceteam.com/bpt-insights-blog/item/73-modeled-performance-isn-t-actual-performance>
Choice. It is perhaps the most distinct and dignifying characteristic of humans. Consciously and with understanding, we choose what is true, honorable, right, pure, lovely … or otherwise. Like the rest of humanity, my choices don’t always align with true, honorable, right, pure, and lovely, but I know those are what I set my sights upon. I choose them.
________________________________
RWDI - A Platinum Member of Canada's 50 Best Managed Companies
This communication is intended for the sole use of the party to whom it was addressed and may contain information that is privileged and/or confidential. Any other distribution, copying or disclosure is strictly prohibited. If you received this email in error, please notify us immediately by replying to this email and delete the message without retaining any hard or electronic copies of same. Outgoing emails are scanned for viruses, but no warranty is made to their absence in this email or attachments. If you require any information supplied by RWDI in a different format to facilitate accessibility, contact the sender of the email, email solutions at rwdi.com<mailto:solutions at rwdi.com> or call +1.519.823.1311<tel:(519)%20823-1311>.
________________________________
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
--
Javed Iqbal, LEED AP, CEA
Sr. Energy Analyst
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
________________________________
RWDI - A Platinum Member of Canada's 50 Best Managed Companies
This communication is intended for the sole use of the party to whom it was addressed and may contain information that is privileged and/or confidential. Any other distribution, copying or disclosure is strictly prohibited. If you received this email in error, please notify us immediately by replying to this email and delete the message without retaining any hard or electronic copies of same. Outgoing emails are scanned for viruses, but no warranty is made to their absence in this email or attachments. If you require any information supplied by RWDI in a different format to facilitate accessibility, contact the sender of the email, email solutions at rwdi.com or call +1.519.823.1311.
________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20170221/adbc6777/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 2227 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20170221/adbc6777/attachment-0003.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 255 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20170221/adbc6777/attachment-0006.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 8477 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20170221/adbc6777/attachment-0007.png>
More information about the Bldg-sim
mailing list