[Bldg-sim] 90.1 - Minimum LPD for dwelling units - LEED
Chris Jones via Bldg-sim
bldg-sim at lists.onebuilding.org
Fri Sep 16 10:29:13 PDT 2016
Has the USGBC allowed lighting power density savings for multi-family projects in the dwelling units?
The CaGBC has allowed credit to be taken in dwelling units for LEED 2009 and I am how it will be handled with LEED v4?
Christopher Jones, P. Eng.
Rowan Williams Davies & Irwin Inc.
Consulting Engineers & Scientists
901 King Street West, Suite 400, Toronto, Ontario, M5V 3H5
T: (519) 823-1311 ext 2052
M: (416) 697-0056
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of via Bldg-sim
Sent: Friday, September 16, 2016 12:40 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] 90.1 - Minimum LPD for dwelling units
Hello,
I'm a little confuse since I have read that article about 90.1 2013 addendum. (http://www.buildings.com/news/industry-news/articleid/20142/title/multifamily-may-be-responsible-for-tenant-lighting-.aspx). It says:
More importantly, the standard would compel owners to address lighting within dwelling units, which have historically fallen outside of 90.1's scope.
Three questions about this statement :
1) For a compliance path (like comCheck), which article from part 9 of the 90.1 standard (2010 or 2013) specifically exclude dwelling unit to have minimum LPD?
2) Since Table 9.5.1 have a minimum LPD requirement for "multifamily" (that obviously include dwelling units), why Table 9.6.1 have no building type specific space type named "dwelling" or a common space type for "bedroom" (for those who want to split the dwelling in different rooms)?
3) In a LEED project (annex G) it's common to combined dwelling units with the same orientation in a single thermal block, which LPD value do you enter in your model for these thermal block ? (I assume LPD are same for your proposed and your baseline simulation)
Thanks
____________________________________________________________________
Julien Dutel, ing., CEM, CMVP.
Ministère des Ressources naturelles
Téléphone : 418 627-6379, poste 8060
mern.gouv.qc.ca
________________________________
RWDI - One of Canada's 50 Best Managed Companies - This communication is intended for the sole use of the party to whom it was addressed and may contain information that is privileged and/or confidential. Any other distribution, copying or disclosure is strictly prohibited. If you received this email in error, please notify us immediately by replying to this email and delete the message without retaining any hard or electronic copies of same. Outgoing emails are scanned for viruses, but no warranty is made to their absence in this email or attachments. If you require any information supplied by RWDI in a different format to facilitate accessibility, contact the sender of the email, email solutions at rwdi.com or call +1.519.823.1311.
________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20160916/3cb7ee2e/attachment.html>
More information about the Bldg-sim
mailing list